- #1
Yes, but not in the normal application. You want to basically drive a 120V winding, and get a center tapped 240V output, which would be two 120V, out of phase, and connected at the output neutral, correct?jimboz said:Summary:: Can I use a multitap transformer to step up 120 to split phase 240? Transformer schematic attached
View attachment 278130
My plan is to power the secondary with my 120VAC generator and use the 240VAC primary connection configuration and use the H3 and H8 taps as the neutral.
Tom.G said:If you do not need the isolation between the generator and pump, there is an easier way:
Connect the transformer Primary for 240V (X2 to X3)
Connect the generator to one half of the primary (for instance to X4 and X2/X3)
Connect the pump to X1 and X4
You can get away with this because the transformer is way oversized (5 times) for the pump. (It would need a minimum of 3X oversized)
edit: If one power lead from the generator is low side ("Ground"), connect it to the X2/X3 terminals. That gives you the conventional 2-phase 120V/240V connection.
Cheers,
Tom
Does anybody know if this generator ties Neutral and Earth ground at its output? At first I was not concerned with Earth ground issues, since it's a floating generator that is making the AC Mains 120Vac waveform. But now that I think about it, if the generator ties its Neutral and Earth ground connections together at its outlets, and you use an autotransformer to make the split center tap 120V-120V to get 240Vac, the placement of the "Neutral" output of the generator may matter.jimboz said:honda eu2200i
I think a lot of them do. I have mixed feelings about that.hutchphd said:Looks like it floats
I understand your unease. But remember those things can be used in places like flying hot air balloons or on a boat where no actual Earth is nearby.Averagesupernova said:I think a lot of them do. I have mixed feelings about that.
But it has a ground terminal (output grounds and case) and the user should use it. It must have double/reinforced insulation also, or it would never get safety certifications. But the "distribution system" it may be connected to should be grounded. The wiring in your house isn't designed for floating sources. OTOH, the wiring in your house should have it's own grounding too.Averagesupernova said:I think a lot of them do. I have mixed feelings about that.
Be careful when discussing this with others. There are two common interpretations:berkeman said:Does anybody know if this generator ties Neutral and Earth ground at its output?
Interesting. So it must be double-insulated (between the AC Mains input and its metal bits), so that a single fault can't energize the metal enclosure? Can you post the model number? Does it have a UL number on its information label/plate?jimboz said:Currently (no pun intended) the well pump is ungrounded.
I think it would have to be for an underwater motor. There just isn't a great way to ground water; or it's already grounded, what with being in the ground. I think it would be essentially for reliability to keep the electrons inside the wires and the water out.berkeman said:it must be double-insulated
There are readily available 240 -> 120V transformers available for using power tools on building sites. They are generally "autotransformers" in that the secondary is simply half way through the primary i.e. centre tap, no isolation. You CAN use any twin-primary transformer by just connecting the primaries in series, connect 240 to the "outer" ends, and take 120V from the one winding.jimboz said:Summary:: Can I use a multitap transformer to step up 120 to split phase 240? Transformer schematic attached
View attachment 278130
My plan is to power the secondary with my 120VAC generator and use the 240VAC primary connection configuration and use the H3 and H8 taps as the neutral.
A 120VAC generator is a type of generator that produces alternating current (AC) electricity at a voltage of 120 volts. This type of generator is commonly used for powering household appliances and electronics.
H3 and H8 taps are specific connection points on a 120VAC generator that allow for different levels of power output. H3 taps provide a higher voltage output, while H8 taps provide a lower voltage output.
To secure power from a 120VAC generator, you will need to connect the generator to your electrical system using a transfer switch. This switch will allow you to safely and easily switch between your main power source and the generator.
The purpose of securing power from a 120VAC generator is to have a backup source of electricity in case of a power outage. This can be especially important for critical systems, such as medical equipment or security systems.
Yes, it is important to follow all safety precautions when securing power from a 120VAC generator. This includes using a transfer switch, grounding the generator, and following all manufacturer instructions. It is also important to never operate a generator indoors or in an enclosed space, as this can lead to carbon monoxide poisoning.