- TL;DR Summary
- To properly size an isolation transformer suppling DC power supply, should the input or output power be used?
Good afternoon,
How should an upstream isolation transformer be sized for a dc power supply?
For example, if we have a power supply with the following specs:
Input Voltage: 120 VAC
Input Current: 2 Amps
Inrush Current: 22 Amps
Efficiency: 90%
Power Factor: 0.55
Output Voltage: 24 VDC
Output Current: 4 Amps
(Spec for 1606-XLP95E power supply)
Should the Isolation transformer be sized for the input or output power of the DC power supply?
I've seen both answers in different blogs. What I haven't seen is a good explanation for either case.
On one side, DC power supply has an input rating implying that it is what it needs to operate properly.
On the other hand, power supply output is much less to drive it's loads. It would also make sense to size the transformer based on the output power with a correction for efficiency. In this case, it would be P=V(out)*I(out)+Efficiency*V(out)*I(out).
This leads me to another question: What happens to the reactive power? Does it need to be accounted for when sizing a transformer?
Because a dc power supply contains capacitors to smooth out the dc waveform after the bridge rectifier, does the reactive power reflect fact to the supply? Does this also mean that when sizing an isolation transformer for an ac motor (inductive load, therefore, reactive power is being used and not reflected back to the line), the reactive power needs to be accounted for?
How should an upstream isolation transformer be sized for a dc power supply?
For example, if we have a power supply with the following specs:
Input Voltage: 120 VAC
Input Current: 2 Amps
Inrush Current: 22 Amps
Efficiency: 90%
Power Factor: 0.55
Output Voltage: 24 VDC
Output Current: 4 Amps
(Spec for 1606-XLP95E power supply)
Should the Isolation transformer be sized for the input or output power of the DC power supply?
I've seen both answers in different blogs. What I haven't seen is a good explanation for either case.
On one side, DC power supply has an input rating implying that it is what it needs to operate properly.
On the other hand, power supply output is much less to drive it's loads. It would also make sense to size the transformer based on the output power with a correction for efficiency. In this case, it would be P=V(out)*I(out)+Efficiency*V(out)*I(out).
This leads me to another question: What happens to the reactive power? Does it need to be accounted for when sizing a transformer?
Because a dc power supply contains capacitors to smooth out the dc waveform after the bridge rectifier, does the reactive power reflect fact to the supply? Does this also mean that when sizing an isolation transformer for an ac motor (inductive load, therefore, reactive power is being used and not reflected back to the line), the reactive power needs to be accounted for?