Test online psychrometric calculator

In summary: I am not sure. :)Yes, that's what I'm saying. When the straight process line intersects the saturation line, it means that the coil is saturated and the process is valid. Otherwise, the process is invalid and the coil is still wet.Thanks for clarifying that.I think that's all I have for this post.In summary, the online psychrometric calculator is working correctly, but needs verification by inputting values from an available psychrometric chart.
  • #1
penderway
Gold Member
10
0
New here and this is my first post. I've developed an online psychrometric calculator and I believe it is now working perfectly.

I would like someone or anyone who has expertise in this area to check my work.

The link is http://efficientcomfort.net/asp/PsychroCoilCalc_Web/PsychroCoilCalc_Web.asp

The calculator is geared towards evaluating coil performance rather than designing a coil. In particular I'm interested in knowing if I'm converting the input of standard or actual air CFM correctly to dry and moist air specific values (depending on selected option) for the calculations.

Any help would be greatly appreciated.

Wayne Pendergast
 
Engineering news on Phys.org
  • #2
I'm sorry you are not finding help at the moment. Is there any additional information you can share with us?
 
  • #3
Thanks for the response.

I believe that the calculator is working correctly. It's a bit different than standard psychrometric calculators in that it can calculate with moist air specific units, instead of just the common dry air specific and standard air units. I had some doubt that I was correctly converting between these different units for calculating actual airflow to use in subsequent calculations.

Dry air specific units are used all the time for HVAC coil design, and standard air is used all the time to rate blowers and fans. Since my goal is not to build another design tool, as there are already many, I am incorporating units of real moist air in order to measure real accurate actual performance. There aren't many resources that I can find that do this.

Since I'm not a formally trained engineer, I thought this would be a good place to get some verification that what I'm doing is correct.

But after going over it again and again for the past couple days, I'm more confident in it.
 
  • #4
Hi penderway,

Have you considered testing it by inputting values from an available psychrometric chart? One could give you many values you could use for testing input/output combinations.

Good luck.
 
  • #5
Mech_Engineer said:
Hi penderway,

Have you considered testing it by inputting values from an available psychrometric chart? One could give you many values you could use for testing input/output combinations.

Good luck.

Thanks, I have, It's right on target with the many typical psychrometric charts available (depending if they incorporate enhancement and compressibility factor. Trouble is they are all "Dry Air Specific".

Now if I could find a moist air specific chart, that would be nice. :)
 
  • #6
What do you mean by "moist air specific"? Maybe I'm rusty on the subject, but my understanding is a psychrometric chart should be valid for all relative humidities, e.g. 0-100% RH.
 
  • #7
Here's my understanding...and I welcome any corrections.

Dry air specific is the most commonly used unit of measure for HVAC design, It is the mass of dry air plus (and separate from) the mass of moisture it carries. Much easier to use in calculations and is accurate enough in the temperature and humidity ranges used in HVAC design. It's expressed, for example in density, as lbda/ft3. When used in HVAC design it errors on the over-sizing side so it is very acceptable.

Moist air specific AFAIK is used in industrial drying processes and is practically never used for HVAC design. It is more accurate and is best for measuring actual performance. It is a measurement of the total moist air mass. Expressed as lbma/ft3 or Humid density. Also Humid volume and Humid enthalpy.

Then there is also Standard Air, which is always 0.075 lbda/ft3. This is used for rating fans and blowers.

I've built my calculator to accommodate each of these units of measure as airflow inputs, and I convert them to either dry or moist air specific outputs. I haven't been able to find any references on this (except for standard air), but I believe I've figured it out correctly.
 
  • #8
When you say "more accurate," what is the typical percent error in an HVAC problem your method corrects for?
 
  • #9
I've not quantified it. I believe it's insignificant in the common ranges of temperature, humidity and altitude. I am in no way disputing the practice of using dry air specific units for design purposes. I only advocate the highest accuracy possible when measuring and calculating the actual performance.

I have another calculator that shows the difference of using 1.08, 0.68 and 4.5 factors in the common formulas.
http://efficientcomfort.net/asp/PerformCalc_Web/PerformCalc_Web.asp
Accuracy depends on how close to standard air the actual air your measuring is. If the airflow you measure is 0.075lbda/ft³ density and 0.24 Btu/ft³·°F specific heat, then the formulas will likely be exact.
 
  • #10
I thought it was common knowledge that the cooling and dehumidifying process had an ADP (apparatus dew point) that was a straight line thru the state points to the saturation curve.

I've read in system design literature that if it did not, then it was an invalid cooling and dehumidifying process because the coil was dry.

But in the real world (not at design conditions) the coil can be wet even if the straight process line doesn't intersect the saturation line.

I found the following quote from “Handbook Of Air Conditionig & Refrigeration - Basics & Constant Volume System Design” In section 20.49 it states:

A straight line has been used to represent a cooling and dehumidifying process, and the intersection of this straight line and the saturation curve is considered the effective surface temperature of
the coil and is called the apparatus dew point. This is a misconception. First, the cooling and dehumidifying process is actually a curve instead of a straight line. Second, the effective surface temperature as a fictitious reference point is affected by many factors and is difficult to determine in heatand mass-transfer calculations.
It is more accurate to define the apparatus dew point as the dew point of the moist air leaving the
conditioning apparatus, the coil, the air washer, or other heat exchangers.


This further demonstrates the flaws of applying design concepts (such as density factors, 1.08, etc.) to performance measurement procedures.

I've updated my psychrometric and HVAC performance calculators to incorporate leaving air dew point as the ADP when the process line doesn't intersect the saturation curve. I've made the ADP invalid only if the bypass factor exceeds .5

Just when I think I really understand psychrometrics... it turns out I don't!
 
  • #11
hey! can i know why your are using specific enthalpy in calculation of cooling load. Can't we directly use enthalpy available fromthe psychrometric table corresponding to the given Dbt and RH.The difference in answers is huge.
 
  • #12
An accurate value of Humid Air Enthalpy (whether moist air specific or dry air specific) is critical for calculating air conditioning load and/or equipment performance, especially when the highest accuracy is desired.

The formulae used in my calculator... (see page 6, 10 & 11 of this pdf download for examples)…are adopted, by the American Society of Heating Refrigeration and Air conditioning Engineers, as The Standard.

You could Google "Thermodynamic Properties for Real Moist Air, Dry Air, Steam, Water, and Ice (ASHRAE RP-1485)" for more details.

What is the source of the table you are using? Have you a link to it? I'm curious to compare.
:)
 
  • #13
I am using SI Units. i used you calculator and just converted the output say btu/lb to kj/kg. I compared this with direct calculation in SI units...the results were different.
I am just a student and not understanding why such a change is coming. Shouldn't just converting the final load from english to SI be giving the same answer as calculating the whole process in SI units. Please guide. I use the following book https://books.google.co.in/books/about/Engineering_Thermodynamics.html?id=91MZ2ZOb3n8C. You can get a pdf copy of this book easily in direct download. I'll try to upload.
 
  • #14
https://drive.google.com/file/d/0B6hjEAwn8lB-cm1IQ3B6Sk1XQWc/edit here you go!
 

FAQ: Test online psychrometric calculator

What is a psychrometric calculator?

A psychrometric calculator is a tool used to calculate the properties of moist air, such as relative humidity, dew point, and enthalpy. It uses mathematical equations and psychrometric charts to determine these properties based on input values such as temperature and humidity.

How does a psychrometric calculator work?

A psychrometric calculator works by using the principles of thermodynamics and psychrometry to calculate the properties of moist air. It takes into account the relationship between temperature, humidity, and pressure to determine the values of various parameters. The calculator uses equations and charts to perform these calculations.

What are the benefits of using a psychrometric calculator?

Using a psychrometric calculator can save time and effort in performing complex calculations related to moist air properties. It also ensures accuracy in the results, as manual calculations can be prone to errors. Additionally, some calculators offer the option to plot data on a psychrometric chart, making it easier to interpret and analyze the results.

Can a psychrometric calculator be used for any air mixture?

No, a psychrometric calculator is specifically designed for calculating the properties of moist air. It takes into account the unique characteristics of air and water vapor mixture, such as the relationship between temperature and humidity, to provide accurate results. It cannot be used for other gas mixtures or for dry air.

Are there any limitations to using a psychrometric calculator?

While a psychrometric calculator can provide accurate results, it is important to note that it is only a tool and not a substitute for understanding the principles of psychrometry. It also relies on accurate input values, so any errors in measurement can affect the results. Additionally, some calculators may have limitations in terms of the range of values they can handle, so it is important to choose a calculator that is suitable for the specific application.

Back
Top