Three Phase Per Unit System - Mark up, represent as single phase equiv

AI Thread Summary
The discussion revolves around calculating per unit impedance in a three-phase system, specifically addressing the confusion around base quantities for impedance calculations. The original per unit impedance of the generator is assumed to be based on a rated power of 500 MVA and a voltage of 22 kV, leading to a calculated actual impedance of approximately 1.936 Ω. The user contemplates using a new base of 100 MVA and 400 kV, noting that this results in a significantly larger base impedance and a much smaller per unit impedance. There is uncertainty about the impact of selecting different voltage levels as reference points, but the user concludes that using 22 kV and 500 MVA as the base for the generator is reasonable for scaling impedances. The final calculations for various components are presented, seeking validation of the approach.
Evari5te
Messages
10
Reaction score
4
Homework Statement
Express in p.u. all the quantities shown in the line diagram of the three-phase transmission system in Figure 2.32.

Construct the single-phase equivalent circuit.

Use a base of 100 MVA.

The line is 80 km in length with resistance and reactance of 0.1 and 0.5 Ω, respectively, and a capacitive susceptance of 10 μS per km (split equally between the two ends).
Relevant Equations
##Value_{per~unit} = \frac{Actual~Value~(any~Unit)}{Base~or~Reference~Value~(in~the~same~unit)}##

For a three phase system:
##S_{base} = V_{base}.I_{base}.\sqrt(3)##

##Z_{base} = \frac{\frac{V_{base}}{\sqrt{3}}}{I_{base}}=\frac{\frac{V_{base}}{\sqrt{3}}}{\frac{S_{base}}{V_{base}.\sqrt{3}}}=\frac{V^2_{base}}{S_{base}}##


##Z_{p.u~(new~base)} = Z_{p.u~(old~base)}\times\frac{S_{new~base}}{S_{old~base}}##

Where S is a rated power selected to be a base or reference quantity, and a Voltage is usually selected as a second base quantity and from these two all other base quantities such as impedance, ##\mathbf{Z_b}## and current ##\mathbf{I_b}## are derived.
I'm seeking some reassurance I've understood the question since there are no answers given in the book and I'm getting a bit tied up in knots.

What I am struggling with most is there are three per unit values for impedance already noted on the diagram without qualifying what ##Z{base}## is or what base quantities were selected from which ##Z_{base}## can be computed.

If I assume that the original per unit impedance (or resistance) given of the generator is derived from its rated power and export voltage then##S_b = 500MVA## and ##V_b = 22 kV##

then the stated ##Z_{p.u.}## of the generator of 2 would be against a ##Z_{base} = \frac{V^2_{base}}{S_{base}} = \frac{2.2^2\times10^8}{5\times10^8} = 0.968\Omega##

The actual Z of the generator would then be ##2\times0.968 = 1.936\Omega##.

While the question gives direction to use a base of 100 MVA it does not specify a base voltage to use so I thought it would make sense to select 400 kV as being common to both transformers in which case both per unit reactances could be used if scaled by 100/500 to reflect the change of base MVA from 500 MVA to 100 MVA.

If I am correct about the original assumption of the generator per unit impedance being based on 500 MVA and 22 kV, giving actual impedance of ##1.936 \Omega## then a new base impedance with reference quantities 400 kV and 100 MVA will be:

##Z_{base~(new)} = \frac{4^2\times10^{10}}{10^8} = 1.6\times10^3\Omega##

and

##Z_{p.u} = \frac{1.936}{1.6\times10^3}=1.21\times10^{-3}\Omega_{p.u}##

But this isn't looking good - selecting 400 kV which is x18 bigger than 22 kV, before squaring it and a new MVA x5 less is leading to a base impedance orders of magnitude bigger and hence a new per unit impedance that is very small....

While the per unit reactance of each of the transformers will be the same whichever of the primary or secondary voltages might be selected as a base, they have dissimilar voltage combinations.

I am not sure if it follows that perhaps it doesn't matter which of the three voltages 22 kV, 400 kV or 11 kV was used as a base simply because they share one common voltage of 400 kV and are each related by turns ratio.

But surely it does matter to know which voltage is or was used as reference when it comes to the line R, X and B, since I will need to compute ##Z_{base}## for ##S_b = 100 MVA##and will get three different answers depending on which voltage level is selected as a reference, Vb. I will also need to be consistent with whatever reference values was used to compute the generator per unit resistance.

In the end I will assume that 22 kV was used as a base quantity along with 500 MVA to compute Zbase for the given generator per unit resistance and will continue to use it so I only need to scale all impedances by the change in ##S_b## from 500 MVA to 100 MVA.

This gives

Generator rating:##500\times0.2 = 5 MVA_{p.u}##
Generator resistance: ##2\times 0.2 = 0.4\Omega_{p.u}##
Step up transformer reactance: ##0.1\times0.2 = 0.02\Omega_{p.u}##
Step down transformer reactance: ##0.15\times 0.2 = 0.03\Omega_{p.u}##
Line Resistance R: ##\frac{0.1}{0.968}\times0.2 = 0.0207 \Omega_{p.u}##
Line Reactance X:=##\frac{0.5}{0.968}\times0.2 = 0.1033\Omega_{p.u}##
Line Susceptance B: = ##80\times10\times0.968\times0.2=154\mu~S = 0.154~ S##

Does this sound reasonable?
 

Attachments

  • chapter 2_problem2_10.JPG
    chapter 2_problem2_10.JPG
    52 KB · Views: 95
Kindly see the attached pdf. My attempt to solve it, is in it. I'm wondering if my solution is right. My idea is this: At any point of time, the ball may be assumed to be at an incline which is at an angle of θ(kindly see both the pics in the pdf file). The value of θ will continuously change and so will the value of friction. I'm not able to figure out, why my solution is wrong, if it is wrong .
Thread 'Voltmeter readings for this circuit with switches'
TL;DR Summary: I would like to know the voltmeter readings on the two resistors separately in the picture in the following cases , When one of the keys is closed When both of them are opened (Knowing that the battery has negligible internal resistance) My thoughts for the first case , one of them must be 12 volt while the other is 0 The second case we'll I think both voltmeter readings should be 12 volt since they are both parallel to the battery and they involve the key within what the...
Thread 'Trying to understand the logic behind adding vectors with an angle between them'
My initial calculation was to subtract V1 from V2 to show that from the perspective of the second aircraft the first one is -300km/h. So i checked with ChatGPT and it said I cant just subtract them because I have an angle between them. So I dont understand the reasoning of it. Like why should a velocity be dependent on an angle? I was thinking about how it would look like if the planes where parallel to each other, and then how it look like if one is turning away and I dont see it. Since...
Back
Top