Torricelli's law problem about a sprinkler system

In summary, to determine the height of the tank needed to supply the sprinkler system in the hotel, we can use Torricelli's law and the volume of a cylinder equation to find the relationship between the volume of water leaving the tank and the depth of the water. Setting this up with the given pressure and time, we can solve for the height of the tank, which is 72.68 ft.
  • #1
spark706
3
0

Homework Statement


Sprinkler in a hotel is supplied by gravity from a cylindrical tank on the roof. Suppose the tank has a radius of 25' and the diameter of the outlet is 4". The system must provide 2270 psf for at least 5 minutes. What height should the engineer specify for the tank to meet these requirements.

Homework Equations


So I'm using Torricelli's law dV/dt=-a√(2gh) and pressure=density x depth
a=area of the outlet=.087266 ft^2
A=area of tank=1963.495 ft^2
g=gravity=32.2
h=height

The Attempt at a Solution



dh/dt*A = -a√(2g)
dh/dt = (-a√(2g))/A * √h
∫-.00035663dt = ∫dh/√h
-.000356663t + C = 2√h
(-.0001783315t+C)^2 =h

pressure / density = depth 2270/62.5 = 36.32' after five minutes

And from here I'm lost. MAybe I'm on the wrong track? Can anybody please help?
 
Physics news on Phys.org
  • #2


Hello there,

First of all, good job on starting with the correct equations and attempting to solve the problem! It seems like you're on the right track, but there are a few things to consider.

First, let's clarify the units for the given values. The radius of the tank is given in feet, so we'll stick with feet for all other dimensions. The diameter of the outlet is given in inches, so we'll need to convert that to feet before using it in our calculations. This means that the area of the outlet is not 0.087266 ft^2, but rather 0.000603 ft^2. Also, the given pressure of 2270 psf should be converted to feet of water, since we'll be using the depth in our calculations. This gives us a pressure of 37.12 ft of water.

Next, let's look at the equation you're using for Torricelli's law. It should be dV/dt = -a√(2gh), where V is the volume of water leaving the tank, a is the area of the outlet, g is the acceleration due to gravity, and h is the depth of the water in the tank. We can rearrange this equation to solve for h:

h = (V^2)/(2ga^2)

Now, we have two variables - V and h - and we need to find the relationship between them. This is where the given pressure and time come into play. We know that the pressure is equal to the depth, and we want the depth to be 37.12 ft after 5 minutes. So, we can set up the following equation:

37.12 ft = (V^2)/(2ga^2)

We also know that the volume of water leaving the tank is equal to the volume of the tank itself, since the tank is being emptied completely. The volume of a cylinder is given by V = πr^2h, where r is the radius and h is the height. Substituting in the given values, we get:

37.12 ft = (π(25 ft)^2h)/(2(32.2 ft/s^2)(0.000603 ft^2)^2)

Solving for h, we get h = 72.68 ft. This is the height that the engineer should specify for the tank in order to meet the given requirements.

I hope this helps! Let me
 

FAQ: Torricelli's law problem about a sprinkler system

What is Torricelli's Law?

Torricelli's Law is a physics principle that explains the relationship between the flow rate of a liquid and its velocity through an opening in a container. It states that the velocity of a fluid exiting an opening is equal to the square root of twice the acceleration due to gravity multiplied by the height of the fluid above the opening.

How does Torricelli's Law relate to a sprinkler system?

In a sprinkler system, Torricelli's Law applies to the water flowing out of the sprinkler head. The height of the sprinkler head above the ground determines the velocity of the water as it exits the sprinkler, and thus affects the area that is covered by the spray.

What is the problem with using Torricelli's Law in a sprinkler system?

The problem with using Torricelli's Law in a sprinkler system is that it assumes the flow rate of the water is constant. In reality, the flow rate of water in a sprinkler system varies depending on the pressure of the water source, the size of the sprinkler head, and the presence of any obstructions in the system.

How can the problem with Torricelli's Law in a sprinkler system be solved?

To solve the problem of varying flow rate in a sprinkler system, the system can be designed with a flow control valve, which regulates the pressure and flow rate of the water. Additionally, the size and placement of the sprinkler heads can also be adjusted to ensure consistent coverage.

Are there any other factors that can affect the accuracy of Torricelli's Law in a sprinkler system?

Yes, there are other factors that can affect the accuracy of Torricelli's Law in a sprinkler system. These include the shape and size of the opening in the sprinkler head, the viscosity of the water, and any external forces such as wind or temperature that may impact the flow of the water.

Similar threads

Replies
1
Views
1K
Replies
8
Views
3K
Replies
14
Views
1K
Replies
15
Views
6K
Replies
3
Views
3K
Replies
3
Views
2K
Back
Top