In summary: This is why in high frequency applications, it is important to minimize the length of leads in a circuit. In summary, the transformer core is modeled as resistance because the real power loss is in phase with the voltage and is dependent on frequency. Even with harmonics and high frequency applications, the core loss remains resistive due to the in-phase relationship between voltage and current. Ohm's law is a good simplified model, but it is not always entirely accurate as resistance can vary with frequency and other factors. Ultimately, the power dissipation is accounted for by the resistive part of the impedance, while the imaginary part contributes to losses in the wiring.
waqasakbar323
Why transformer core is modeled as resistance even though it is frequency dependent.With increasing frequency current rises. Doesn't it seem capacitive reactance behaviour? Which decrease with increasing omega?
Likes Delta2
A power transformer is specified for operation at a fixed frequency.
The real power loss is in phase with the voltage, not in quadrature as VAR.
Core loss is when flux change is greatest, which is in phase with the voltage, so must be resistive.
Likes DaveE
Correct, it make sense. But because in reality harmonics exist and are growing with increasing power electronics. So if someone want to model transformer, specially for harmonic studies. Than the generic model is not enough. For example capacitance between windings should also be considered. But i am confused abit about core. But as you said even we consider harmonics it would still be resistive due to inphase V and I.
Are you considering the core used for 50/60 Hz power,
or the small high frequency isolation transformer in a switching voltage regulator ?
There should be some low-pass network to prevent switching noise entering the AC supply.
There should be power-factor control of the rectifier input to a switching converter.
Core losses depend on frequency. See attached articles.
  • Eddy current and hysteresis losses calculation.pdf
  • Hysteresis and Eddy Current Losses Epstein.pdf
Likes Delta2
I took a closer look only to the 1st paper, I agree with the analysis there.
However though the voltage in a loop of eddy current has 90 degrees phase difference with the current that drives the coil whose core we study, this voltage is in phase with the eddy current, and though the eddy losses are proportional to the square of the frequency you still can't model it as a capacitance or inductive reactance, for the simple reason that in a capacitor or inductor the energy balance in 1 cycle is zero, while the eddy loss in 1 cycle is not zero.
I believe the correct modeling is as ohmic resistance whose value R depends on frequency. This modeling is happening in skin effect for example, where increasing frequency makes almost all of the current to flow in a thinner outer layer of the conductor, thus reducing the effective cross section of the conductor and thus increasing ohmic resistance.
Likes alan123hk
Yes! @Baluncore nailed it with his reference to the phase of the impedance in your modelling of the losses.
Ohm's law is a really good simple model for many things, but it's also often not true. Resistance can vary with frequency, with excitation level, etc. This is common in RF circuits where the losses in a capacitor dielectric or and inductor core are usually frequency dependent (nearly everything is, if you look closely enough). It's also true in things like light bulbs, thermistors, or semiconductors where resistance is a strong function of temperature because temperature often depends on the power loss.
The key point is that losses are modeled with real valued impedance (i.e. resistance) that has current that is in-phase with the voltage. An impedance can be modeled with a real part (lossy) and an imaginary part (energy storage, not loss). When you do the power calculation (integration of voltage times current) the imaginary, out of phase, part sums to zero. This is ultimately a definition IMO, if there's power dissipation, it has to be the resistive part, that's how the math works out.
Likes Klystron
@Baluncore and @DaveE both gave good advice. I would like to add that the imaginary portion of the power also cause real power losses via the resistance in the wiring that brings current to the device in question.
Likes DaveE
FAQ: Transformer modelling for harmonic studies
What is transformer modelling for harmonic studies?
Transformer modelling for harmonic studies is a process of creating a mathematical model of a transformer to analyze its response to harmonic currents and voltages. This is important for understanding the impact of harmonics on power systems and ensuring the safe and efficient operation of transformers.
Why is transformer modelling for harmonic studies necessary?
Harmonics are unwanted frequencies that can cause disturbances in power systems, leading to equipment damage and power quality issues. Transformer modelling allows us to predict the behavior of transformers under different harmonic conditions and design solutions to mitigate any negative effects.
What are the key parameters considered in transformer modelling for harmonic studies?
The key parameters considered in transformer modelling for harmonic studies include the transformer's impedance, inductance, capacitance, and resistance. These parameters can be affected by the presence of harmonics and can help us understand the transformer's behavior under different harmonic conditions.
How is transformer modelling for harmonic studies performed?
Transformer modelling for harmonic studies is typically performed using specialized software programs that can simulate the behavior of transformers under different harmonic conditions. These programs use mathematical equations and algorithms to create a virtual model of the transformer and analyze its response to harmonics.
What are the benefits of transformer modelling for harmonic studies?
The benefits of transformer modelling for harmonic studies include a better understanding of the impact of harmonics on transformers, the ability to design and implement effective solutions to mitigate harmonics, and improved power quality and reliability in power systems. It also allows for cost-effective and efficient design of transformers for specific harmonic conditions.