Transformer Voltage in case of Short-Circuiting
In summary, the conversation discusses the voltage across the secondary windings of a distribution transformer when the primary and secondary windings are short-circuited. According to the book, the voltage should not be much larger than 120V, but the person speaking finds this surprising and hypothesizes that it could be due to the resistance of the ground wire. Another person adds that in this situation, the transformer will have several turns shorted and the voltage control on the secondary will be lost, causing the voltage to rise and potentially damage LV equipment. They also mention that this can occur when LV cables are on the same poles as HV distribution cables.
QwertyXP
66
Consider a distribution transformer: The primary winding (HV) has a nominal voltage of 14.4 KV, whereas secondary (LV) has a nominal voltage of 120 V. One terminal from each of the primary and secondary windings is solidly grounded. A HV line (14.4 KV) is connected to the primary.
Now, if the HV line is short-circuited with the LV line, what will the voltage be across the secondary windings?
According to the book I have, the voltage will not be much larger than 120V. I find this very surprising. After the HV and LV lines are short-circuited, the potential difference across secondary should also have been 14.4KV, not a bit larger or smaller!
I think I have the answer already. The book was probably only referring to normal situations. The voltage between a terminal and ground can be slightly higher than 120V because of the resistance of ground wire.
When the primary to secondary circuit short is made, the transformer will have what is effectively several turns shorted that will saturate the core. This will remove voltage control on the secondary so the voltage on the secondary circuit will rise close to the HV and destroy LV equipment connected to the secondary circuit. The HV fuse will then open, but only after LV equipment has been damaged.
This happens when LV cables are on the same poles below the HV distribution cables. When a cable breaks and drops onto the LV wires you need a good insurance policy. You can tell when this has happened with a 3 phase MEN system because one third of the houses in the street have damaged equipment. Those were the houses that were powered by the LV phase that shorted.
Likes 1 person
Thank you Baluncore!
I would like to clarify that the voltage across the secondary windings in this scenario will not be exactly 14.4 KV, but it will also not be significantly larger than 120V. This is because a short circuit in the transformer causes a significant increase in current flow, leading to a drop in the voltage across the transformer.
The voltage across the secondary windings will depend on the impedance of the transformer, which is the ratio of the voltage to the current in the windings. In the case of a short circuit, the impedance decreases due to the increased current flow, resulting in a decrease in voltage across the transformer.
Therefore, it is expected that the voltage across the secondary windings will be slightly higher than 120V, but not as high as 14.4 KV. This is a normal behavior of a transformer during a short circuit and is a result of the transformer's design and construction.
Related to Transformer Voltage in case of Short-Circuiting
What is transformer voltage?
Transformer voltage refers to the amount of electrical potential difference between the input and output terminals of a transformer. It is typically measured in volts (V) and can vary depending on the design and specifications of the transformer.
How does a transformer handle short-circuiting?
In case of short-circuiting, a transformer is designed to automatically reduce the output voltage to a safe level. This is achieved through the use of protective devices such as fuses or circuit breakers that disconnect the transformer from the power source when a short-circuit occurs.
What is the effect of short-circuiting on transformer voltage?
Short-circuiting can cause a significant decrease in transformer voltage, as the resistance of the short-circuited circuit is much lower than the resistance of the transformer windings. This results in a large amount of current flow and subsequent voltage drop in the transformer.
How can short-circuiting be prevented in transformers?
Short-circuiting can be prevented in transformers by proper installation and maintenance procedures, such as ensuring proper insulation, regular cleaning and inspection, and avoiding overloading the transformer. Additionally, using protective devices like fuses and circuit breakers can help prevent short-circuiting.
What are the potential dangers of short-circuiting in transformers?
Short-circuiting in transformers can cause overheating, which can lead to fires or explosions. It can also damage the transformer and other connected equipment, leading to costly repairs and downtime. Additionally, short-circuiting can pose a safety hazard to individuals working near the transformer.
  • Electrical Engineering