In summary: Do #4. Install gP bypass valve on parallel zoned systems. The ability to extensively zone heating distribution has long been heralded as a major advantage of hydronic systems. At first, the concept appears so simple: Just install an electrically operated valve for each zone and open a given valve when its zone needs heat. Too often overlooked is the increased pressure differential across the circulator each time a zone valve closes. Left unchecked, high differential pressures can lead to flow noises, overheated pumps, flow leakage in other (closed) zone valves, and even erosion of piping materials.The solution
  • #1
TSN79
424
0
Several apartments have under floor heating (water) with a common boiler room and a central pump. There is no pump in the apartments. Each pipe run on each apartment's manifold has its own flow-indicator. The owner of one apartment is worried that if the neighbor turns off its heating, then more water will be forced through her manifold - increasing the usage and cost (they only have volumetric meters). They don't have any valves installed to prevent overflow to each apartment.

Some argue that even if this is the case, this will only result in the apartment being heated a bit quicker, and so the manifold actuator will close a bit earlier than it otherwise would - and there will be no difference in final cost. I can understand the reasoning, but I'm unsure if it's that easy. If she receives 20% more water, does that mean that the apartment will reach its set room temperature 20% earlier?
 
Engineering news on Phys.org
  • #2
What system controls the indoor temperature for each apartment?
What happens to the main flow and pump when all or most apartments have reached the temperature set point and are satisfied?
 
  • #3
Lnewqban said:
What system controls the indoor temperature for each apartment?
What happens to the main flow and pump when all or most apartments have reached the temperature set point and are satisfied?

The temperature is controlled by room thermostats that open and close actuators (on/off) on the manifold. I'm not sure how the pump is controlled. My best guess is that it keeps a constant pressure - so I do believe it reduces rpm as head loss increases when most actuators close.
 
  • #4
TSN79 said:
The temperature is controlled by room thermostats that open and close actuators (on/off) on the manifold. I'm not sure how the pump is controlled. My best guess is that it keeps a constant pressure - so I do believe it reduces rpm as head loss increases when most actuators close.
That is a common setting; pump may use a variable frequency drive, or a by-pass loop.
In that case, the inlet pressure at that each would be more or less constant, regardless hot water demand from other apartments.
 
  • #5
Lnewqban said:
That is a common setting; pump may use a variable frequency drive, or a by-pass loop.
In that case, the inlet pressure at that each would be more or less constant, regardless hot water demand from other apartments.

So the pump setting might eliminate the whole issue? Worst case is that the pump is constant speed only. If an apartment was to get some overflow - would the reasoning about faster heating hold at all?
 
  • #6
TSN79 said:
So the pump setting might eliminate the whole issue? Worst case is that the pump is constant speed only. If an apartment was to get some overflow - would the reasoning about faster heating hold at all?
If the pump is constant speed, then the operating point will move along the pump curve. It may be slightly less efficient with lower flow, but that's a tiny fraction of the system energy; the vast majority is in the actual heating of the water. Your logic is correct that if the apartment isn't overheating it is getting the same total amount of heat (again, to a pretty good first approximation).
 
  • Like
Likes Lnewqban
  • #7
I would think the most accurate way to do this would be that the system attempts to maintain a constant pressure. If not, one apartment could be overcharged if they were the only one calling for heat. There would likely be enough flow in that one apartment that the heat exchanger in said apartment would not extract the heat at the same rate as with a lower flow. To me, in order for the system to work, there needs to be a constant system pressure.
 
  • Like
Likes Lnewqban
  • #8
TSN79 said:
So the pump setting might eliminate the whole issue? Worst case is that the pump is constant speed only. If an apartment was to get some overflow - would the reasoning about faster heating hold at all?
Yes, and yes, but with increased noise and operational costs.
In order to make systems more efficient, the flow supplied by the pump(s) is reduced via slowing down rpm's.

Copied from
https://www.pmengineer.com/articles/84208-the-dos-donts-of-hydronic-system-design

"Do #4. Install gP bypass valve on parallel zoned systems. The ability to extensively zone heating distribution has long been heralded as a major advantage of hydronic systems. At first, the concept appears so simple: Just install an electrically operated valve for each zone and open a given valve when its zone needs heat. Too often overlooked is the increased pressure differential across the circulator each time a zone valve closes. Left unchecked, high differential pressures can lead to flow noises, overheated pumps, flow leakage in other (closed) zone valves, and even erosion of piping materials.

The solution in small to medium size systems is to install a differential pressure bypass valve across the supply and return mains of the distribution system. In effect, this valve "caps" the upper differential pressure across the mains.

On larger systems, circulator speed can be adjusted using a variable frequency drive (VFD) to maintain differential pressure within prescribed limits. In addition to regulating pressure, this approach reduces energy consumption of the pump under partial load conditions. Look for variable speed distribution pumps to be available for smaller residential and light commercial applications in the near future."

You can find more info by using "control of hydronic loops" in any search engine.
 
  • Like
Likes russ_watters
  • #9
Averagesupernova said:
If not, one apartment could be overcharged if they were the only one calling for heat. There would likely be enough flow in that one apartment that the heat exchanger in said apartment would not extract the heat at the same rate as with a lower flow.
I think it is unlikely, but it would indeed be a bad metering system design if it was only measuring flow and not heat. The system needs to measure flow and inlet/outlet temperature.
 
  • #10
Lnewqban said:
Look for variable speed distribution pumps to be available for smaller residential and light commercial applications in the near future.
The future was here over 10 years ago. Photo of the Grundfos 15-55F/LC hydronic pump in my house:
P2020017.JPG

It adjusts speed according to the number of open zone valves. The display alternates between GPM and watts. It shows 3 GPM at 24 watts with one zone open, and 8-9 GPM at 35 watts with all three zones open. The pump is self contained. It apparently calculates flow and head from power and RPM, then sets speed to maintain the desired head. This particular model has been around long enough that it is obsolete.
 
  • Like
  • Informative
Likes berkeman, Lnewqban, russ_watters and 1 other person

Related to Under floor water heating - result of overflow

1. What is under floor water heating and how does it work?

Under floor water heating is a type of heating system that uses hot water pipes installed under the floor to heat a room. The hot water is circulated through the pipes, which radiate heat upwards and warm the room. This is known as radiant heating and is considered more efficient than traditional heating systems that use air to distribute heat.

2. What causes an overflow in under floor water heating?

An overflow in under floor water heating can be caused by a variety of factors, such as a leak in the pipes, a malfunctioning thermostat, or an improperly installed system. It can also be the result of excessive pressure in the system, which can cause the pipes to burst.

3. How can an overflow in under floor water heating be prevented?

To prevent an overflow in under floor water heating, it is important to regularly maintain and inspect the system. This includes checking for leaks, ensuring proper installation and functioning of the thermostat, and monitoring the pressure in the system. It is also important to follow manufacturer's instructions and guidelines for proper use and maintenance.

4. What are the potential consequences of an overflow in under floor water heating?

The consequences of an overflow in under floor water heating can vary depending on the severity of the issue. In some cases, it may lead to water damage to the floors and surrounding areas, as well as potential mold growth. It can also result in higher energy bills and damage to the heating system itself.

5. How can an overflow in under floor water heating be fixed?

The first step in fixing an overflow in under floor water heating is to identify the cause of the issue. If it is a leak, the pipes may need to be repaired or replaced. If it is a malfunctioning thermostat, it may need to be replaced. It is recommended to seek the help of a professional plumber or heating technician to properly diagnose and fix the issue.

Similar threads

  • Mechanical Engineering
Replies
15
Views
2K
Replies
3
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
10
Views
2K
Replies
49
Views
12K
  • General Engineering
Replies
3
Views
2K
  • Mechanical Engineering
Replies
6
Views
1K
  • Mechanical Engineering
Replies
4
Views
3K
Replies
9
Views
1K
  • DIY Projects
Replies
23
Views
4K
  • DIY Projects
2
Replies
39
Views
9K
Back
Top