Unstable Static Pressure in Exhaust Duct

  • Thread starter Haotranphotomask
  • Start date
  • Tags
    Pressure
In summary, the pressure oscillations may be caused by the discharge of the two fans to the same header, which swings the dampers and induces vibration. The VFD's and dampers on the same fans make for a bad design, and replacing them with only one at the outlet of the common duct might improve the situation.
  • #1
Haotranphotomask
20
7
Hello, I have a system where two exhaust fans are running simultaneously. However, they both discharge to the same outlet. The suction pressure seems to be quite stable, but the discharge pressure fluctuates between 2" wc to 4" wc frequently. Below is a rough setup of my system. The rectangles are the dampers that we have on the discharge side. The ones with the red circles are dampers with a linkage and secured. The other ones are backdraft dampers and are not staying in place. I believe this happens due to both fans discharging to the same header, which causes the airflow to fluctuate the backdraft dampers.

My questions are:
  • Does this setup cause a reduced efficiency of the fans?
  • Would it be possible to lock open the backdraft dampers to reduce the static pressure fluctuations? I cannot find any codes referring to not locking the backdraft dampers. I understand the risk of fan shutting down and having air circle back into the rooms. If I accept that risk, would it be a possible solution short term?

IMG_E1029.JPG
 

Attachments

  • IMG_E1029.JPG
    IMG_E1029.JPG
    39.2 KB · Views: 108
Engineering news on Phys.org
  • #2
I would replace both back-draft dampers with only one at the outlet of the common duct, if possible.

If not possible, modifying the ductwork layout and connection in order to reduce the flow from each blower from hitting the opposite damper head on, would help.

Reducing the airflow of one blower via VFD or discharge volume damper may improve the current situation as well.

Pressure pulses from each blower may be deforming the metal ducts walls and swinging the dampers, inducing vibrations, and the fluctuations in static pressure and airstream velocity.
Even resonance may be possible.
 
Last edited:
  • Like
Likes russ_watters
  • #3
Lnewqban said:
I would replace both back-draft dampers with only one at the outlet of the common duct, if possible.
I was more worried if one fan fails, air blown from the running fan would travel through the failed fans into the rooms.

I have plans to redesign the entire duct work. I am trying to find short-term solutions. I may try to adjust the VFDs as suggested.
 
  • #4
Haotranphotomask said:
I was more worried if one fan fails, air blown from the running fan would travel through the failed fans into the rooms.

I have plans to redesign the entire duct work. I am trying to find short-term solutions. I may try to adjust the VFDs as suggested.
The diagram suggests that both are working in parallel and extracting from a common point.
If changing velocities is not sufficient, replacing that tee with a Y connector may be an effective minimum change to the existing ductwork.
 
  • #5
Haotranphotomask said:
The ones with the red circles are dampers with a linkage and secured.
VFD's and dampers on the same fans make for a bad design. One or the other, but not both. Are those dampers secured in the full open position? If not, they should be.
Haotranphotomask said:
the discharge pressure fluctuates between 2" wc to 4" wc frequently.
How frequently is frequently? If it is one to several times per second, it is probably a duct resonance. If it is once every several seconds, it might be the VFD's fighting each other. Is the blower speed under feedback control, or does an operator set the speed manually?

If that pressure is measured at the blower discharge, there is very high resistance in the discharge ductwork. What is the differential pressure across the blowers? What is the fan curve for the blowers? Please post the fan curve, and show the operating point(s).
 
  • Like
Likes berkeman and russ_watters

FAQ: Unstable Static Pressure in Exhaust Duct

What causes unstable static pressure in exhaust ducts?

Unstable static pressure in exhaust ducts can be caused by several factors, including improper duct design, blockages, changes in airflow demand, malfunctioning dampers or fans, and leaks in the ductwork. These issues can disrupt the balance of air pressure, leading to fluctuations.

How can unstable static pressure in exhaust ducts be diagnosed?

Diagnosing unstable static pressure involves a combination of visual inspections, airflow measurements, and pressure readings. Technicians may use manometers, anemometers, and smoke tests to identify irregularities in pressure and pinpoint the sources of instability, such as blockages or leaks.

What are the consequences of unstable static pressure in exhaust ducts?

Unstable static pressure can lead to inefficient ventilation, increased energy consumption, potential damage to HVAC equipment, and compromised air quality. It can also cause noise issues and discomfort for building occupants due to inconsistent airflow.

What solutions are available to stabilize static pressure in exhaust ducts?

Solutions to stabilize static pressure include proper duct design and sizing, regular maintenance to clear blockages, sealing leaks, adjusting or replacing malfunctioning dampers and fans, and installing variable air volume (VAV) systems to better manage airflow demands.

How often should exhaust ducts be inspected to prevent unstable static pressure?

Exhaust ducts should be inspected at least annually as part of routine HVAC maintenance. More frequent inspections may be necessary for systems with a history of pressure issues or in environments with high particulate loads that can lead to blockages.