Voltage readings in 14-3 Romex connected to combo switch

In summary: With the 'other' end of the 14-3 not connected, there is not any current flow to create magnetic coupling. You are seeing capacitive coupling between the wires in the 14-3 cable.
  • #1
Stephen Tashi
Science Advisor
7,861
1,600
TL;DR Summary
Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?
In a house (USA) there is "combination switch" ( e.g. https://www.acehardware.com/departm...utlets-and-plugs/switches/3235199?store=16359 ) containing 2 two-pole switches. [Edit: correction: 2 single pole switches]. The electrical diagram for the circuit ought to be the following:
comboSwitch.JPG


Should the voltage between R and W depend on whether switch S2 is open?

The input to the switch is the black wire from a 14-2 cable. The white wire of the 14-2 is connected to one end of the white wire of a 14-3 Romex cable. One end of the red wire of the 14-3 cable is connected to switch S1. One end of the black wire of the 14-3 cable is connected to switch S2. ( The 14-2 is an older type of cable that does not contain a ground wire.)

The other ends of the 14-3 cable are not yet connected to anything. When I measure the AC voltage from R to W with S2 open, I get about 120V or 0 V depending the position of S1. However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

The 14-3 cable is about 20 ft long. I assembled a bench top version of the circuit using about 1 ft of 14-3 cable. With switch S1 open, I get about 3 V beween R and W with switch S2 open and about 6 V between R and W with switch S2 closed.
 
Last edited:
Physics news on Phys.org
  • #2
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

Does this have to do with induced voltages?
Yes. Not induced, that implies magnetic field coupling due to current flow, which you don't have. It's really capacitive coupling inside the cable, most likely.

Voltage readings to a "floating" circuit node (i.e. disconnected from everything) are ambiguous. If you connected this configuration to whatever loads you intend, then you would get reliable (eg. 0) readings.
 
  • Like
Likes Stephen Tashi
  • #3
Stephen Tashi said:
Summary:: Should the voltage between the red and white wires in 14-3 Romex depend on the positions of both switches in a combo 2-pole switch?

However, with S2 closed, I get about 60 V with S1 open. Does this have to do with induced voltages?

With the 'other' end of the 14-3 not connected, there is not any current flow to create magnetic coupling. You are seeing capacitive coupling between the wires in the 14-3 cable.

You are probably using a digital voltmeter for the measurements. These have a very high input impedance so it doesn't take much stray capacitance for a significant voltage to show up.

Due to their much lower impedance, an older analog, moving coil, meter would read little or no voltage under the above conditions.

Cheers,
Tom
 
  • Like
Likes hutchphd and Stephen Tashi
  • #4
If you use a meter that loads the circuit (ie a "wiggy") you will see very different readings.
 
  • Like
Likes Stephen Tashi

FAQ: Voltage readings in 14-3 Romex connected to combo switch

What is 14-3 Romex and why is it used?

14-3 Romex is a type of electrical cable that contains three insulated wires - a black wire, a white wire, and a red wire - as well as a bare copper ground wire. It is commonly used in residential and commercial buildings to supply power to outlets, switches, and appliances.

What is a combo switch and how does it work with 14-3 Romex?

A combo switch is a type of electrical switch that combines multiple switches into one unit. It typically has two or more switches that control different lights or appliances. The 14-3 Romex is used to connect the combo switch to the electrical circuit, allowing the switches to control the flow of electricity to the connected devices.

How do I read voltage in 14-3 Romex connected to a combo switch?

To read the voltage in 14-3 Romex connected to a combo switch, you will need a voltage tester. Place one probe on the black wire and the other probe on the white wire. The voltage reading should be between 110-120 volts. If the reading is significantly lower or higher, there may be an issue with the electrical circuit.

Is it safe to touch 14-3 Romex while it is connected to a combo switch?

No, it is not safe to touch 14-3 Romex while it is connected to a combo switch. The wires inside the Romex are carrying electrical current, and touching them can result in an electric shock. It is important to always turn off the power before working with electrical wiring and to use proper safety precautions.

What should I do if I am getting a low voltage reading in 14-3 Romex connected to a combo switch?

If you are getting a low voltage reading in 14-3 Romex connected to a combo switch, there may be an issue with the electrical circuit. Check the connections to make sure they are secure and not damaged. If the issue persists, it is best to consult a licensed electrician for further assistance.

Similar threads

Back
Top