What Battery Bank Size Do I Need to Replace My 1250 kVA Diesel Generator?

In summary, the conversation discusses the possibility of replacing a 1250 kVA diesel generator with a battery bank. The estimated cost of such a project is around $1 million, and would require thousands of batteries to produce the necessary power for 4 days. The conversation also mentions the need for consulting with an engineer and considering factors such as protection and reliability before making a decision. Ultimately, it is recommended to stick with the diesel generator due to its reliability and lower cost.
  • #1
micuklein
7
0
Hello,

I have a bit of an issue and can't figure out how to find out the answer. I want to understand how to find out what battery I would need if I want to scrap the diesel generator I have and go for a battery bank.

I have a 1250 kVA rated generator. PF is 0.85, Rated voltage is 400V, rated current 1804 A and rated freq is 50Hz.

If I want to replace this generator with a battery bank, how do I go about trying to size the battery bank needed? It is assumed that the battery bank would have to provide power for 4 days, discharge to 85% max and only be used tops once a year.

Thank you!

Looking forward to hearing from you!

Kind regards,

mk.
 
Engineering news on Phys.org
  • #2
For starters what is your budget? Based on the numbers in your OP, you need more than 100 MWh of energy storage.
In very rough numbers, the batteries alone will cost nearly a quarter million dollars, the whole project perhaps $1 million. That puts you in the utility scale energy storage.

General Electric makes battery systems in that size range for utility use. https://www.gerenewableenergy.com/innovative-solutions/energy-storage/energy-storage-technology.html

energy-storage-rendering-hero.jpg
 
  • Like
Likes Averagesupernova
  • #3
To deliver that power for 96 hours would require thousands of batteries. Assuming lead acid batteries because they are cheaper you need to limit the amount of current from each battery to about 2 amps so that they last 96 hours. So each battery will need to produce 24 watts of power. Your power requirement is 720,000 W. So on this info you would need 30,000 deep cycle 12V batteries (e.g. Surrette 12-CS-11PS ) with quantity discount ($800 ea) you might be talking $24 M(US). FYI the total wgt of the batteries is about 4000 tons (272lbs x 30000)

This does not include the space to put them about 81,000 cu-ft (10x90x90) The cable to connect them (over 15,000 ft), the DC to AC converter(s), the chargers since the batteries may loose up to 10% of their capacity per month plus possible other equipment and expenses.

Battery technology just isn't up to snuff yet at a reasonable price. To produce the amount of energy from a mechanical generator talks only about 70 gal of fuel. Stick with the generator. If you needed to provide backup power for an hour then batteries would be doable but still expensive.
 
  • #4
Thanks a lot guys for the answer.
Let assume money and footprint are no issue.

How can I get a number of how big of a battery I need from the generator figures?
Anorlunda...you mentioned a battery bank of 100MWh, how did you get that number?

Thanks a lot!

Kind regards,

mk.
 
  • #5
micuklein said:
Thanks a lot guys for the answer.
Let assume money and footprint are no issue.

How can I get a number of how big of a battery I need from the generator figures?
Anorlunda...you mentioned a battery bank of 100MWh, how did you get that number?

Thanks a lot!

Kind regards,

mk.
I'm guessing, maths?

400V * 1804 A * 4 days * 24hrs/day = 69 million watt hours
 
  • #6
the energy in watt*hours is gotten by multiplying the output voltage by the current by the hours you needed to provide the power. Now the voltage and current that you gave was not specified as peak or average since you have an AC generator.. This will produce a difference in the calculation of power by a factor of two. Poweraverage = 0.5*peak voltage *peak current. Average power is what you need to consider. I assumed it was average and I got 69 M-watt-Hrs.of energy Each battery I used for the calculation can store about 2000 W-hrs of energy at a nominal voltage of 12.3 V which will reduce the full charge voltage from about 12.7V to 11.9V. after 4 days using a current 1.9 amps each. So we get about 30,000 batteries. The energy that you are producing (720,000 W-hrs) will power a house like mine for a about two weeks.
 
  • #7
micuklein said:
you mentioned a battery bank of 100MWh, how did you get that number?

##1250 KVA * 0.85 PF = 1062 KW \approx 1 MW"##
## 4 days = 96 hours \approx 100 hours ##
##1 MW * 100 hours = 100 MWH##

But listen, for something like this, you need to hire a consulting engineer rather than asking questions on an Internet forum. (:wink: speaking as one who spent most of his life as a consulting engineer :wink:). There is much more than price and footprint to consider. For example protection. Suppose the whole thing experienced a short circuit and exploded in a ball of fire the first day.

Then tell the consultant to work with one of the big four suppliers (ABB, Siemens, GE, Westinghouse) who can design, deliver, install, and test a turnkey solution). Most important, they can warrant the adequacy and suitability of the solution and their pockets are deep enough to do that without involving insurance companies.

Be prepared for some push back and arguments that you should stick with a diesel generator. Your reasons for wanting to switch may be perfectly valid, but they are unusual.
 
  • #8
anorlunda said:
But listen, for something like this, you need to hire a consulting engineer rather than asking questions on an Internet forum.

I will second that, this forum can give you an overview of possibilities. But based on the cost of a commercial 1500 Kw diesel generator about 310,000 $(US) I still would recommend the diesel genset over a battery bank. Gensets are reliable and I think are used in all large scale mission critical backup systems. You could reduce the number or batteries to 13,000 by by draining the batteries to 80% of their capacity over the 96 Hours of use which might be OK if you do this once a year and not decrease their life too much. But still your talking about $10M for the batteries. And these batteries require maintenance periodically keeping them charged, checking water levels and specific gravity. Maintenance free batteries do not require watering and specific gravity checks but still must be charged periodically but are more expensive.

Good Luck.
 
  • #9
Thanks a lot guys!
You've been really helpful.
I just wanted to get an idea of feasibility and it is clear that such a project is not feasible due to very high costs.

Appreciate your effort!

Have a nice week!
 

Related to What Battery Bank Size Do I Need to Replace My 1250 kVA Diesel Generator?

What is a battery bank?

A battery bank is a collection of batteries that are connected together to provide a larger capacity and longer run time than a single battery. It is commonly used in off-grid or backup power systems to store energy for later use.

How do I calculate the battery bank requirements for my system?

The battery bank requirements depend on the power consumption and the desired backup time. To calculate the requirements, you need to determine the total power consumption of your system and divide it by the battery voltage. Then, multiply this number by the desired backup time in hours. This will give you the total amp-hour (Ah) capacity needed for your battery bank.

What type of batteries are suitable for a battery bank?

There are different types of batteries that can be used in a battery bank, such as lead-acid, lithium-ion, or nickel-cadmium batteries. Each type has its own advantages and disadvantages, so it is important to consider factors like cost, lifespan, and maintenance requirements when choosing the right battery for your system.

What is the lifespan of a battery bank?

The lifespan of a battery bank depends on the type and quality of batteries used, as well as the usage and maintenance of the batteries. On average, a battery bank can last anywhere from 3 to 10 years.

How do I maintain my battery bank?

To ensure the longevity of your battery bank, it is important to regularly check the battery levels, clean the terminals, and avoid overcharging or deep discharging the batteries. It is also recommended to have a battery monitoring system in place to keep track of the battery health and performance.

Similar threads

  • Electrical Engineering
Replies
7
Views
1K
Replies
19
Views
5K
Replies
11
Views
2K
Replies
1
Views
2K
Replies
15
Views
2K
  • Electrical Engineering
Replies
2
Views
2K
Replies
14
Views
20K
Replies
27
Views
3K
Replies
19
Views
2K
  • Other Physics Topics
Replies
22
Views
4K
Back
Top