In summary: Sounds insane but...Very pure water is a good insulator. Some generator windings are water cooled.I've heard of success washing insulators on transmission lines. Our trial on a transformer didn't work out...
  • #36
@William White
Very interesting! I was under the mistaken assumption that only the final distribution transformer's secondary is star wound and all upstream transformers are delta wound.
I never realized that the 11kV primary on my TX (which is delta wound) would be connected to the 22 kV feeder's secondary that would be star wound.
Can you elaborate about why a Earth reference is needed at every stage? What would be the problem in having a voltage level that has only deltas i.e. no Earth reference?
Also, in your description some stages are star-star. What's the choice that goes into deciding if to have a delta-star or a star-star etc.
  • #37
a) A reference provides the quoted voltage with a physical meaning. This reference is the mass of earth, which is taken to be 0V.
b) Say you had a (33kV) circuit with no earth, how would you achieve safety in Earth fault conditions?
Safety is the most important reason for earthing an electrical system. A lot of money is spent on protection to detect Earth faults in EHV networks.
this might be of interest
https://en.wikipedia.org/wiki/Zigzag_transformer
Its to ensure that you have a Earth point at that voltage. If you look at the list above, if the 11/33 TX was delta-star there would be no star point on the 11KV network. If that was the case, there would need to be another transformer (connected somewhere) at 11KV that did have a star point.
I've attached (a small part of a) schematic of one of the primary s/s in my town. It shows two 33/11 TXs connected in parallel. The HV and LV windings are both star.
If you look carefully the star points of both TXs LV windings are connected to the same Earth point, which is a liquid-water resistor (just a great big tank of water which limits Earth fault current - its rated at 1,200A for 30sec).
There is the ability to close the neutral of either TX down to "solid" Earth (instead of through the resistor). You might see those switches in the middle of the diagram. You can also see the CTs on the TX neutral - these are there to detect earth-currents. They are connected relays which will trip the transformers CB if Earth current is flowing (for too long)
This is the law in the UK regarding earthing
http://www.legislation.gov.uk/uksi/2002/2665/regulation/8/made
I guess many countries would have the same meaning (but obviously worded differently)
Likes rollingstein
  • #38
it's almost off-topic and trivial to mention this , given the overwhelming importance of earthing
...but for the record
when you go through a transformer ΔΔ or star star there's no phase shift
when you swap between Δ and star there's 30 degree phase shift
since the system designer must arrive at his destination with all his feeders coming from different directions still in phase
sometimes that'll play a part in his choice of transformer connection.
  • #39
Ah! That makes sense. I had never thought of that part!
Out of morbid curiosity, say a mistake was made and an out of phase feeder was connected. Would the results be spectacular?
PS. The linemen, for example, typically carry no easy tool to detect relative phase in the field do they?
  • #40
yes, one will see TXs described as DY11 and such like
D - delta
Y - wye(star)
11 the o'clock phase shift (one -hour being 30°)
  • #41
D - delta
Y - wye(star)
So that's why they have all those esoteric vector groups (Dyn5, Dyn11 etc.) they sell transformers in, eh? To give the designer the freedom to get his phases all lined up before he ties them in?
  • #42
HV switchgear is normally rated for a short circuit right up on the TX:
The rating is, say, 250MVA at 11kV; 750MVA at 33kV for three seconds.
So if you closed a breaker in onto such a situation it would (should!) trip instantaneously. Depending upon how good the breaker was, it might grumble for a split second or so (and that can be quite alarming!)
The speed of protection is determined by how much current is flowing (except in instantaneous trip relays which can be set to trip instantly for any fault current or for fault current above a certain threshold)However, you would not want to be using a manually operated switch (rather than a breaker) to close onto such a fault. That is madness and dangerous, and against every rule in the book!
The rule is, that if connections have been unmade, and then remade, or new connections are made, the circuit is made live remotely (after phasing checks have been confirmed - see below) whilst everybody is clear of the point of work.
yes, you use a voltage stick to detect HV
Its an insulated rod, with a voltage detector that beeps when close to HV.
So, say you wanted to Earth a HV line for maintenance; you would make it dead, isolate it and then test dead using the stick before you put your Earth's on.
You approach the line with the stick and as it gets close it beeps if the line is live.If you wanted to check phasing; then you use phase sticks (which are glorified test lamps). You check l1-l1 (should be in phase) then l1 to l2 (should not be) and so on...
Likes rollingstein
  • #43
that's it,
the n is saying the Y has a neutral connection
Likes rollingstein
  • #44
I've seen the voltage sticks in use. But never knew they carried phase sticks too.
The closest I can recall is those set of lamps and the synchroscope / spinning needle when bringing a generator on-line the old school way.
  • #45
Spectacular is in the eye of the beholder.
Some protective device should gracefully subdue the overcurrent.
The distribution fuses in your neighborhood sound like a shotgun when they go.This is extremely unlikely but possible
http://www.newson6.com/story/195654...sion-damages-ponca-city-electrical-substation
expanding vapor , be it dynamite or copper, follows the same gas laws...
  • #46
rolling:
Its very important to confirm phasing before remaking conductors.
If there is an LV backfeed available from another HV source; the phasing can be checked on the LV.
I think this is safer - can be done with a test lamp, and no special safety procedures and documents required - but it is not always possible.
  • #47
When I worked on networks, I would often get called out to replace LV fuses after they popped on a fault.
You had to keep banging the fuses in until the fault cleared (ie the cable blew in half, or blew back together).
Once, the fault was right under my feet, I slapped the fuse in and the ground lifted about 3 inches. I was out of the sub like a rocket!
  • #48
Taking LONG steps might not be the best thing to do. :devil:
A couple of my favorite images. Compliments of http://ecmweb.com.
Likes davenn
  • #49
no worries with that
a) substations are equipotentially bonded
b) one wears heavy duty insulated boots when working live
c) if there is danger of an imminent explosion, you get out! (before working live, you ensure you have a clear, quick escape route: doors are left open, no tools or rubbish lying around, nobody else in the substation etc)
sad story about step potential
About 10 years ago a colleague of mine had to walk a 33 kV line to look for damage (it had tripped earlier)
He found a dead man on the ground next to a tractor. The dead man's young son was in the tractor.
The farmer had hit a 33kV line with his tractor (the machinery on his tractor was raised and he drove under the line).
There was a bang as the conductors shorted and then the circuit tripped. He jumped out of the tractor onto the ground to see what happened just as the circuit reclosed. Dead.
His young son had either the sense, or fear, to stay in the tractor. (It was about two hours before the linesman turned up and called the police)
  • #50
You mean he was killed by the "step potential"? He was not in contact with the tractor when he was killed?
As an aside, are reclosers triggered by the fault current? In such a case like when a tractor contacts the line is the fault current much higher than any normal load current through the 33 kV line? i.e. How easy or difficult is it to select a threshold that can cleanly separate a fault like this from just regular load spikes.
Also, is 33 kV a transmission voltage or a distribution voltage? How far apart are these reclosers on a transmission line?
  • #51
He was safe in the tractor because it has great big 6 feet rubber tyres.
The tractor was at the same voltage as the overhead line.
The ground was at zero Earth potential.
As he stepped out of the tractor and put one foot down on the ground there was a massive voltage across him and he fried (HV, because of the power involved, tends to cook you alive rather than shock you into death)The auto-reclose is normally a relay on the supply CB.
Overhead lines are prone to nuisance tripping. Wildlife can short out the conductors, so can flying debris in the wind (branches etc). High winds can clatter the lines together.
All these sorts of faults clear themselves (the dead animal falls to the ground, the branch falls down etc). So after a few seconds (generally 3-5 seconds) the relay sends a signal to the CB to close. If the CB trips again (the fault is still standing) the relay is either programmed to lock the breaker open or try again.A load spike at 11 kV or LV would generally not even be a blip at 33kV. Thats one of the reasons for discrimination.
A dead short across a 33kV line can be several hundred MVA. There is no load spike that could require such power - the maximum load of the 33 transformer is typically 15/30 MVA. (15 continuous/30 short time, or with coolant pumps and air fans running(
(an oil filled CB contails several hundred litres of mineral oil - a large fault will cook the oil black)
Earth faults generate lower fault levels, but last longer. So the trick is to set different protection schemes to operate at different rates.
Designing protection curves is not a trivial task. The protection closest to the fault should trip first and it should diffentiate between load and faults, and different types of faults (ie do you want to take out the LV breaker and just disconnect load, or the HV breaker and take out the transformer)In the UK 33 is a now distribution voltage, but many still call it subtransmission (distibution was below 22kv; subtransmission was historically up to 132 kv; transmission 275 kv and the "supergrid" 400 kv. The distinction was generally due to the different departments that looked after the work)
  • #52
Understood. Stepping out is a sure way to get yourself killed.
I was imagining a guy who didn't step out but jumped and then while standing on the ground the recloser closed and the step potential between his feet got him killed. That would sure be bad luck.
As I understand, it's very tricky to estimate the effect of a step potential while standing on the ground close to a downed conductor. e.g. the gait / stride varies, ground resistivity varies etc.
Have you heard of fatalities due to the step potential in real life? i.e. People who didn't actually touch a conductor nor a piece of live equipment nor were in the water but got killed merely by the current flowing through the ground from one leg and out through the other?
I've seen calculations of this but never heard of any anecdotal electrocutions of this nature.
  • #53
yes, if he jumped clear, he would (could) have been okay
They teach people who operate HV switches to keep their feet planted firmly together when operating the switch in case the earth-mat fails (or is missing - farmers love to plough up Earth mats near switches in fields)
I've heard of plenty of people getting to close to the safety clearance and getting fried - idiot metal theives.
And this
http://news.bbc.co.uk/sport1/hi/other_sports/horse_racing/9400599.stm
horses being much more likely to die than people
  • #54
Indeed! But that's more like an arc from the conductor to the idiot's body.
  • #55
Reminds me of another anecdotal story I've heard that stray potentials can cause cows to reduce milk production. Sometimes a tingle below the perception threshold of a human will be enough to severely impact the milk production of a dairy barn.
  • #56
"Step" potential is called that because it's the voltage that would appear between a man's feet when he takes a step
as opposed to a step change in time
it'd be volts per meter or yard or foot ; volts/lengthclearly a horse has more distance between his front and rear feet than the span of a man's step
and the path from horse's front to rear legs goes through horse's chest, unlike a man on two legs,
Lightning strikes produce a lot of Earth current and it goes a surprisingly long way from the strike.
Once while i was swimming in a freshwater lake lightning struck about a mile away and the shock was surprising but not very painful. "Wow , " i thought, "glad that wasn't any closer !"Once upon another time when returning from a fishing trip in Everglades, with the afternoon thunderstorms menacing us from behind, we passed a flock of flamingos standing on one leg.
That's when it dawned on me, that one legged stance protects them from a shock should lightning strike anywhere nearby.
i wonder...
  • #57
If a one legged stance would protect a flamingo from feeling a shock then how come a "zero legged" swimmer you still felt a shock?
  • #58
make up some numbers (just for example - it doesn't matter what the numbers are for illustration)
There is a lightning strike in the water which results in a voltage gradient. Say it is 1000 volts per metre in the region of interest.
The body of the swimmer is 1 m long. There is a voltage across the swimmer of 1000 V AND the flow of current is across his organs!
The flamingo has one leg in the water. Its tiny little foot is 2cm across. There is a voltage gradient of just 20V across its foot BUT the current will not flow into its organs because there is no circuit.
Its exactly why birds can sit on a live wire. The voltage gradient along the wire is (for all intents) zero. They sit on the wire and their entire body is at the same voltage as the line and there is no voltage gradient.
If it was a big bird (like a swan) and it opened its wings and touched the adjacent line then there is the full voltage across the bird body. Its fried.
  • #59
William White said:
Its exactly why birds can sit on a live wire. The voltage gradient along the wire is (for all intents) zero. They sit in the wire and their entire body is at the same voltage as the line and that voltage is fixed. No gradient.
But humans too can sit on live wires right? In spite of having much larger bodies. e.g. Those guys doing hot work on high voltage transmission lines? Or is their protective suit a Faraday cage?
  • #60
well they wear a protective suit but the principle is that same with the bird
at any two points on the same line the voltage difference is (for all practical purposes) zero (significant volt drops occur over very long distances - hundreds of metres).
What the linemen cannot do is touch two lines that are at different voltages.What is interesting, is that you will not see birds sitting on EHV lines (above 132kV). The air is conductive around the line and there is a voltage gradient in the air. When the birds get close enough it is very uncomforable for them and they fly away.slightly off topic - but if you have a flourescent tube and live near a supergrid line (400kV); walk under it with the tube and it will light up. You can plant the tubes in the ground and they will light up. An artist made a electric forest of flourescent tubes
http://www.richardbox.com/
  • #61
The voltage gradient was down to some number of volts per meter that's not lethal but still impressive .
I'm about 1.72 meters long , a bit more with arms extended
so whatever voltage was developed across the roughly two meters of water surrounding me was impressed across me.try a search on 'electrofishing'
  • #62
try a youtube search on high voltage suit
great video here
www.youtube.com/watch?v=9tzga6qAaBA
  • #63
great video here
@jim hardy
Oh that one's one of my favorite vids. But the thing that confused me is whether it's the faraday cage that protects him or the fact that he's always on an equipotential surface.
i.e. If someone tried to go on the live line using the same careful technique but sans the special suit, would he get electrocuted? I've always wondered about this.
PS. Are live lines hot to touch? How much would the surface temperature of a line like this one likely to be?
  • #64
The suit is used because of the potential gradient AROUND the conductor.
The air around the conductor has voltage gradient.
When the voltage is large enough, this gradient can become substantial
Birds can sit on a 11kv or 33kv line; they will not sit on a 132kV line
Likewise, the worker needs to be at an equipotential; so at lower HV, the suit is not needed (linemen use hot glove technque). at EHV, the voltage gradient is large enough to set up a current that can flow through the worker. I have spoken to live line workers and they say it feels like insects crawling all over.The temperature of the line depends on the current flowing through it.
You can think of the line as a single-bar electric heater.
A single bar electric heater is about a foot long and is rated at 1kWA 33kV is tens of miles long (supergrid line is hundreds of miles long)
Power is i^2 R (where R is the resistance of the line and i is the current flowing). Current can be several hundred amps. Its important that the line has as low a resistance as possible (the electricity company is losing money if the line is acting like a long bar heater!)
In short, no they do not get appreciably hot, there is just not enough power loss per short unit length. Icing can be a big problem in the winter: the weight of ice can bring the line down.
You can work out how hot they get compared to a bar heater. Just work out the reistance of the line. Say its 150 sq mm aluminium (for arguments sake). Say its 10 miles long. There you have your resistance. Then say it has 200 Amps flowing. You can then divide into a short length (say a foot, like a bar heater) and compare the power output to a bar heater.
Hot spots can occur at loose connections. Helicpoters regularly patrol EHV lines with an infrared camera to keep an eye on the growth of hot spots.
  • #65
William White said:
In short, no they do not get appreciably hot, and icing can be a big problem in the winter: the weight of ice can bring the line down.
Thanks @William White
The other problem that ice build up reminds me of it conductor gallop. I remember reading that when impending gallop risk is high due to icy conditions in an area the power dispatchers can, to some extent, route extra power through a branch bringing up I-squared-R heating to the point where it could melt off some of the ice. Not sure how realistic this is and whether dispatchers actually have the kind of routing flexibility needed to achieve this.
  • #66
good question.
I think of the phenomenon as one of capacitance , where the line's surface area is one plate of a capacitor and the rest of the universe forms the other plate
Think for an instant in DC - freeze frame your thinking... AC is after all at any instant going in only one direction
You saw the sparks to the helicopter as he attached the clamp to the HV wire.
That current brought the helicopter to same potential as the line. The helicopter became a 'wide spot' on the capacitor plate to which it connected.. the spark charged the capacitance of the helicopter to line voltage.
Now back to AC thinking: Since that helicopter's capacitance must be constantly charged between positive and negative high voltage as the power line cycles, AC current must flow. That's why the sparks persist, were that a HVDC line there'd be only one spark.
The lineman sits inside his HV suit which has capacitance to the rest of the universe. So charging current flows into and back out of his suit at line frequency. But since he's inside the suit which is an equipotential surface he experiences no voltage gradient.
Were he to grab the line without a protective suit, the current necessary to charge his body's capacitance would flow through his hand.
Would it be enough to feel ? I suspect so. Let's put a number on it.
I know from tinkering with analog meters that i can't feel 20 microamps but a couple milliamps will make me jump.
The Human Body Model is the oldest and most commonly used model for classifying device sensitivity to ESD. The HBM testing model represents the discharge from the fingertip of a standing individual delivered to the device. It is modeled by a 100 pF capacitor discharged
through a switching component and a 1.5k Ωseries resistor into the component.
http://www.esda.org/assets/Uploads/documents/FundamentalsPart5.pdf
at 60 hz, 100 pf = 26.5 megohms, compared to which the 1.5K resistance is insignificant
so 500 KV / 26 megohms = 19 milliamps, a surely painful shock. 20 ma through the chest can stop your heart.
Were the helicopter's capacitance added to the lineman's i expect it'd be lethal.The field way of thinking also explains it - the suit being conductive makes an equipotential surface , reducing field strength in its immediate vicinity to zero.
So the two ways of thinking - electric field or capacitance - lead to the same result. Either mental model works for me.
Birds begin avoiding power lines around 40KV i think it tickles their feet.
  • #67
@jim hardy
Ah, that's a neat observation. I never realized that the duration of the spark (i.e. initial one time versus continuous) was related to AC vs DC.
  • Electrical Engineering