In summary, the catalogue of a relay lists the rated insulation voltage as 250V (IEC) and 300V (UL, CSA), without specifying if it is for AC or DC. The dielectric strength between coil and contact is 2500V, while between poles and contacts is 1500V. It is suggested to contact the manufacturer to verify if the relay will work for an application involving 230V DC across the pole. If the relay is only being used to discharge a capacitor through a resistor and not breaking current, it may work. However, if the load is inductive or the current exceeds the rating, it may not work. The relay can handle opening a 6V circuit at 100mA
  • #1
hanhao
20
0
what is Rated insulation voltage for relay?

On the catalogue of a relay, it says

"Rated insulation voltage (Ui) V 250 (IEC), 300 (UL, CSA)"

it doesn't say its AC or DC.

it also says

"Dielectric strength

(rms voltage)

Between coil and contact a V 2500
Between poles a V 2500

Between contacts a V 1500"

Lets say my application involves putting 230V DC across the pole of the relay, will it work?

For Rated insulation voltage, it doesn't says AC or DC.
 
Engineering news on Phys.org
  • #2
Probably won't work if you are opening a circuit under load.

Contact manufacture to verify if relay will or will not work.

Relay contacts that open in air usually won't open more than 60 or 80 volts DC when there is current through them.
Some relays that use magnets to deflect the arc can operate at higher voltages.

If are only using relay to discharge capacitor through resistor and not breaking current, relay may work.
 
  • #3
hanhao said:
Lets say my application involves putting 230V DC across the pole of the relay, will it work?

For Rated insulation voltage, it doesn't says AC or DC.

Isolation voltage. As long as your load in not inductive and the current it passes is within rating and all that, it will work.
 
  • #4
"Lets say my application involves putting 230V DC across the pole of the relay, will it work?"

Depends by what you mean by putting 230V DC across the pole of the relay.
If you mean that the pole is 350V DC above ground and you are only opening say 6 volt at say 100 mA, then it will should work.

If you mean that you are opening 230V DC at say 100 mA, then it probably won't work.

Let us know how you are actually operating the relay.

Good Luck
 

FAQ: What is Rated insulation voltage for relay?

1. What is the definition of rated insulation voltage for relay?

Rated insulation voltage for relay refers to the maximum voltage that can be applied to the relay without causing damage to its insulation system. It is an important factor in determining the reliability and safety of the relay.

2. How is rated insulation voltage determined for a relay?

Rated insulation voltage is determined by the manufacturer of the relay, based on the materials and design of the insulation system. It is tested and certified according to industry standards to ensure it can withstand the specified voltage without failure.

3. Why is rated insulation voltage important for relays?

Rated insulation voltage is important because it ensures the relay can safely and reliably operate within its designated voltage range. If the voltage exceeds the rated insulation voltage, it can lead to insulation breakdown and potential failure of the relay.

4. Is the rated insulation voltage the same for all relays?

No, the rated insulation voltage can vary depending on the type and design of the relay. For example, a high voltage relay may have a higher rated insulation voltage compared to a low voltage relay. It is important to check the specifications of the relay to determine its rated insulation voltage.

5. Can a relay operate at a voltage higher than its rated insulation voltage?

No, it is not recommended to operate a relay at a voltage higher than its rated insulation voltage. Doing so can cause damage to the insulation system and potentially lead to a malfunction or failure of the relay. It is important to always adhere to the specified rated insulation voltage for proper and safe operation of the relay.

Back
Top