hi dudes...
i m confuse about apparent, reactive and real power, please explain...any help wll be appreciated..thanks in advance
 
Last edited by a moderator:
Engineering news on Phys.org
  • #2
I'm not sure that "reactive power' has a meaning. Power refers to the rate of energy transfer and that works for AC or DC.
Reactance is a quantity that is used for AC circuits and no net energy transfer is involved. Energy is stored, temporarily, in a capacitor or an inductor during parts of the AC cycle but comes out in another part of the cycle. In the light of that, I would say that you can't actually have reactive power.

The power transferred in an AC circuit will be V I cos(θ) , where θ is the phase angle between V and I. Cos(θ) is the 'power factor'. For a power factor less than 1, there will be higher voltage or current for a given power. This will introduce higher losses or involve embarrassingly higher voltages than the equipment can handle - but I wouldn't have said that was actually reactive power.

I guess that V I would be what you refer to as "apparent power"

In a resonant circuit, you can have reactive energy which is built up in the reactive components as energy is supplied at the right frequency.

Does that make sense?
 
  • #3
The apparent power is a complex number, S=P+jQ. I'd think of it as active power is the energy that feeds the load. Reactive power can't be really be used to feed a load, though it stresses components and transmission lines. Therefore you have to dimension everything according to the apparent power. I don't know if I'm right that's just the way I think about it. Search for the power triangle on google and then it might be easier to understand.
 
  • #4
But isn't the definition of power rate of energy transfer? Energy in the reactive bits is not transferred anywhere. I think the two terms "apparent" and "reactive" are not very helpful and don't actually need to be used. 'VI' is a useful term, which is used everywhere and that would, presumably, be 'apparent power', I guess. This isn't worth losing sleep over as it's only a fringe term - possibly introduced by someone who wanted to 'help' students in some way. If it doesn't help then don't use it.
 
  • #5
I like the idea of looking at reactive power as energy that is simply stored and released with no net effect. It results in additional movement of current because energy is being stored, but no actual work is done other than expanding and collapsing a magnetic and/or electric field. That's why a power supply with a rating for 1000VA may only be able to supply 600W to a purely resistive load. That's how I've always looked at it and hopefully my understanding is sound.

I believe the term apparent is being used as a synonym for real power, the real component of the complex power vector, where the imaginary axis is the reactive component.
 
Last edited:
  • #6
There is a BIG difference between reactive, active and apparent power and it is why the terms were invented for AC circuits. One must be careful not mixing them with instantaneous power. In AC circuits, power is a function of time [itex]t[/itex] given by

[tex] p(t)=e(t)i(t)[/tex]
where [itex]e(t)[/itex] is the instantaneous voltage and [itex]i(t)[/itex] is the instantaneous current. Note that in DC, everything is constant, so instantaneous power is just power.

Now let us examine 3 basic cases for this instantaneous power:

The Resistor

Let us assume we have a resistor of linear resistance [itex]R[/itex] connected to a voltage source [itex]e(t)=E\cos{\omega t}[/itex] (i.e. a sinusoidal waveform of magnitude [itex]E[/itex] and angular frequency [itex]\omega[/itex]). Since the current in the resistor is in phase with the voltage, we get some current [itex]i(t)=I\cos{\omega t}[/itex] in the resistor. From the definition of [itex]p(t)[/itex] above, we get
[tex] p(t)=e(t)i(t)[/tex]
[tex] =E\cos{\omega t}\cdot I\cos{\omega t}[/tex]
[tex] =EI\cos^2{\omega t}[/tex]
[tex] =\frac{1}{2}EI(1+\cos{2\omega t})[/tex]
(the last step included the identity [itex]2\cos^2{\omega t}=1+\cos{2\omega t}[/itex])
Hence, we can express the instantaneous power of the resistor as 2 parts: a first part which is independent of time (mean value) and a second part which oscillates at twice the frequency. The active power [itex]P[/itex] is defined as the mean value of the instantaneous power
[tex]P=\frac{1}{2}EI[/tex]
Notice here the presence of the [itex] \frac{1}{2}[/itex], because [itex]E[/itex] and [itex]I[/itex] are the magnitudes of the cosines, not the RMS value. This is where the definition of RMS kicks in, since we know the power in DC (instantaneous or mean value, all the same) is
[tex]P=EI[/tex]
and we know for sinusoidal waveforms the RMS values are [itex]E_{RMS}=\frac{E}{\sqrt{2}}[/itex] and [itex]I_{RMS}=\frac{I}{\sqrt{2}}[/itex]. Hence, we get
[tex]P=E_{RMS}I_{RMS}[/tex]
for the sinusoidal waveforms of the resistor. We see the equivalence of the AC so-called active power with the power in DC. The RMS values in AC represent the values needed to perform the same amount of work in DC with a resistor. We can express this active power by using Ohm's law in other forms for the resistor
[tex]P=E_{RMS}I_{RMS}=RI_{RMS}^2=\frac{E_{RMS}^2}{R}[/tex]


The Inductor

This case is a bit trickier. Let us assume we have the same voltage source [itex]e(t)=E\cos{\omega t}[/itex] applied to an inductor of inductance [itex]L[/itex]. The current of an inductor is lagging by 90 degrees its voltage, so the current is [itex]i(t)=I\sin{\omega t}[/itex]
From the definition of [itex]p(t)[/itex] above, we get
[tex] p(t)=e(t)i(t)[/tex]
[tex] =E\cos{\omega t}\cdot I\sin{\omega t}[/tex]
[tex] =\frac{1}{2}EI(\sin{2\omega t})[/tex]
(the last step included the identity [itex]2\cos{\omega t}\cdot \sin{\omega t}=\sin{2\omega t}[/itex])
Here, we see a big difference from the case of the resistor. The mean value of instantaneous power is 0. Which means that energy is transferred back and forth within a cycle (actually twice within a period of [itex]e(t)[/itex]).

Even though the mean instantaneous power is 0, that doesn't mean we don't have current in the source necessary for the inductance (in practice, this current has to flow in the power lines, cables, etc.). Hence, we need a measure of this fictitious necessary power that draws AC current from the source. In a similar fashion as in the resistor [itex](p(t)=P+P\cos{2\omega t})[/itex], we can define this reactive power [itex]Q[/itex] as [itex]p(t)=Q\sin{2\omega t}[/itex], where [itex]Q[/itex] will be again given by
[tex]Q=\frac{1}{2}EI[/tex]
or
[tex]Q=E_{RMS}I_{RMS}[/tex]
These formulas are, of course, for the inductor. Then again, we could replace the last equation by using Ohm's law (in complex form)
[tex]Q=E_{RMS}I_{RMS}=L\omega I_{RMS}^2=\frac{E_{RMS}^2}{L\omega}[/tex]

The impedance

Since the capacitor case is relatively simple, let us now look at the impedance case, where we get an arbitrary phase difference [itex]\theta[/itex] between voltage and current waveforms. Again, let us assume we have the same voltage source [itex]e(t)=E\cos{\omega t}[/itex]. The current of the impedance will be of the form [itex]i(t)=I\cos{(\omega t-\theta)}[/itex]. So we will get for the instantaneous power
[tex] p(t)=e(t)i(t)[/tex]
[tex] =E\cos{\omega t}\cdot I\cos{(\omega t-\theta)}[/tex]
[tex] =EI\cos{\omega t}(\cos{\omega t}\cos{\theta}+\sin{\omega t}\sin{\theta})[/tex]
[tex] =EI(\cos^2{\omega t}\cos{\theta}+\cos{\omega t}\sin{\omega t}\sin{\theta})[/tex]
with the 2 identities mentioned earlier, we finally get
[tex] p(t)=\frac{1}{2}EI\cos{\theta}(1+\cos{2\omega t})+\frac{1}{2}EI\sin{\theta}(\sin{2\omega t})[/tex]
[tex] =P(1+\cos{2\omega t})+Q(\sin{2\omega t})[/tex]

We can see that in the general case (impedance), the active power in the last equation is now [itex]\frac{1}{2}EI\cos{\theta}[/itex] and the reactive power is now [itex]\frac{1}{2}EI\sin{\theta}[/itex]. Since both powers do affect the current that must be drawn from the AC source, there was also a name given for that power, which is the apparent power. Following the complex notation for the impedance, we can formulate this power as a complex power, which real part comes from active power [itex]P[/itex] and the imaginary part comes from [itex]Q[/itex]
[tex] \vec{S}=P+jQ[/tex]
[tex] S=\frac{1}{2}EI=E_{RMS}I_{RMS}[/tex]

**From an AC point of view, this is all very important. In order not to mix these powers, each one has a different unit (even though all equivalent to the SI unit W for power). Active power is in W, reactive power is in var (lower-case), which stands for volt-ampere reactive and apparent power is in VA (volt-ampere). The active power is the power that creates work (lift charges, heating, etc.). The reactive power is stored and restored power (in the form of electromagnetic field). The apparent power is the result of both powers, it is what you will measure in the end, by multiplying the RMS voltage and current. Hence, this is why you usually have ratings for transformers in VA, because depending on what the impedance (connected to it) is, you must not have more than a certain amount of current (RMS) in the conductors (in order for them not to overheat) and a certain amount of voltage (RMS) on the ends of the conductors (in order for the dielectric to withstand this voltage). Of course, there is always a margin for these (steady-state) values, but one has to understand that if there was a transformer rated 10W, that would mean I could connect 10W and whatever reactive power to it (such as 1Mvar). But the currents drawn from that load would melt the conductors right away... This is why the distinction in AC is important.

Sorry for the long post, perhaps only the last part is necessary.

M.
 
  • #7
Nice explanation, thanks for that.
 

FAQ: What is the difference between apparent, reactive, and real power?

What is apparent power and how is it different from reactive power?

Apparent power is the combination of real power (measured in watts) and reactive power (measured in volt-amps reactive or VARs). It is the total power that is being drawn from a power source. Reactive power, on the other hand, is the power that is required by certain types of loads, such as motors and transformers, to create and maintain magnetic fields. It is not actually consumed by the load, but instead it flows back and forth between the load and the power source.

How is apparent power calculated?

Apparent power can be calculated using the formula S = VI, where S is apparent power in volt-amps (VA), V is voltage in volts (V), and I is current in amps (A). This formula takes into account both real power and reactive power to give the total power being drawn from the power source.

Why is reactive power important to consider?

Reactive power is important to consider because it affects the efficiency and capacity of power systems. When there is a high demand for reactive power, it can lead to voltage drops and power outages. In addition, reactive power can also cause extra strain on power equipment and increase energy costs. Therefore, it is important for power companies to manage and control reactive power to ensure a stable and efficient power supply.

How is reactive power managed and controlled?

Reactive power can be managed and controlled through the use of devices called capacitors and inductors. These devices can either supply or absorb reactive power to balance the system and maintain a stable voltage. Power companies also use control systems and monitoring equipment to adjust and optimize the flow of reactive power as needed.

Can apparent power ever be greater than real power?

Yes, apparent power can be greater than real power in certain scenarios. This can happen when there are loads with a high demand for reactive power, such as motors and transformers. In these cases, the apparent power will be higher due to the addition of reactive power, even though the real power being consumed by the load is lower. This is why it is important to consider both apparent and reactive power when analyzing power systems.