Why Does My Vintage Single Phase Generator Produce No Power?

In summary, the conversation discusses a friend's generator that is not producing any power. The generator is a ?40-50 kVA, 240 V, single phase generator from the 1970s that is directly coupled to an engine. The internals of the generator include a large capacitor, a 40A bridge rectifier, and four heavy-wound coils. The wires are difficult to access and covered in dust, making it hard to determine the function of each component. The conversation also mentions a button marked 'excite' that seems to have no effect, as well as the possibility of the generator being self-excited and not having a battery. The participants suggest checking the capacitor and re-magnetizing the field with a battery.
  • #1
Guineafowl
791
383
A friend has a ?40-50 kVA, 240 V, single phase generator, of 1970s vintage, coupled directly to an engine. It was working fine but now produces no power at all. All the brushes and spring holders are fine, as are the fuses. I can't find a decent description/diagram of the internals, other than very basic animations of the principles of AC generation. Does anyone have any tips on what to check, or where to look for information?

Within the generator body is a large capacitor, a 40A bridge rectifier (which is good) and four heavy-wound coils (?tranformers). It's hard to see what goes where as the wires are hard to get to and covered in dust. Also, there's a button marked 'excite' which seems to make no difference, although I've metered it and it works as a SPST switch shorting two wires together. What are all these bits for? I did clean the excite switch once and got the generator working again, but only briefly, and I suspect it was just a coincidence.
 
Engineering news on Phys.org
  • #2
You might attract the attention of readers who have dabbled with these if you attach a photo or two of the generator's internals. :smile:
 
  • Like
Likes jim hardy and Averagesupernova
  • #3
Is this a self exciting generator? In other words, does it rely on the residual magnetism to build up enough of an output to provide current to the field? Is there provisions for a battery? I would also assume there is some type of voltage regulation on a unit of this size.
 
  • #4
Have you checked the capacitor?
Use an ohm-meter set to high scale at least RX1K . You should see an initial low reading that quickly increases to infinite, and reversing the leads should give a reading that's initially negative then increases to infinite.

That's because the ohm meter charges the capacitor to a volt or two.

The capacitor should hold that charge for several minutes - check this way... When reading reaches infinite remove one meter lead, wait some time and reconnect it. Reading should remain infinite, not dip.
That's a "Poor Man's Capacitor Check" .

Really it sounds like you have a broken wire that's intermittent. Examine them carefully anyplace they might flex in the wind, and right where they attach to something rigid. Mechanical things subject to vibration tend to fail where there's a change of cross section.
 
  • #5
Averagesupernova said:
Is this a self exciting generator? In other words, does it rely on the residual magnetism to build up enough of an output to provide current to the field? Is there provisions for a battery? I would also assume there is some type of voltage regulation on a unit of this size.
I'm guessing it's self-excited, as there's no provision for a battery. The voltage output appears fairly well coupled to engine speed, i.e. Not regulated, but I'm not sure. It's an old generator.
 
  • #6
jim hardy said:
Have you checked the capacitor?
Use an ohm-meter set to high scale at least RX1K . You should see an initial low reading that quickly increases to infinite, and reversing the leads should give a reading that's initially negative then increases to infinite.

That's because the ohm meter charges the capacitor to a volt or two.

The capacitor should hold that charge for several minutes - check this way... When reading reaches infinite remove one meter lead, wait some time and reconnect it. Reading should remain infinite, not dip.
That's a "Poor Man's Capacitor Check" .

Really it sounds like you have a broken wire that's intermittent. Examine them carefully anyplace they might flex in the wind, and right where they attach to something rigid. Mechanical things subject to vibration tend to fail where there's a change of cross section.
I didn't check the cap, but my meter does measure capacitance. I'll do that as well as your suggestion. The rectifier appears to take in 140V AC and put out about 100V DC. Would it be reasonable to assume the rectifier and cap are to provide DC for the field coils?
 
  • #7
Oh, and thanks for your replies.
 
  • Like
Likes jim hardy
  • #8
Guineafowl said:
Would it be reasonable to assume the rectifier and cap are to provide DC for the field coils?

Yes. Reasonable but not guaranteed. Rectifier could be overvoltage protection for the field.

At standstill, try re-magnetizing the field with perhaps a lantern battery or car battery charger between the brushes... just touch it. If you get a spark on disconnect that's good, you have inductance.

We had a 150 kva generator that we had to occasionally re-magnetize that way . We had access to field terminals at a cabinet so did not have to get near moving parts. A 9v transistor radio battery did the job.

<<Use common sense precautions around rotating machinery - no long sleeve shirt, no necktie, orient hands so contact will push fingers free not pull them in.>>>
 
  • Like
Likes Dr.D
  • #9
jim hardy said:
Yes. Reasonable but not guaranteed. Rectifier could be overvoltage protection for the field.

At standstill, try re-magnetizing the field with perhaps a lantern battery or car battery charger between the brushes... just touch it. If you get a spark on disconnect that's good, you have inductance.

We had a 150 kva generator that we had to occasionally re-magnetize that way . We had access to field terminals at a cabinet so did not have to get near moving parts. A 9v transistor radio battery did the job.

<<Use common sense precautions around rotating machinery - no long sleeve shirt, no necktie, orient hands so contact will push fingers free not pull them in.>>>
I can access the rectifier quite safely - could I connect a car battery + and - to the recifier + and - and remagnetise that way?
 
  • #10
Guineafowl said:
I can access the rectifier quite safely - could I connect a car battery + and - to the recifier + and - and remagnetise that way?
That should work. Of course observe + to + . Just touch the wires for if it's running it should come up to voltage quickly.
 
  • Like
Likes Guineafowl
  • #11
jim hardy said:
Just touch the wires for if it's running it should come up to voltage quickly.
Try it first at standstill, of course.

Do you have pictures ? Just get them on your computer and use "upload" button.
I use Paint to resize them about 600 pixels wide and save as jpg .

Curious what that "excite" button is for.
 
  • #12
jim hardy said:
Try it first at standstill, of course.

Do you have pictures ? Just get them on your computer and use "upload" button.
I use Paint to resize them about 600 pixels wide and save as jpg .

Curious what that "excite" button is for.
I'll take some next time I'm at my mate's place. The excite button has two wires connected to it with a resistance of 9.5 ohms between them. It shorts these together when pressed.
 
  • #13
The generator is sorted - we stripped it down to reveal a hidden area with various boxes and terminals which I assume was some sort of automatic voltage regulation kit. Amongst the components was a double capacitor unit with two taps and a common ground which was shorted. I replaced this (decoupler?), and we cleaned up all the terminals, and the genny has run without missing a beat since.

I guess the cap had nothing to do with the fault, as the rig would work sometimes and sometimes not - often the signature of a poor connection as suggested.

Anyway, we celebrated with a nip or two of Balvenie single malt from the local distillery and enjoyed the feeling of, "refer servicing to authorised personnel only - my arse! (Or ass if you prefer)".

Thanks for all your advice.
 
  • Like
Likes sophiecentaur, Asymptotic, dlgoff and 2 others
  • #14
Guineafowl said:
Anyway, we celebrated with a nip or two of Balvenie single malt from the local distillery and enjoyed the feeling of, "refer servicing to authorised personnel only - my arse! (Or ass if you prefer)".

I enjoy that feeling from two perspectives.
1. Beating the system. Or if you prefer, "Civil Disobedience"* style protest of today's 'Throwaway Paradigm' ", which keeps consumers in perpetual debt.

2. You breathed new life into an old machine of which once upon a time somebody was very proud. See @dlgoff's signature...

*"Civil Disobedience" may not be an everyday phrase in UK - Henry Thoreau was an eccentric American writer of 19th century whose essays still inspire modern day protesters. I think he was quietly removed from US high school curricula in 1970's.old jim
 
Last edited:
  • Like
Likes sophiecentaur, Asymptotic, Guineafowl and 1 other person
  • #15
jim hardy said:
I enjoy that feeling ...
Beating the system. Or if you prefer, "Civil Disobedience*
I know that's right. :approve:
 
  • Like
Likes jim hardy and Guineafowl

FAQ: Why Does My Vintage Single Phase Generator Produce No Power?

What is a single phase generator?

A single phase generator is a type of electrical generator that produces alternating current (AC) with only one single waveform. It is typically used for smaller power applications and residential or light commercial use.

How do I know if my single phase generator is experiencing a problem?

If your single phase generator is not producing any electricity, or if the output voltage is unstable or too low, it may be experiencing a problem. Other signs of a problem can include unusual noises, excessive vibration, or smoke/odor coming from the generator.

What are the most common problems with single phase generators?

The most common problems with single phase generators include issues with the fuel system, such as clogged fuel filters or stale fuel, as well as problems with the electrical components like the voltage regulator or capacitors. Overloading the generator or improper maintenance can also lead to problems.

How can I troubleshoot a problem with my single phase generator?

The first step in troubleshooting a single phase generator problem is to check the basics, such as fuel levels, oil levels, and any visible damage. Then, you can test the electrical components with a multimeter and check for any loose connections. If the issue persists, it is best to consult a professional.

How can I prevent problems with my single phase generator?

To prevent problems with your single phase generator, it is important to perform regular maintenance, such as changing the oil and filters, checking the fuel system, and keeping the generator clean and dry. It is also important to avoid overloading the generator and to follow the manufacturer's instructions for proper use and storage.

Similar threads

Replies
12
Views
4K
Replies
1
Views
2K
Replies
4
Views
9K
Replies
1
Views
6K
Replies
17
Views
11K
Replies
2
Views
5K
Back
Top