  • #1
qbnchopper
3
0
Gents, Ladies,

I have a design where I have:

AC -> RCD -> UPS (dual conversion apparently) -> PowerStrip -> Equipment

If I induce an Earth leakage fault downstream of the UPS (i.e. at the powerstrip), the RCD upstream of the UPS trips.

The UPS is in the "normal" not bypass state, and the UPS is supposedly dual conversion.

I cannot understand how this can happen unless the UPS is not true dual conversion !

Can someone confirm or debunk my understanding here please ?

Q
 
Engineering news on Phys.org
  • #2
Another name for the RCD is GFCI, BTW. Does the GFCI trip if the UPS is in bypass mode too? I agree that if it really has switching power supply transformer isolation between the AC Mains with the GFCI, and the load where you introduce the ground fault, that the GFCI should not see anything different, other than a slight change in its AC load (no common-mode load change).

On second thought, it might see a common-mode load change because of the winding-to-winding capacitance of the switching transformer. Does it only trip the GFCI if you introduce a hard fault to ground (like with a wire)? What if you use a 10kOhm resistor instead? Try some resistor faults right at the GFCI to see where its sensitivity threshold is, and then do the same downstream of the UPS. It may just be the capacitive common-mode transient from a hard wire fault downstream of the UPS that is tripping the GFCI.
 
Last edited:
  • #3
Berkeman,

Thanks for your reply ! I new that the RCD was called something else - but couldn't remember ...

Being an Aussie - RCD = Aussie; GFCI = American ? :-)

In bypass mode, the RCD/GFCI trips as expected.

In normal mode, the RCD/GFCI trips (not really as expected - but noting your second though!)

I am using a tool to induce the Earth leakage fault - it allows me to change the mA-erage to see how quickly an RCD responds. I came across this situation when I was testing to see if the UPS had anything in it to cope with a Earth leakage fault (i.e an experiment) ...
Anyway, I'll look at the tool and also try as you suggest ...

Thanks !
 
  • #4
Glad to help, qbnchopper, and welcome to the PF. It's a great place.

I'd really be interested in the results of your experiments. Your initial test results are a bit non-intuitive for me as well.
 
  • #5
The UPS loops the ground circuit thru to the UPS outlet.
I'm not entirely certain, but I think they also loop the neutral line thru.
If so, then at some point in a normal mains circuit the neutral and ground lines have a common bond.
Then a leakage current from the UPS hot to ground will loop back thru the neutral to complete the circuit. The unbalanced current in the RCD (GFCI) neutral will cause the breaker to trip.
 
  • #6
Notime,

Thanks and Interesting ... in my case the Earth and neutral are not bonded ... however, on another problem that I am working that is related, earth/neutral are bonded upstream of the ups ... have to have a think about this ...

Q
 

FAQ: Why Does RCD Trip with Earth Leakage Fault Downstream of UPS?

What is RCD upstream of UPS tripping?

RCD stands for Residual Current Device, which is a safety device that detects and interrupts electrical faults in a circuit. UPS, or Uninterruptible Power Supply, is a backup power supply that provides electricity to critical equipment in case of a power outage. RCD upstream of UPS tripping refers to the situation where the RCD detects a fault and interrupts the power supply before it reaches the UPS.

Why does RCD upstream of UPS tripping occur?

RCD upstream of UPS tripping can occur due to a variety of reasons, such as a fault in the electrical wiring, a malfunctioning appliance, or a ground fault. It can also happen when the RCD is not properly sized or designed to handle the load of the UPS.

What are the potential consequences of RCD upstream of UPS tripping?

RCD upstream of UPS tripping can lead to power outages and disruptions in critical equipment, which can result in financial losses and safety hazards. It can also cause damage to the electrical system and result in costly repairs.

How can RCD upstream of UPS tripping be prevented?

To prevent RCD upstream of UPS tripping, it is important to ensure that the RCD is properly sized and installed by a qualified electrician. Regular maintenance and testing of the RCD and electrical system can also help identify and address any potential issues before they lead to tripping.

What should I do if RCD upstream of UPS tripping occurs?

If RCD upstream of UPS tripping occurs, it is important to immediately turn off all equipment connected to the UPS and contact a qualified electrician to inspect the electrical system. It is also important to have a backup plan in place to maintain critical operations in case of a prolonged power outage.

Similar threads

Replies
4
Views
7K
Back
Top