In summary, the limited power output and maximum operating voltage of Mineral Insulated heating cables is due to the dielectric strength of the insulation, which is higher than the current voltage limit. If power is supplied over the rated maximum, the cable will fail. The dielectric strength can be increased by melting the insulation, but the melting point is high and the cable has a limited temperature gradient across the insulation, limiting the rate of heat transfer.
  • #1
amrmohammed
45
0
Hello

Why does Mineral Insulated heating cables have such limited power output per feet and maximum operating voltages?
I thought it has to do with the dielectric strength of the MgO, that is used as an insulation in the coaxial cable, but the dielectric strength for MgO is higher than the current voltage limit. The highest voltage limit I read about was around 2 KV and the dielectric strength of MgO is around 10-35 KV/mm. What happens if you supply power over the rated maximum?
 
Engineering news on Phys.org
  • #2
What's thermal conductivity of MgO?
 
  • #3
45–60 W/m·K (Wikipedia)
 
  • #4
Does the melting temperature of MgO establish an upper limit to operating temperature?
 
  • #5
No it doesn't, MgO has a very high melting point (~2,800 °C)
 
  • #6
amrmohammed said:
No it doesn't
And, that limits the temperature gradient that can be maintained across the insulating annulus, does it not?
 
  • #7
Bystander said:
that limits the temperature gradient that can be maintained across the insulating annulus

Would you please elaborate? how does high melting temperature of the MgO in the annulus be a limitation to the maximum temperature gradient?
 
  • #8
What's the purpose of a non-conducting solid insulator in the cables?
 
  • #9
To electrically insulate the heating element from the outer metallic sheath
 
  • #10
How well can it perform that function as a melt?
 
  • #11
it will fail, but it has a very high melting point
 
  • #12
amrmohammed said:
it will fail, but it has a very high melting point
It sets an absolute upper limit to the temperature gradient that can be maintained across the insulation. (The practical limit is much less due to increased electrical conductivity of MgO as temperature increases.)
What does that limit to the temperature gradient imply as far as rate of heat transfer (power)?
 
Last edited:
  • Like
Likes amrmohammed
  • #13
The limitation in temperature gradient should limit the rate of heat transfer, as additional power will increase the temperature of the heating wire and thus exceed the maximum temperature gradient to the surrounding. but does the change in the electric resistivity of MgO with increasing temperature that significant? most of the available heating cable have a maximum of only 600 V and MgO have a very high dielectric strength!
 
  • #14
Please refer to this pdf file. The resistivity of MgO do decrease with temperature but it is still very high.
resistiity.png


and in http://www.emersonindustrial.com/en-US/documentcenter/EGSElectricalGroup/products_documents/heating_cables/commercial_heating_cables/commercial_pipe_tracing/mi_comm_pipe_trace_cable/308-SA-001_Mineral_Insulated_heater_cable_lit.pdf , the resistivity of the heating wire is presented and it is very small that it will always be much less than the resistivity of MgO insulation (using the graph above) so I though there should be no worry from short circuit, however they set a maximum temperature of 350 C and maximum voltage of 600 V. What is wrong with my understanding of this data and graphs?
 
Last edited by a moderator:
  • #15
  • Like
Likes amrmohammed
  • #16
The lifetime of a resistor or fuse is reduced at higher temperatures.
For a resistive heating element, the cost of replacement following failure can be the factor that requires limits to the operating temperature.
 
  • #17
I can't find any mention here,m of the effect of having a hot cable on its environment. (Setting fire to floor joists and melting nearby PVC cabling etc.) Surely that must be relevant. Or is it there 'by implication' in the rest of the spec of the cable?
 
  • #19
Yeah. I guess the design of the heater would take that into account. If the cable gets red hot then it would be mounted safely, by design.
 
  • #20
Baluncore said:
The lifetime of a resistor or fuse is reduced at higher temperatures.

That will limit the operating temperature (different from temperature gradient across the insulator that @Bystander mentioned), how is that related to the limit on maximum operating voltage? I guess the voltage limit should be somehow related to the dielectric strength of the insulator or the electrical properties of one of heating cable's components.

sophiecentaur said:
If the cable gets red hot then it would be mounted safely

That is true and there is a maximum sheath temperature set and published by IEEE. However, in many applications this is not a concern (like underground pipes and downhole oil heating) and the heating cable still have the same limit on the operating voltage and power output.
 
  • #21
Power is transmitted through coaxial conducting cables that is insulated by a dielectric material, could capacitance play any rule?
 
  • #22
amrmohammed said:
Power is transmitted through coaxial conducting cables that is insulated by a dielectric material, could capacitance play any rule?
Capacitance only becomes a problem above kHz frequencies. It is not important at 50Hz or 60Hz power distribution frequencies. Parallel capacitance is probably an advantage at power frequencies as it will slightly improve the power factor of the normally inductive grid.

amrmohammed said:
That will limit the operating temperature (different from temperature gradient across the insulator that @Bystander mentioned), how is that related to the limit on maximum operating voltage? I guess the voltage limit should be somehow related to the dielectric strength of the insulator or the electrical properties of one of heating cable's components.
You seem confused.
The thread title is “Why Mineral Insulated Heating Cables have power output limit? ”
Maximum operating voltage determines electrical insulation requirements.
The durability requirement is determined by the maximum specified operating temperature of the inner conductor.

The mineral insulation needs to be both thermally conductive and electrically resistive.
 
  • Like
Likes amrmohammed
  • #23
Baluncore said:
Maximum operating voltage determines electrical insulation requirements.

So to sum up, current commercial heating cables handle a maximum of 2 kV, because the currently available insulation (MgO) can not insulate higher voltages in field conditions?
 
  • #24
... and conductors (heating elements) with high enough resistance to function as heating elements (10-100 W/m) at applied voltages greater than 2 kV are too fragile.
 
  • Like
Likes amrmohammed

Related to Why Mineral Insulated Heating Cables have power output limit?

1. Why do mineral insulated heating cables have a power output limit?

Mineral insulated heating cables have a power output limit because of their construction and the materials used. These cables are made of a heating element, usually nickel-chromium alloy, surrounded by magnesium oxide insulation and enclosed in a metal sheath. The heating element and insulation have a specific resistance, which restricts the amount of current that can flow through the cable and, therefore, limits the power output.

2. What is the maximum power output of mineral insulated heating cables?

The maximum power output of mineral insulated heating cables can vary depending on the manufacturer and specific design of the cable. However, in general, these cables have a maximum power output of around 30 watts per linear foot.

3. Can the power output limit of mineral insulated heating cables be increased?

No, the power output limit of mineral insulated heating cables cannot be increased. These cables are designed and tested to operate safely and efficiently within their specific power output range. Increasing the power output could cause the cable to overheat and potentially lead to failure or damage.

4. Are there any safety concerns related to exceeding the power output limit of mineral insulated heating cables?

Yes, exceeding the power output limit of mineral insulated heating cables can be unsafe. These cables are designed to operate within a specific temperature range to ensure safe and efficient heating. Exceeding the power output limit can cause the cable to overheat, potentially leading to damage or fire hazards.

5. Are there any alternatives to mineral insulated heating cables that do not have a power output limit?

Yes, there are alternative heating cables, such as self-regulating or constant wattage cables, that do not have a power output limit. However, these cables may have other limitations or requirements, and it is essential to consult with a professional to determine the best option for your specific heating needs.

Similar threads

  • Electrical Engineering
2
Replies
38
Views
2K
  • Electrical Engineering
Replies
8
Views
1K
  • Electrical Engineering
Replies
19
Views
2K
  • Electrical Engineering
Replies
10
Views
2K
  • Electrical Engineering
Replies
10
Views
1K
  • Electrical Engineering
Replies
10
Views
4K
  • Electrical Engineering
Replies
9
Views
3K
  • Electrical Engineering
Replies
11
Views
2K
  • Electrical Engineering
Replies
1
Views
2K
Replies
4
Views
4K
Back
Top