ZigZag transformer and harmonics

In summary, the conversation discussed the use of zig zag connections on the secondary side of a transformer to prevent triplen harmonics from flowing further up the power system. The pdf provided in the conversation explains how the triplen harmonics, when in phase with each other, can be cancelled out in a zig zag connection, but only if they are real currents and not just mathematical identities. This may cause confusion when considering the presence of other harmonics, such as 5th harmonics, in the current waveform.
  • #1
KraakeCrest
18
2
Hi again,

Can/are zig zag connections used on the secondary side to avoid triplen harmonics flowing further up the power system? Let's say 3rd harmonics are flowing up the power system from some loads connected to phases a,b,c and the neutral. Since 3rd harmonic are all in phase, the ampere-turn created will cancel in a zig zag connection and thus not couple to the primary and further up the power system?

This pdf: http://static.schneider-electric.us...ansformers/Harmonic Mitigating/7400DB0301.pdf says on page 12 and 13:
"With all of the triplen harmonics in phase with each other, by vector analysis, the triplen harmonic currents produce ampere-turn fluxes that cancel each other such that no currents are induced in the primary winding. For this to work, the triplen harmonics must be real currents and not mere mathematical identities derived by the Fourier Transformation."

The last sentence in bold kind of confuses me.
zig.png
 
Engineering news on Phys.org
  • #3
Nice post @jim hardy , so from that post if I understand correctly, you can use a zig zag connection as secondary in a transformer to prevent triplen harmonics from coupling magnetically back to the primary.

But I am still alittle confused about the sentence in the PDF: "For this to work, the triplen harmonics must be real currents and not mere mathematical identities derived by the Fourier Transformation."

So if the current caused by the load contains fundamental + 3rd AND 5th harmonic, this would not work because the waveform is not a pure 3rd harmonic waveform? Hmm..
 

Related to ZigZag transformer and harmonics

1. What is a ZigZag transformer?

A ZigZag transformer is a type of transformer that is designed to provide a neutral connection for three-phase electrical systems. It consists of three interconnected single-phase transformers, with the secondary windings connected in a zigzag pattern. This allows for the neutral connection to be created without the need for a separate transformer or grounding device.

2. How does a ZigZag transformer reduce harmonic distortion?

A ZigZag transformer can reduce harmonic distortion by providing a path for the harmonic currents to flow back to the source. The zigzag configuration of the transformer allows the harmonic currents to cancel each other out, reducing the overall harmonic distortion in the system.

3. What are harmonics and how do they affect electrical systems?

Harmonics are electrical currents or voltages that have frequencies that are integer multiples of the fundamental frequency of the system. They are caused by non-linear loads, such as computers and variable speed drives. These harmonics can cause issues in electrical systems, such as overheating of equipment and interference with communication systems.

4. How can harmonics be measured in a system?

Harmonics can be measured using a power quality analyzer. This device measures the voltage and current waveforms and calculates the levels of harmonics present in the system. It can also provide information on the type and severity of the harmonics.

5. Can a ZigZag transformer be used in single-phase systems?

Yes, a ZigZag transformer can be used in single-phase systems as well. In this case, it is used to provide a neutral connection for unbalanced loads, where the neutral is required to carry the difference in current between the phases. It can also help to reduce harmonic distortion in single-phase systems.

Similar threads

  • Electrical Engineering
Replies
13
Views
7K
  • Electrical Engineering
Replies
4
Views
9K
  • Electrical Engineering
Replies
20
Views
3K
  • Electrical Engineering
Replies
16
Views
3K
  • Electrical Engineering
Replies
3
Views
2K
  • Electrical Engineering
Replies
11
Views
4K
  • Electrical Engineering
2
Replies
40
Views
20K
Replies
4
Views
2K
  • Electrical Engineering
Replies
1
Views
1K
Replies
64
Views
5K
Back
Top