Zone heating with a single furnace

  • Thread starter mheslep
  • Start date
  • Tags
    Heating
In summary, the conversation discusses a two-story residence with separate basement and attic gas forced air furnaces-chillers. The basement furnace is a high efficiency hybrid heat pump/aux gas heat, while the attic unit is less efficient and only uses gas. The house has older insulation and construction, resulting in a heat loss of 110,000-120,000 btuh. By improving the insulation, the heat loss can be reduced to 60,000 btuh. The conversation also explores the possibility of eliminating the attic unit and using a two-zone control system with one heat source. However, this may result in higher humidity levels. Solutions for this issue are suggested, such as using a controller with two thermostat inputs and one HVAC unit output
  • #1
mheslep
Gold Member
364
729
Given: a two-story residence currently with separate basement and attic gas forced air furnaces-chillers. The basement furnace is a recently updated high efficiency (96%) hybrid heat pump/aux gas heat at around 80,000 btuh (out); the attic unit is much less efficient and maybe 60-70,000 btuh (out), gas only. The home insulation and construction is oldish - walls, windows, etc. With the house as is, a Model J analysis tells me the current total house heat loss is ~110,000-120,000 btuh. In looking at a serious improvement in the insulation - walls, new windows, R-30 attic - it appears as if I could easily bring down the loss to ~60,000 btuh. The heat gain numbers present a similar case in that the entire house, well insulated, could be supplied by just the basement chiller equipment.

In that case, I'm wondering if I could find away to stop using the older, more expensive attic furnace and chiller, along with its duct system that runs in the outside ventillated ~ambient attic space. I'd especially like to know that answer before replacement time of the old attic unit anyway at end of life in 3-5 years. Currently the basement unit duct system supplies just the basement and the first floor. I understand that to maintain comfort in all rooms of a such a multi-story house, it will need at least a two zone control system. How might that be done with one heat source? I'm aware of some controlled damper solutions, but I also read, vaguely, about over heating or freezing problems caused by damper on/off instead of furnace-chiller on/off. Is there no answer but continuing to run the attic unit, and having to replace it in a few years?
 
Engineering news on Phys.org
  • #2
If you have a good location where you can cross-connect the two systems, you'll have a vastly larger ductwork system than a single unit was designed-for and as a result, when feeding air to either level, you'll have plenty of airflow to avoid the problems typically seen with zoning. You'll create a new problem, though, which you may or may not care about: your cooling supply air temperature will be too warm to adequately dehumidify the space and your house will be more humid than is typically designed-for.

Try browsing smarthome.com for some ideas on solutions. Basically, though, you get a controller with two thermostat inputs and one HVAC unit output plus multiple damper outputs (you can actually slave all of the dampers for each zone to a single output). The controller decides whether/when to heat/cool and sets the dampers appropriately to send air where it needs to go.
 
  • #3
russ_watters said:
If you have a good location where you can cross-connect the two systems, you'll have a vastly larger ductwork system than a single unit was designed-for and as a result, when feeding air to either level, you'll have plenty of airflow to avoid the problems typically seen with zoning. You'll create a new problem, though, which you may or may not care about: your cooling supply air temperature will be too warm to adequately dehumidify the space and your house will be more humid than is typically designed-for.

Try browsing smarthome.com for some ideas on solutions. Basically, though, you get a controller with two thermostat inputs and one HVAC unit output plus multiple damper outputs (you can actually slave all of the dampers for each zone to a single output). The controller decides whether/when to heat/cool and sets the dampers appropriately to send air where it needs to go.
Thanks russ_watters. Regarding the humidity problem, the issue there, if I understand correctly, is that the humidity tied to vent outlet air temperature, and that by using a larger duct system on a single chiller the outlet air temperature must inevitably increase, and any increase will raise the humidity over what it would have been previously with a smaller duct system?
 
  • #4
Correct. A psychrometric chart will tell you the resulting relative humidity from a certain dew point. http://docs.engineeringtoolbox.com/documents/816/psychrometric_chart_29inHg.pdf

Room (dry bulb) temperature is at the bottom. Dew point temperature is horizontally across the chart. When you cool air, it becomes saturated, so the supply air temperature is roughly equal to the dew point (plus a degree or two due to heat gain in the duct and inefficiency of the coil). Where the dew point line and the dry bulb temperature line cross, you can read the RH. For example, if the room temperature is 75F and the dew point (supply air temperature) is 55F, the resulting RH is 51%.
 
Last edited:

Related to Zone heating with a single furnace

What is zone heating with a single furnace?

Zone heating with a single furnace is a heating system that divides a home or building into separate zones, with each zone having its own thermostat and control. This allows for different areas of the building to be heated to different temperatures, providing customized comfort and potentially saving energy and money.

How does zone heating with a single furnace work?

A single furnace is used to heat the entire building, but dampers are installed within the ductwork to control the flow of heated air to different zones. Each zone has its own thermostat, which signals the furnace to turn on and off based on the desired temperature for that specific area.

What are the benefits of zone heating with a single furnace?

Zone heating with a single furnace can provide more precise temperature control, allowing for different areas of the building to be heated to different temperatures. This can lead to energy and cost savings, as well as increased comfort for individuals who prefer different temperatures.

Are there any drawbacks to zone heating with a single furnace?

One potential drawback of this system is that it can be more expensive to install, as it requires additional equipment and ductwork modifications. It also relies on proper installation and maintenance to ensure that the heated air is evenly distributed throughout the building.

Can I retrofit my current furnace for zone heating?

In some cases, it may be possible to retrofit an existing furnace for zone heating. However, this will depend on the specific furnace and ductwork setup, and it is best to consult with a heating professional to determine if this is a feasible option for your home or building.

Similar threads

Replies
23
Views
7K
Replies
1
Views
4K
Replies
7
Views
3K
  • Mechanical Engineering
Replies
2
Views
13K
  • Engineering and Comp Sci Homework Help
Replies
9
Views
7K
Replies
4
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
12
Views
2K
  • Introductory Physics Homework Help
Replies
1
Views
2K
  • Thermodynamics
Replies
4
Views
3K
  • General Discussion
Replies
30
Views
5K
Back
Top