Arcing - What affects size of arc when switch is opened?

  • Thread starter Thread starter Crazyhorse2882
  • Start date Start date
  • Tags Tags
    Arc Switch
AI Thread Summary
The size of an electrical arc when a switch is opened is influenced by the voltage, current, and inductance in the circuit. Arcing occurs when there is a load or resistance present, as an open circuit without resistance does not generate an arc. When a main breaker is closed while individual circuits are open, there is voltage but no current, resulting in no arcing. Medium voltage switches are categorized into "no load disconnect" and "load disconnect," with interlocking mechanisms to prevent operation under load conditions. Understanding these principles is essential for safe electrical system design and operation.
Crazyhorse2882
Messages
20
Reaction score
0
When an electrical circuit is opened or closed there is an arc between the terminals/buss that the switch or breaker is connecting or disconnecting and the arc is greater depending on the amount of voltage. My question is, is the arc greater when there is a resistance/load on the circuit? I'm guessing yes, but what is the effect and how could you calculate it?
 
Engineering news on Phys.org
You have to consider the whole circuit to determine that.
In general, inductances (especially coils), large switching voltages and large currents will increase the amount of arcing you get.
 
Crazyhorse2882 said:
... is the arc greater when there is a resistance/load on the circuit? ...

Without a resistance/load, you wouldn't have a circuit in the first place, and therefore wouldn't have an arc at all.
 
So then if a main breaker was closed outside of a building feeding equipment inside the building but their individual circuits were open then there would be no arc as that breaker closed? There would be voltage but no current and my understanding is that it will arc
 
Crazyhorse2882 said:
So then if a main breaker was closed outside of a building feeding equipment inside the building but their individual circuits were open then there would be no arc as that breaker closed?
That is correct.
There would be voltage but no current and my understanding is that it will arc
No, it will not arc.
 
To emphasize this point - for medium voltage switches - there are two general classes "no load disconnect" and "load disconnect" - The no load types are ideally interlocked ( often literally with locks and keys - ref Kirk Key) - with the load side circuit breaker. The Load side circuit breaker must be open - to get the key that allows the line side "no load" switch to be operated ( opened or closed).
TO feed a transformer a MV switch used on the primary is technically a load break switch (it will have an arc chute & arcing contacts- separate form the main contacts) , but only rated to interrupt the magnetizing current of the transformer it feeds - so you still see the interlocking scheme.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...