Armature Reaction Drop: Synchronous Generator Explained

In summary, synchronous generator armature reaction causes a 'drop' in generated voltage. It is different from the leakage reactance of stator windings. The way to visualize it is to freeze-frame your thinking. Armature amp-turns will either aid or oppose field amp-turns. So they'll add to or subtract from field, affecting terminal volts just as if they were an internal impedance. Look up 'Synchronous Impedance' for more information. In case of unity pf, armature amp-turns neither add to nor subtract from the field amp turns. They just distort the field amp turns. And if they enhance or weaken field flux at other power factors, this will
  • #1
cnh1995
Homework Helper
Gold Member
3,483
1,164
In synchronous generator, how does armature reaction cause a 'drop' ? How is it different from the leakage reactance of stator windings? I can't visualize it..Please help..
 
Last edited by a moderator:
Engineering news on Phys.org
  • #2
The way to visualize it is to freeze-frame your thinking. Stop the rotor with its pole centered underneath a phase winding and think of it as DC.
Armature amp-turns will either aid or oppose field amp-turns.
So they'll add to or subtract from field, affecting terminal volts just as if they were an internal impedance
Look up "Synchronous Impedance"
 
  • #3
jim hardy said:
The way to visualize it is to freeze-frame your thinking. Stop the rotor with its pole centered underneath a phase winding and think of it as DC.
Armature amp-turns will either aid or oppose field amp-turns.
So they'll add to or subtract from field, affecting terminal volts just as if they were an internal impedance
Look up "Synchronous Impedance"
In case of unity pf, armature amp-turns neither add to nor subtract from the field amp turns. They just distort the field amp turns. And if they enhance or weaken field flux at other power factors, this will reduce the 'generated emf'. What I read in book was 'part of generated emf is used to overcome the armature reaction reactance'. That means generated emf is constant. But with reactive loads, its not true because some part of armature amp turns enhance or weaken the field amp turns. Is there anything similar to 'back emf' that is induced in the armature windings due to armature reaction? What does the term 'drop' mean in this context? Is it reduction in the generated voltage or a part of it being used to overcome synchronous reactance? If it is later, how does that reactance work??
 
  • #4
cnh1995 said:
Is it reduction in the generated voltage or a part of it being used to overcome synchronous reactance? If it is later, how does that reactance work??
Armature reaction and synchronous reactance are two names for the same thing, and reflect two ways of thinking about it.
The math works out nicely to treat it as an internal reactance, you'll probably see it treated that way in your books and on phasor diagrams.

Let's really simplify our thinking down to a synchronous machine with a one turn armature and a permanent magnet rotor.
We'll allow the complication that the rotor is machined to produce sine shaped flux, though.
Recall that voltage and flux have a derivative/integral relationship meaning our sine shaped flux gives a cosine shaped voltage
because e = - n*dΦ/dt
and cosine is 90 degrees out of phase with sine. That's a quarter cycle.

so--- peak voltage appears at the flux zero crossing
and zero voltage appears at the flux peak
because of that sine-cosine relation.

Do we all accept that unity pf current is in phase with terminal voltage ?
and zero pf current is 90 degrees ahead or behind it ?
............

We'll make our simple one turn machine with only one pole pair so electrical and mechanical degrees are the same, 90 deg = ¼ turn.

Okay,
please -
pardon my crude sketch i just don't do well with computers.

The circles are my one-turn armature windings. I've freeze-framed my thinking as mentioned earlier, so these would be like high speed photographs.
one_turn_machine.jpg

Left sketch:
Flux from armature zero pf(real) current is perpendicular to flux from field
so there is little interaction beyond a phase shift, and that's why there is a power angle.
At this instant, zero pf current is zero so it does nothing.

Right sketch:
A quarter turn later (or earlier) when unity pf (real?) current is zero
and reactive(zero pf) current is maximum,
look where the rotor is !
That's why zero pf current in the armature adds or subtracts directly to field flux. It peaks when rotor pole is right underneath the armature turns.

You should stick with the notation in your textbook

but i find this mental image useful to understand why there's such a thing as synchronous reactance. It's not same as leakage reactance.
It does affect terminal voltage by reducing flux in the machine(,or raising it )
but the external characteristics are same as if it were another circuit element
and that's how most authors present it.

Is that any help ?

old jim
 
Last edited:
  • Like
Likes cnh1995 and OliskaP

Related to Armature Reaction Drop: Synchronous Generator Explained

What is armature reaction drop in a synchronous generator?

Armature reaction drop is the reduction in output voltage of a synchronous generator due to the presence of magnetic flux created by the current in the armature windings. This flux opposes the main magnetic field and causes a decrease in the generated voltage.

What factors contribute to armature reaction drop?

The amount of armature reaction drop depends on the load current, the strength of the main magnetic field, and the amount of armature winding flux. The higher the load current and armature winding flux, and the weaker the main magnetic field, the greater the armature reaction drop will be.

How does armature reaction drop affect the performance of a synchronous generator?

The armature reaction drop reduces the output voltage of the generator, which can lead to a decrease in power output and efficiency. It can also cause voltage fluctuations and distortion, which can affect the stability and quality of the generated power.

How can armature reaction drop be reduced or eliminated?

The most common method for reducing armature reaction drop is by using compensating windings in the generator. These windings produce a magnetic field that counteracts the effects of the armature reaction, resulting in a more stable output voltage. Another way to reduce armature reaction drop is by using interpoles, which are small auxiliary windings that produce a magnetic field that compensates for the armature reaction.

Is armature reaction drop always a disadvantage in synchronous generators?

No, in some cases, armature reaction drop can be beneficial. For example, in motors with a large starting current, the armature reaction drop can help limit the starting current and prevent damage to the motor. Additionally, in certain applications, such as wind power generation, armature reaction drop can be used to control the output voltage and frequency of the generator.

Similar threads

  • Electrical Engineering
Replies
6
Views
1K
  • Electrical Engineering
Replies
2
Views
2K
  • Electrical Engineering
Replies
10
Views
5K
Replies
1
Views
1K
  • Electrical Engineering
Replies
4
Views
3K
  • Electrical Engineering
2
Replies
37
Views
4K
  • Electrical Engineering
Replies
3
Views
2K
  • Electrical Engineering
Replies
5
Views
1K
  • Electrical Engineering
2
Replies
46
Views
5K
  • Electrical Engineering
Replies
5
Views
2K
Back
Top