Can misting systems improve HVAC efficiency?

  • Thread starter Thread starter jvanniel
  • Start date Start date
  • Tags Tags
    Hvac Systems
AI Thread Summary
Misting systems can potentially enhance HVAC efficiency, particularly in hot and dry climates, by pre-cooling the air entering the condenser. Calculations indicate that a 2-degree Kelvin drop in outside temperature could yield about 12% savings, though this figure may seem low. The discussion highlights the importance of understanding the refrigerant cycle and the impact of environmental conditions on system performance. Concerns are raised about the potential downsides of using misting, such as fouling of condenser fins and the risk of operating below designed condensation pressures. Overall, while misting may offer benefits, careful consideration of its implementation and effects is necessary.
jvanniel
Messages
1
Reaction score
0
Hi Guys,

I'm fairly new here, but I can't solve my problem (or I did but than I found a miracle)

I'm trying to optimize a HVAC system, especially for dry and hot areas. Now I was thinking about the use of a misting system in front of the condensor as done by for instance these guys; https://www.mrmistsystems.com/new/store/document/ac_pre_cooling/Coolnsave_Tulane_Study.pdf

However, I wanted to calculate the actual savings myself, so started to build a model;

Basic working principle HVAC

In the ideal vapor-compression cycle, refrigerant enters the compressor as a saturated vapor. As the refrigerant is compressed, it increases in temperature and pressure. After the compressor the refrigerant passes through the condenser. Heat energy (QH) is exchanged with the surrounding environment causing the refrigerant to cool and become a saturated liquid. Next, the refrigerant passes through the expansion valve causing the temperature and pressure to decreases. Because of the reduction in temperature and pressure, the refrigerant enters the evaporator as a saturated mixture. As the refrigerant passes through the evaporator, it absorbs heat energy (QL) from the environment that it is trying to cool. The refrigerant exits the evaporator as a saturated vapor and returns to the compressor to begin the process all over again.

Model

For the sake of the end product, we are taking the air surrounding the condensor as a starting point for the calculation. Since the effect of pre-cooling has to be shown.

A general rule of thumb is that the saturation temperature of the refrigerant at the condensor pressure should be at least 10-15 degrees above the temperature of the environment. From that criterion, the condensor pressure can be chosen.

The second important input number is the refrigerant mass flow rate of the system. Since, in this case it will not be variable for the different temperatures

Thirdly we have to calculate the heat removal by the evaporator, which can be described as:

Qe = Vair * d-air * Cpair * ΔT incoming air

Where:
Qe = heat removal in evaporator
Vair = volume of the air passing by the evaporator, dependent on refresh rate (m3)
d-air = density of air at room temperature (kg/m3)
Cp air = specific heat of air (kJ/kg*K)
ΔT = temperature between the outside air and the inside air

Based on the heat removal and the refrigerant mass, one can calculate the refrigerant conditions at evaporator outlet;

Qe = mref * (hevap - hconl)

Where
Qe = heat removal in evaporator
mref = mass flow refrigrator
hevap = enthalpy at evaporator outlet
hconl = enthalpy of saturated liquid at condensor outlet, since in the throttle only pressure is reduced; h condensor liquid ≈ h evaporator inlet

hence; hevap = Qe/mref + hconl


Compressor power

W = n / (n-1) .Pevap . Vevap . (Pcon/Pevap)^( (n-1)/n) ) - 1

Where:
W = compressor power
Pevap = evaporator outlet pressure
Vevap = Volume at evaporator outlet
Pcon = condensor inlet pressure
n = polytropic factor, normally between 1.25-1.41

For the throttling valve: % flash = (hf high pressure - hf low pressure) / (hfg low pressure)

Problem

With these formulas I end up with savings of about 12% for a 2 degree (Kelvin) drop of outside temperature, this feels off to me.

What am I doing wrong?
 
Engineering news on Phys.org
Are you really trying to figure why you should mist the air, or if you should? Hot and dry climates are practically asking for Water Cooled Towers or at least Hybrid Dry Coolers. But if you have to stay dry, most dry condensing units will meet their rated capacities with 115 degree ambient air.


-chris
aec.us.com
 
Sudden (unexpected) hot whether waves sometimes force to do this on the equpment not designed for high temperatures. But to keep without big reason the condensation pressure lower than designed may turn wrong. (However many would argue it would not.) Besides, for sure, the condenser fins get fouled from the water.
 
Here's a video by “driving 4 answers” who seems to me to be well versed on the details of Internal Combustion engines. The video does cover something that's a bit shrouded in 'conspiracy theory', and he touches on that, but of course for phys.org, I'm only interested in the actual science involved. He analyzes the claim of achieving 100 mpg with a 427 cubic inch V8 1970 Ford Galaxy in 1977. Only the fuel supply system was modified. I was surprised that he feels the claim could have been...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...
TL;DR Summary: Heard in the news about using sonar to locate the sub Hello : After the sinking of the ship near the Greek shores , carrying of alot of people , there was another accident that include 5 tourists and a submarine visiting the titanic , which went missing Some technical notes captured my attention, that there us few sonar devices are hearing sounds repeated every 30 seconds , but they are not able to locate the source Is it possible that the sound waves are reflecting from...
Back
Top