Computing Copper Loss: Examples & Reduction Strategies
Copper loss, calculated using the formula P = I²R, refers to power lost due to resistance in electrical wires. It can be reduced by using larger wires, which have lower resistance; however, the "skin effect" in AC current can limit the effectiveness of this approach. For accurate calculations, factors such as the application type, wire dimensions, and temperature effects must be considered. Installing capacitors can help reduce reactive current in inductive loads, potentially lowering copper losses at the meter. Understanding these principles is crucial for effective loss management in manufacturing and commercial settings.
energysaver
Good day. just want to ask anyone about copper loss. How is it computed for example in a manufacturing plant or in a dept mall.Could anyone give an illustration/example?
Also , is it true that copper loss can be reduced by using big wires?What if the wire is big enough?
thank you. hope you can help me...
Copper loss is the power lost because of the resistance in the wires. P = I2R.
Big wires have less resistance, but with AC current there is such a thing as the "skin effect", which means that most of the current is concentrated around the surface of the conductor, lowering the effective cross sectional area of the conductor and increasing its resistance.
what estimated percentage of a copper loss in a certain manufacturing plant? if i install capacitors in loads , would the demand at the meter be reduced by 10% by eliminating copper loss?...
thank you...
You are correct. If you have an inductive load (induction motor, for example) with a poor power factor, a capacitor could reduce the reactive current and the resultant current demand at the meter. Power meters usually measure only real power, and not reactive power, however, so as you point out, only the extra I2R losses in the copper are reduced.
Bob S
Hello
as our colleagues says in the above replies , copper losses is equivalent to I^2 X R
but what type of application are you going to calculate copper losses for ??
for example , if you are going to calculate copper losses for a flat busbar just calculate the resistance by knowing the cross sectional area of the bar and its length and the grade of copper you are using and then calculate it by resistivity x length divided by area then multiply the result by the current squared
but if you need to calculate this losses for temperature rise or when considering the heat effect for a transformer as an example then take into your consideration the current density , and the heat dissipation to the surrounding , and there are specific tables which can guide you to select the value of the current density in the first place as if you only looks at the value of the losses , it will not give you good indication for temperature rise
hope information was useful for you
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
Thread 'How Does Jaguar's 1980s V12 Dual Coil Ignition System Enhance Spark Strength?'
I have come across a dual coil ignition system as used by Jaguar on their V12 in the 1980's. It uses two ignition coils with their primary windings wired in parallel. The primary coil has its secondary winding wired to the distributor and then to the spark plugs as is standard practice. However, the auxiliary coil has it secondary winding output sealed off. The purpose of the system was to provide a stronger spark to the plugs, always a difficult task with the very short dwell time of a...