The discussion revolves around calculating the rate of heat loss through a concrete slab and determining the associated daily heating costs. The heat loss was calculated to be 4312 W, and the challenge lies in incorporating the furnace's efficiency into the cost calculation. The formula used indicates that cost is inversely related to efficiency, meaning higher efficiency results in lower costs. Participants clarify that since the furnace operates at 90% efficiency, this affects the overall cost of heating the basement. Understanding this relationship helps resolve confusion regarding the calculations involved.
jdawg
Messages
366
Reaction score
2

Homework Statement


The concrete slab of a basement is 11m long, 8m wide, and 0.20m thick. During the winter, temperatures are nominally% °C and 10°C at the top and bottom surfaces, respectively. If the concrete has a thermal conductivity of 1.4W/m*K, what is the rate of heat loss through the slab? If the basement is heated by a gas furnace operating at an efficiency of 90% and natural gas is priced at Cg=$0.02/MJ, what is the daily cost of the heat loss?

Homework Equations


Simplification of Fourier's Law: q'' = -k(T1-T2)/L
q=q''*A

The Attempt at a Solution


So I had no problems calculating the heat loss (q=4312 W), but I'm a bit confused on how to incorporate the efficiency. I'm used to just multiplying the efficiency by the amount of energy that I calculated in order to find the actual energy produced or lost, but I know in this case I'm trying to calculate the cost.

This is the formula that the solution I have uses:
Cost = (q*t*Cg) / efficiency (Where q=heat loss, t=time,Cg=cost per Mg)

How do they know to divide by the efficiency?? I guess in the problem they tell you that the furnace giving off energy is 90% efficient and we are looking at the daily cost of heat loss and not heat produced...

I'm having a bit of a mental block with this problem, I would really appreciate an explanation :)
 
Physics news on Phys.org
Well, since they are looking for cost, consider how much would it cost to heat that space with a 50% efficient furnace, versus a (theoretical) 100% efficient furnace.

Does that explain it?

OK, mathematically, looking at the formula for cost, "efficiency" is in the denominator. So that mean cost goes down as efficiency goes up, right? Doesn't that make sense?
 
  • Like
Likes jdawg
Thank you so much! It makes total sense, great explanation!
 
Thread 'Have I solved this structural engineering equation correctly?'
Hi all, I have a structural engineering book from 1979. I am trying to follow it as best as I can. I have come to a formula that calculates the rotations in radians at the rigid joint that requires an iterative procedure. This equation comes in the form of: $$ x_i = \frac {Q_ih_i + Q_{i+1}h_{i+1}}{4K} + \frac {C}{K}x_{i-1} + \frac {C}{K}x_{i+1} $$ Where: ## Q ## is the horizontal storey shear ## h ## is the storey height ## K = (6G_i + C_i + C_{i+1}) ## ## G = \frac {I_g}{h} ## ## C...