The discussion centers on calculating power loss in transmission lines supplying 120kW from a power station 20km away, with a resistance of 0.5Ω/km. The total resistance in the wires is determined to be 10Ω, but the participant struggles with finding the current and voltage across the resistors. Clarification is sought on whether the 100kV is the source voltage or the voltage supplied to the factory, with a consensus that it likely refers to the source. The approach involves setting up a quadratic equation to solve for current, which will then allow for the calculation of power loss. The importance of considering both voltage scenarios is highlighted to address potential ambiguities in the problem.
Larfleeze
Messages
2
Reaction score
0

Homework Statement


A factory receives 120kW of power from a power station 20km away via transmission lines. If the resistance in the power lines is 0.5Ω/km, what is the power loss in the lines if the electricity is transmitted at 100kV (Approximate to a simple DC circuit).

Homework Equations



V = IR
P = VI = I2R = V2/R

The Attempt at a Solution



Now first I simply found the total resistance in the wires by

Rw = 20km * 0.5Ω/km = 10Ω

The DC circuit I then approximated consisted of 2 resistors, one representing the total resistance from the wires and the other being the load of the factory. Since the question states the voltage is transmitted at 100kV I used that as the EMF and set up my imaginary circuit thusly:
http://img15.imagevenue.com/img.php?image=951360451_Circuit_122_536lo.jpg

However, it appears at this point I don't have enough information to answer the question, since I don't have the current or the Voltage over either resistor. Am I missing something or is there an easy solution I'm just not seeing?

(I'm not very knowledgeable in this area of Physics, only did it in my first year of my undergrad, but I am mathematically inclined so I don't think I'll be frightened by the solutions... hopefully)
 
Physics news on Phys.org
What does "transmitted at 100 kV" mean? Is that the voltage at the source, or voltage supplied to the factory?
 
I suspect 100 kV is the voltage at the source.

One quick thing to mention - you will make your life a lot easier if you think in SI-units. Yes, I can see that when you calculate the wire-resistance there is a kilo- in the numerator and the denominator, but still.

You are given all the necessary data to solve this problem. There is a voltage drop across the line and you are given the power the destination receives. In a series, the current stays the same throughout.
 
Last edited:
The 100kV being the source was the conclusion I came to as well.

Thanks, lendav_rott, I think I may be getting where I'm going. I think I can find the current by reducing to a quadratic equation by saying that:

V = I(Rw + Rf)

=> V = I(Rw + Pf/I2)

=> RwI2 - VI + Pf = 0

And just solving for I. From there I can figure out all of the other data, I think.

Personally, I don't tend to worry about number crunching until I get there.
 
You should also compute the loss assuming that the voltage given is the voltage at the factory. If the results differ significantly, you should warn the instructor that the problem is formulated ambiguously.
 
Thread 'Voltmeter readings for this circuit with switches'
TL;DR Summary: I would like to know the voltmeter readings on the two resistors separately in the picture in the following cases , When one of the keys is closed When both of them are opened (Knowing that the battery has negligible internal resistance) My thoughts for the first case , one of them must be 12 volt while the other is 0 The second case we'll I think both voltmeter readings should be 12 volt since they are both parallel to the battery and they involve the key within what the...
Thread 'Correct statement about a reservoir with an outlet pipe'
The answer to this question is statements (ii) and (iv) are correct. (i) This is FALSE because the speed of water in the tap is greater than speed at the water surface (ii) I don't even understand this statement. What does the "seal" part have to do with water flowing out? Won't the water still flow out through the tap until the tank is empty whether the reservoir is sealed or not? (iii) In my opinion, this statement would be correct. Increasing the gravitational potential energy of the...