Following up on the recent thread about Earth Resistance measurements
  • Thread starter Thread starter sophiecentaur
The discussion revolves around concerns regarding earth resistance and electrical safety in an older house with an underground supply. The user experiences frequent trips of the Residual Current Device (RCD) and questions the adequacy of the earthing system, noting a lack of visible connections to an earth stake. There is speculation about whether the presence of a photovoltaic (PV) system could impact the earthing requirements and RCD performance. Participants emphasize the importance of having a proper earth connection to ensure safety and suggest that an inspection by a qualified electrician is necessary to address these issues. Overall, the conversation highlights the complexities of electrical systems and the need for proper grounding to prevent electrical faults and ensure safety.
sophiecentaur
I have recently moved into a new (rather ancient) house and had a few trips of my Residual Current breaker.
I dug out my old Socket tester which tell me the three pins are correct. But then the Red warning light tells me my socket(s) fail the loop test.
I never had this before but my last house had an overhead supply with no Earth from the company. The tester said "get this checked" and the man said the (high but not ridiculous) earth resistance was acceptable. I stuck a new copper earth spike into the ground with a pair of thick earth conductors connected to my system and it was 'better but my tester was not totally happy.
My new house has an underground supply and all the metal bits in the house seem to be connected by a maze of earth conductors but I can;t find any conductor going to Earth. Previous houses all had underground supplies and a strap round the armoured supply cable so I assumed I would find the same. But no. Also, if I stick my meter pointed probe into the cable cladding, I get many kΩ when I eventually make contact. How bad is that? I feel safe within the house as everything in it seems to agree about zero potential. Would a better earth reduce the likelihood of annoying RCD trips? I thought it might be the problem.
Being a bit lazy I thought that PF could give a quick, if unofficial answer. The house is 1930 build iso it will have had several generations of installations - including an array of 10 PV panels. Is it possible that the PV system could have changed the situation? It seems to be documented.
I guess in the UK you have a MEN system. That will have no PE from the supplier, only a neutral. Does the armoured supply cable contain both Neutral and Active conductors? The armour on the supply cable will be earthed at the supplier's end.
In the distribution box there should be a Neutral bar and a PE bar, with one link between them. From the PE bar, there should be a PE wire going down to an Earth stake. Follow that wire to find the stake.
Is the building wired with ring mains or radials?
Yes; just like all the underground supplies I have had before. There is a third (ground) wire alongside all neutral conductors ('twin and earth') indoors. Some lighting circuits were made with just twin conductors in the wiring. The consumer unit (as all others I have ever seen) has a neutral bus and a fused live bus.
I assume that but it is not connected to my local earth network afaik. Without visibly interfering with the covering of the armouring, all I can do is to punch a small hole in the covering. The resistance between that and the house wiring earth is still high (k's) when I have finally made some contact with the armour.
The system is not what I have always been used to. As I said before, there has always been a strap around the incoming armour (four past houses) as a local earth. The last house had just two overhead conductors (no supply earth) and an earth spike plus a bigger / better one of my own.
Bottom line is that I could always (not conveniently) take an earth conductor from the distribution box / fuses to a spike outside. It's an old house and the services only appear inside the house. It's possible that the underground water supply pipe could now be plastic (replacing the old lead from 1930) So my question is really what's wrong with making use of the armour layer? You'd need to be familiar with the systems on UK. Of course, there are ring mains plus star connections to Cooker etc.. All pipes seem to be earthed with several straps.
I ask again whether the presence of a PV system could affect best practice.
I may have to bite the bullet and pay someone to look into it and fit an outside earth. Aamof, I will fairly soon be taking power to an outside workshop so I could kill two birds with one stone.
PS What is "VK7 Land"?
That sounds like TN-S earthing. Max external earth fault loop impedance reading (Ze) is 0.8##\Omega##.
I’d certainly call someone in to verify your new house’s earthing system. If you get only L and N, you’d normally need your own earth rod, so-called TT earthing. Max Ze is technically around 200##\Omega##, but should be investigated if above 100##\Omega##, really. All circuits must be protected by an RCD, although a 30mA one is a poor choice for whole-house protection.
I doubt your RCD tripping is due to a too-high earth reading. If it’s a 30mA flavour one, it will, in theory, trip even if the earth loop is up to 1667##\Omega##, any higher and it would cause the opposite problem, ie not tripping when it should. Your socket tester (check the specs) might not be set up to check TT systems.
The RCD is reading earth leakage, so the task is to find out where that’s coming from, a fault or cumulative small amounts of ‘normal’ leakage from multiple circuits. That would involve, amongst other things, insulation resistance testing or live earth leakage measurements. Solar is a common culprit, and really should be served by a type ‘B’ RCD.
First move should be an inspection, perhaps an EICR, as it looks like there’s lots to unpick here.
Side-note:
I moved in to a new place a year ago, with big stables near the house, with an obviously DIY electrical supply. Earth loop at the sockets was up around 400##\Omega##! Substantially different from at the house DB, which was comfortably under the 0.8##\Omega## expected from the TN-S earthing.
I traced the fault back to a junction box up on the chimney, where the earth was simply not connected. The earth conductor had been stripped back, and was the right length, but not inserted in the junction. It looked deliberate, and my bet was, the PO was experiencing RCD trips and so decided to ‘float’ the stables. Bizarre.
Likes sophiecentaur
Im unfamiliar with the practices in the UK. However, the main thing to be concerned with is if the neutral has a solid connection to:
sophiecentaur said:
...all the metal bits in the house seem to be connected by a maze of earth conductors...
If some metal chassis is connected to a hot wire through some defect in an appliance then this effectively shorts the supply out and blows a fuse or trips a breaker. The system does not rely on the conductivity of the actual earth in this case.
It is important for the system to be referenced to the actual soil/earth. By not doing this it is possible for the whole system to float up and develop a dangerous voltage between the ground you stand on and anything attached to:
The concencus in the US sometimes seems to be that there is an excessive use of grounding/earthing rods. The small shed adjacent to the house that is fed through a breaker in the house requires a grounding/earthing rod. As far as I know, any stand-alone structure requires this regardless of what it's fed from. In the event that the neutral and protective ground/earth in the feeder that runs to this small shed is broken, the grounding rod will have a tendency to hold the metal chassis of anything electrical in the shed close to the same potential as the ground close to the shed. This reduces the chance of shock. It is redundant but often redundancy = increased safety.
. . . . earth. The RCD would instantly blow for more than 30mA of imbalanced L-N current. Your N-E connection is not part of the UK system. N and L float with respect to the potential of the local Earth. The balance of the three phases from the local sub-station will determine the N volts (relative to Earth) at each single phase outlet in each house. The system floats when there's a difference between the loads on the three phases. There is little similarity to the terms and the arrangements in the US system.
It amazes me how many approaches and opinions there are about the basic function of the Earth connection. It surely has to limit the possible volts between two random pieces of metal and the amount of current that can pass between them (through a body). The earth path through a fault must also be low enough resistance to cause a fuse to blow - another safety feature.
My main concern is that there seems to be no local connection between my company earth (the armour) and anything in the house circuit. If there is, in fact, any local earth spike, I'd expect to measure (DVM) some low value of resistance. ( path between my earth - through the cable armour - to company transformer earth - back via the Earth. This, of course will not apply to where the supply is through two overhead conductors.
When I was a boy, we had a two wire supply (overhead) and no solid state technology. To deal with a fault to earth, the earth spike was connected to the house earth via an Earth Leakage Trip which tripped with a low(ish) current. Not low enough to avoid killing you but enough to deal with many equipment faults.
This makes no sense in the context of this thread. If N and L are not referenced in any way then what is the point?
Not possible. You cannot rely on the soil to blow a 20 amp fuse. Too much resistance. Unless what you mean is what I already said here:
You have made my point about the wide range of 'philosophies' involved with this topic.
I don't disagree with your points but I have actually dealt with them in my last post. The Earth Leakage trip (when I was a lad) dealt with heavy currents to earth where the earth loop resistance is high. That's the point of using the company Earth when available. I do not seem to have one connected.
The N voltage is always 'near zero relative to Earth (round about the mean values vector sum of the three phases. The "point" would be to understand the system. You can always measure a few N volts reference to earth.
The "context of this thread" has been ignored in most of the above posts; Any PF conversation about electrical power supply always seems to chase its own tail, rather than answering the point of the OP.
Third try: should I be concerned that the company armoured sheath appears to not be connected? Relevant replies from anyone with actual practical knowledge of PV installations would be appreciated because that might (?) change things. Is it the case that protection can only be achieved by active protection with a PV system.
So what happens if you connect a resistive load such as an incandescent light bulb between live and the metal chassis of some known good appliance that has all three pins? Will it trip an RCD somewhere? Will the bulb simply light normally or will it be dim due to the extra resistance of the soil? I can't really make heads or tails out of what the actual problem is. I'm not 100% sure where the device is that detects the imbalance between live and neutral. You have a tendency to be more than willing to state that there are a wide range of varying philosophies yet I never get a solid answer about how things are SUPPOSED to be done over there in the UK. You cannot expect good answers from misinformed people. I suspect the reason I never get a straight answer is because things are a little looser than we here in the USA are lead to believe. From what I've noticed folks from the UK seem to think it's a Wild West that anything goes concerning our system in the USA. There are people who will always diddle with something they have no business messing with but that cannot be blamed on the standard we try to adhere to.
I’d say you might be on a TT or TN-C-S system (see below), so in that case, no, but we can’t be sure yet. I also can’t yet explain your high k reading between supply cable armour and your earth, except to suggest inadequate earthing at your end.
- Can you post a pic of the service head?
- Where does the main earth wire to your house DB come from? It should be thick, 6mm2 or bigger. You might follow red herrings to a metal water or gas pipe, known as main bonding conductors. The maze of interconnecting earths are supplementary bonding. If you don’t find a dedicated earth rod, and are on TT, you need one.
Hopefully to clear up some uncertainty, here are the three main earthing types in the UK. Number three is by far the most common; the other two being old relics:
1. TT.
You get L and N only, and fit your own earth rod. Earth loop perhaps 100##\Omega##, too much to pop MCBs and fuses reliably, so the whole installation must be protected by RCDs. Mainly older, remote rural properties.
2. TN-S.
You get L, N and E, the latter usually via incoming cable lead (as in Pb) or armour sheath. Earth loop max 0.8##\Omega##. Mainly older properties. My favourite type of earthing.
3. TN-C-S.
You get L and PEN (combined Protective Earth and Neutral, aka CNE).
At the service head the PEN is split into N and E, presumably the N/E link being discussed above. Max loop 0.35##\Omega##. Sometimes referred to as one of its forms, PME, Protective Multiple Earthing.
Likes Averagesupernova
Guineafowl said:
I’d say you might be on a TT system, so in that case, no, but we can’t be sure yet. I also can’t yet explain your high k reading between supply cable armour and your earth, except to suggest inadequate earthing at your end.
1. TT.
2. TN-S.
3. TN-C-S.
I see. This explains the confusion and seemingly contradictory explanations I have experienced in the past.
Guineafowl said:
1. TT.
You get L and N only, and fit your own earth rod. Earth loop perhaps 100Ω, too much to pop MCBs and fuses reliably, so the whole installation must be protected by RCDs. Mainly older, remote rural properties.
This is the one that confuses me. If it is expected that an RCD will trip, the system must be referenced to a ground rod someplace. The grounding wire attached to the chassis of appliances is attached to the customer supplied ground rod as I understand. Well and fine but if the line and neutral are truly floating then there is no possible path for shock current. If it's truly floating then touching live while standing on the ground simply causes the live wire to be connected through the person's body to the earth. No shock will occur since there is no return path in a floating system. If then at the same time someone touches the neutral then current will pass through both people. What's interesting in that case is that an RCD would still not trip since the currents still have to be equal. For the RCD to work the neutral has to be referenced to the earth somewhere and I assume it's at the transformer.
Yes, in all three systems the neutral/PEN is earthed at the transformer end.
Ok. Makes sense. So line and neutral do not float.
One further thought, @sophiecentaur , is that your PV installation should have involved some basic electrical tests on the existing supply.
Did the PO leave behind some paperwork with regard to this? It should be in the form of an electrical test certificate, detailing earthing system and Ze reading.
Failing that, the PV company should have left some stickers with their contact details. They might have the certs on file.
If the active current is not equal and opposite to the neutral current, then the RCD will trip.
PE and N are linked in the distribution box, and for MEN, on every pole along the street. That is necessary to protect all the insulation.
But earth is not necessary, the trigger could be conduction to another A or N circuit on another RCD.
Likes sophiecentaur
I’d have to add (see post #11) that this is not the case for TT and TN-S installations.
Look at the diagram at the top of the wiki article.An RCD can be placed anywhere in the circuit - on the feed to one load - on a group offload - or the whole input to the house. It's a current transformer. Both L and N go through a core are 'two primaries' and the secondary has many turns which feed an amplifier. Normally the L and N currents are equal and opposite but any imbalance (say 30mA or 10mA) will be detected via the secondary.
If the L and N currents are not equal because there's an alternative return path (not the N) the RCD will trip. This is not new technology; I fitted one fifty years ago.
This has been my point; I don't know (as I thought I'd made clear)..
In four of my past houses (with underground feeds) they all had a visible, chunky connection to the sheath of the armoured cable which supplied a good very low potential to all metal in the house. There was never an issue of a failed 'earth loop test' because there was an excellent ground connection to the substation.
My one house with just two wire overhead connection had visible earth spikes but the earth resistance was only 'ok' but apparently it was acceptable.
Ok. It’s hard without being there or seeing pictures, that’s all. Does it dive into the wall, where do you lose sight of it?
In any case, if it doesn’t connect to the service head (earthing types 2 and 3 above), then you have TT earthing. If you can’t find the rod, next stage is a live loop impedance test (Ze). This should have been done before the PV was installed.
With regard to the PV, any earthing type 1-3 is suitable, as long as it’s within spec. After verifying your earth, I would then start chasing the RCD trip.
- What circuit(s) does it serve, when does it trip, etc.
- Visual inspection as far as possible, especially junction boxes and outlets.
- For the PV part, isolate AC and DC sides, then IR test individually.
Side note - my PV was tripping during rain when I moved in. Proceeded as above, and found an unsealed junction box outside the house, full of insect debris and cobwebs that were getting damp.
With respect, the N conductor is never at 0V ground potential, even in the best systems. A 'scope always shows a few volts of 50Hz relative to earth. In my book, that could be 'floating'. You could say that VN doesn't 'float' between the N and E, right next to the transformer but you can see it happening with a DVM.
In UK homes, it's forbidden to connect N to E. Why would that be if it were not relevant?
Many decades ago, it was decided that a single conductor was not the way to go and that a low (near zero) voltage neutral would be optimal. This is for a three phase stystem and the advantage is that it allows a degree of old balancing among the loads on the three phases. Conventional power distribution to houses in UK is to spread the phases 1,2,3,1,2,3,1,2,3 to a row of houses and statistics does the rest.
True. The head consists of an armoured cable, emerging from the floor with just two conductors coming out at the top. There's no other box / sleeve / clip attached. Trust me; I know what I'm looking for and there seems to be nothing like an earth connection. Your comments show that you are aware of of my confusion and concern, particularly in the light of the PV installation. Problem with the (whole) house is the various legacies we discovered when we moved in; the electrics was just one of them. The last owner died four years ago and he would have had many of the answers. Unfortunately, he died whilst walking up to the Pub (which say it all; everyone loved him, though.
As mentioned, I'm having 'a man' to look at it today and to decide what we should do. He may know where to look for a possible earth installation. Unfortunately there's a lot of concrete close in to the house and that's unlikely to be a good place for an earth spike.
It's true that there has to be a path other than between the L and N. But a current transformer knows nothing about anything but the net L and N currents. I guess Kirchoff applies so the net current flow at any node must be zero. But the RCD will spot any difference and doesn't care about the nature of the extra path.
I feel like I'm in a space ship with no handy local earth connection. Never had any suggestion of a shock, though.
I’m not sure what you mean by this - in the common TN-C-S system they are linked. Unless you mean YOU are forbidden from doing it, which would be true - the service head belongs to your DNO (Distribution Network Operator), and changing the earthing system would require permission from them and a building warrant.
Please let us know what happens! If he agrees it’s TT, and the readings aren’t good enough, and the earth rod can’t be found, I suspect he’ll sink a little earth pit in the concrete and bang one or two rods in.
Both you and @sophiecentaur seem to be missing my point. Of course I realize that an RCD works by sensing unequal currents in the live and neutral. Those currents will NEVER be unequal if the system is completely floating. The system has to be referenced to something else (the earth) upstream of the current transformer of the RCD in order for the system to allow an RCD to work correctly.
Edit:
I do see your point about a pathway between two different RCDs on the same system would cause a trip on a truly floating system. This in my opinion is not safe enough.
I agree but how can you expect to find a perfectly floating system? All the circuit diagrams of mains supplies show substation transformers with a Neutral connected to earth. That gives a possible path to the transformer neutral via the path through earth. Even a high resistance earth fault path will allow lethal current to flow.
We, of course, are saying the same things about this. Stating a problem without any misunderstandings is hard and can turn into a dialogue of the deaf. Not uncommon in PF.
Ahhh, you are not a amateur radio operator :smile:
VK7 is the callsign prefix for Tasmania, Australia,
I am in VK2 = NSW state .... VK2TDN
Dave
The point is that as far as I can remember on this forum I have never gotten a straight answer as to how the electrical system in the UK was done concerning grounding. You said yourself:
But, apparently not according to others and you also said:
Now concerning a floating system to remain completely isolated, we don't need to worry about it since it's likely never done except in special cases. But, there are plenty of places the system is small enough that it's entirely possible that it could remain isolated for years. At any rate, I would not consider it safe without something in place for monitoring isolation. Here's an example. The video covers some things that are pretty basic to most of us but still worth watching.
I dug around in the conveyancing documents and actually found a 'sparse' report on electrical systems. It suggests that I have a TT system. This link has some interesting figures, including the fact that earth resistance can vary a lot , according to temperature and ground saturation, and be over 1kΩ. Bottom line (to me) is that active protection is essential. Fine, but something that's inherently safe(r) would make me happier.
Q. is my electrician likely to be prepared to connect my earth to the armoured cable? Seems like a no-brainer.
Unlikely.
- Service head belongs to your DNO.
- Meter belongs to your energy company.
- Anything after that belongs to you, and you or your electrician can play with it.
Secondly, going from TT to TN-S, you are changing from customer-supplied earth, to one supplied by the DNO and which they are responsible for. You’d need their permission and they’d probably send their own installer out.
That said, it’s worth asking. TN-S is best, followed by TT. TN-C-S can cause problems with outbuilding supplies and car chargers (search ‘broken PEN conductor’).
Likes sophiecentaur
Guineafowl said:
Unlikely.
Thanks for the info and opinion. Something that I can't understand is how this house has T-T earthing. I'd bet money on finding the armoured cladding connected to house earth system in any random house I looked in our street. It's the only arrangement I have ever seen except in our last house with two overhead conductors.
I don't know how many generations of electricity supply have been installed since the house was built in 1930 but how come the PV installers didn't raise the problem ten years ago?
I found a record of earth loop resistance of 130Ω which would be lethal with just 2A current flowing and no fuse blown. Can any supply company argue against making 'that earth connection' and reducing the resistance to 1Ω?
As an aside, I notice that an 'island connection' is used for a EV charging points and protection is just local to the charger. Also there are special considerations for protection of hot tubs etc. with a requirement for a 10mA RCD. A real toaster in the bath situation, potentially.
The PV installers wouldn’t have seen a problem - 130Ω is within spec for TT. Don’t forget the RCD requirement.
I can’t explain why you’re not TN-S - perhaps the earth loop impedance (as it’s called, although I was scoffed at on here for doing so!) was above the 0.8Ω max due to poor connections or long cable run.
  • #31
I had an interesting chat with a guy in UK Power Networks. He saw my problem.
He did say that the supply may never have been changed since 1930 and that could explain why TT is there. He will send engineers to look at the system and they may well fit a termination to the armoured sheath. However, it appears that not all installations 100 years ago used a metal (lead) sheath so I can't get my hopes up too high.
Another thing. I was talking to my neighbour and she let me look at her installation. Despite having been re-wired not long ago, it still has a TT system. But the installers presumably measured an 'acceptable' earth impedance so no one wanted to fix it. She was worried, of course but I told her she's legal and that I'm just fussy.
The UPN service is FREE though!
  • #32
Keep us posted!
  • #33
Guineafowl said:
Keep us posted!
There has been a development. Men from ' National Power Networks' arrived today and took a look. They stripped off the insulation at the end of the sheath and found no continuity between that and the Neutral conductor.
They told me that it's probably a legacy from the original DC System that was common in our area. There are two conductors coming into the house so at least it wasn't Earth Return.
They told me I have a TT earthing system (which we knew) and that I would need to get a 'better' earthing connection if I want to improve things.
The guy didn't want to commit to what the lead sheath is connected to at the other end but I can't imagine it's not continuous back to the substation so I have to ask WTF. I'll follow this up with Power Networks but I imagine that even making connections to all substation transformers could cost them a fair bit. So "just put up with it mate" is probably going to be the answer. I am surprised that there have been no small disasters in the system if there are widespread TT systems around our area (and many others, probably. Our lives are obviously subject to the need for 100% reliability of RCDs.
I'll look into the history of power distribution and, of course, would be grateful for any input from PF.
  • #34
Remember that of the three earthing options, only TN-S and TN-C-S are the DNO’s responsibility. TT is entirely the customer’s.
I’d say they had three options:
1. Convert to TN-S. No, since there’s no N-sheath continuity. Cable is probably too old to trust the integrity of the sheath long-term anyway.
2. Convert to TN-C-S. The old cable is probably not suitable, being more at risk of the dreaded broken PEN. Modern supplies use split concentric cable, where the N is split into multiple wires to reduce the risk. A TN-C-S system for you might also require changing the final distribution to PME, where the N is earthed at multiple points, so, a lot of work.
[Note: for both the above, you’d likely have to upgrade your side of the supply as well; earthing/bonding conductors on TT can be tiny compared to the 10mm2 or so needed for the others, which might have to handle the full prospective earth fault current (PEFC) in the kA range.]
3. Leave you on TT.
If they’re talking about a converted DC supply, then surely your cable must be at least 1960s vintage? In which case, past its sell-by date. Is it the old paper-wrapped stuff? Perhaps you could try ‘please replace my antiquated supply, and while you’re at it, give me a decent earth’. Reasonable, given the electrification of modern life - heat pumps, EVs, etc. They’ll have to do it at some point.
In the meantime, why not bang in your own earth rod, or get one put in? You can couple two 4’ ones together. You can also get your RCDs tested for trip time and level under various conditions. At the very least, you can use the test button quarterly (as everyone does, of course!).
If it comes to it, TT isn’t that bad. It’s even the earthing of choice these days in some cases, eg outbuildings, hot tubs, EV chargers.
  • #35
Thanks.
It could be nearly 100 years old.
I'll tell them that my 60A supply fuse is not enough for my electric shower, planned EV and garden extension. If it's as bad as it could be, there could be a lot of digging trenches in our road. The neighbours would all benefit and would need to give approval for upgrades.
  • #36
sophiecentaur said:
Thanks.
Feeble! Your electric shower would draw 40A or so, for a start. My house has 100A*, and it’s just a rural croft house.
I’d say you’ve got a pretty good case for an upgrade. Try to catch them for a quote before the winter, when they’ll all be chasing storm damage.
* The fuse carrier is rated 100A, but without breaking the company seal and looking inside, I can’t be sure. Sometimes they fit a smaller fuse than rated.
  • #37
@Guineafowl
I got back to UKPN and it's apparent that they have a structure with several different 'departments' and you have to ask the right question of the right department. When I talked about an 'upgrade' they put me through to a lady who assumed I wanted a three phase supply - because I was talking to the upgrade department. Nobody ( none of the the young women) would have known about the 20th Century but I got an email back with a copy of what I had said about the historical DC service. That particular woman was very helpful and she has booked a 'surveyor' to give an estimate of the possible cost to me!! of any upgrade. She was talking in terms of holes in the road, road closure or traffic control. Top end could be tens of £k.
I've done some trawling around and opinions are not high about T-T systems. Unless my bloke comes and accepts that some installations are just too old to be acceptable and that UKPN would pay for any change, I can see that the Ombudsman might have to be involved. The Ombudsman's website stresses that they cannot deal with 'whatif' situations and users need something to appeal against.
I remember in the 1950s, my parents moved into a remote cottage with no supply and it took several months of oil lamps etc. before there was a hearing and we got connected. Several poles were involved, iirc. (Not the European ones)
I should be a lot better informed by next Tuesday.
  • #38
I’ve just read this bit again - am I missing something, or did those engineers just walk away from a fault? At least part of your cable sheath is floating. What you need is not so much an upgrade, as an urgent repair.
If there were a phase-sheath/earth short after the break, would there not be step potentials? What if you were using an earthed appliance outside, and simultaneously touched something conductive sticking out of the ground, eg a metal railing, near the fault?
  • #39
Almost. They left an 'assessment form' with the comment "No earth reading. Advisedto get a TT Earth by a qualified electrician"
So they would say that the advice didn't constitute actually walking away from a fault. There might be a problem if the installation was judged to be a hazard. In a possibly similar situation when gas is smelled, the gas company can disconnect you.
  • #40
Guineafowl said:
1. TT.
Based on the above, I don't see why the power company should be responsible for the scenario at hand. If this was an accepted practice at one time then it should be now. The ground rod may in fact be missing or previously removed, etc. Of course this is not correct and needs to be dealt with but since the original plan was that the customer provides the earthing then it should be reasonable that the customer is expected to replace or repair what is involved in earthing this system.
  • #41
There are many accepted practices in the past which are not acceptable now. It's only cost that affects that.
The presentEarth Loop resistance is 130Ω which is in spec. But that is not inherently safe because it relies on active protection. The standards for T-T earthing are surely only there because of the cost of replacement with safer methods. It's understandable in certain circumstances but, in an urban situation with dense population, 'proper earthing' should be a matter of course.
IMO, this is as much a political matter as anything and it's only because people don't understand the relevance of earthing and the possible dangers and costs of sorting out the problem. Underground services are all potential time bombs. Sewerage, water supply and gas need attention and so does the electricity supply. I feel it's worth while my trying for a solution to my personal problem here.
  • #42
That’s right, a TT earth is the customer’s responsibility, and perfectly acceptable if in spec. The OP requested an engineer visit to assess for TN-S connection to avoid the drawbacks of TT.
The visit revealed something separate - that the ancient incoming service cable, belonging to the power company, has a conductive sheath that isn’t continuous back to the supply earth/neutral, nor bonded at the customer end.
To me, this is a fault for the reasons given above, post #38. Not grounds for immediate panic, but something that would form a case for service cable replacement. What say the EEs?
Likes sophiecentaur
  • #43
@sophiecentaur based on your last post then I see this as you simply want an updated system. Why the beating around the bush?
As far as this goes:
This is a straw man argument. It may be your opinion and of course you are entitled to it. If systems like this exist and are not on a list for updating then I'd say it is acceptable now.
  • #44
Hardly a straw man argument. I could ask you if you had the opportunity to change from a TN-S system to T-T would you change? What would be a good reason? T-T is a last resort when there is no low resistance company earth supplied? I notice you write from US which is often a different electrical environment from UK.
RCDs work pretty well but not as reliably as an earth connection which can blow a fuse and disconnect the supply from the faulty circuit.
Acceptable to whom? That demonstrates a strong faith in the politics and economics of your supply industry.
  • #45
In the USA no matter how old the service is there is nothing stopping me from updating to a 'safe' installation by adding three wire circuits or replacing the main panel, etc. Those costs are on me. There is no TT, TN-S, etc. All residences get two hots and a neutral. Very very old residences may get only one hot and a neutral. It is expected that at the main service panel the neutral will be attached to the chassis of the panel and from there a third wire will attach to the chassis of anything plugged in. Doesn't matter how old the wires are feeding the service. We don't have, nor ever had the variability that the UK seems to have. Yes, I feel safe and have faith in the system as it is intended.
Yes, the third wire attached to chassis as I described is certainly safe. However, don't think a ground rod or two connecting to the neutral in your case will will cause a fuse to blow in the event that a hot wire touches a chassis. This is a common misconception. There are videos out there that demonstrate this. The actual earth is unable to provide a low resistance path in order to blow a fuse.
I searched for a bit but couldn't find a video demonstrating this. Put out by Mike Holt.
  • #46
There are pros and cons to every earthing system.
Likes sophiecentaur
  • #47
That statement includes the word "misconception" and I agree with that in some circumstances. Many faults are not just a simple 'short circuit' though. I'm used to fused plugs which prevent excessive current through an appliance. But even they will not blow when in series with a typical T-T earth resistance when the 'fault to case' is in series with an internal resistive path, leaving the case at a lethal voltage. True, any nearby conducting parts are likely to be bonded to the house earth so the pd may be very low but the internal fault could be nicely cooking the faulty appliance without blowing any fuse and still leave the appliance case live. A TN-S system will not allow that to happen because a fault current will always be enough to blow a fuse. I lived in a house in the 60's which had an Earth Leakage Trip which was a relay in series with the house earth and the rod in the ground. No biological protection there (no solid state products available at the time) and definitely not fail-safe. Strangely, they don't do it that way any more.
Of course, the RCDs should avoid disasters happening but, of all the millions of RCDs in homes around the world, how many are tested regularly? (That is recommended by the makers.) They're only tested when 'the man' calls to fix a fault or instal something else. Fail safe is a very comforting design. I don't think I should be criticised for wanting high levels of safety. The parallel with driving applies here; doing (the legally marked) 50mph in a country lane doesn't guarantee your safety all the way along the 50mph zone
  • #48
So what is to stop you from joining the earth and neutral in your main panel? You would end up with TN-C-S right? I'm not suggesting you do this. It is truly a question. Post #34 touched on this a bit. I can't see how it would not be safer than leaving it as it is.
  • #49
Various reasons:
- A TN-C-S earth is almost always PME (protective multiple earthing), meaning the neutral must be earthed at multiple points along the final distribution path, establishing a decent equipotential zone. So, it’s a network thing, not simple link in the home thing.
- You’d be making the earthing the DNO’s responsibility without their permission.
- As far as I know, the N-E link is never in the distribution board here, always at the service head. A glaringly obvious DIY bodge if anyone were to inspect.
Again, there’s nothing really wrong with a TT earth. I had one for 8 years. Many consider it safer than TN-C-S (or N-E link, or MEN, depending where you are)* and opt to use it even today. For example, a distant outbuilding (too far out of equipotential zone) or EV charger.
* Imagine you have TN-C-S/N-E link/MEN, and the supply neutral goes open circuit, for whatever reason. All the earthed metalwork in your property, including the charging EV, will be enlivened. A big drawback.
  • #50
Ok. I suspected as much. Here in the USA the transformer is seldom very far from the service panel. Several hundred feet at the most. There will be a ground rod at the transformer as well as one at the service panel for the residence. Two in a lot of cases because NEC says if the resistance is too high with one it needs to be two. This often translates into just put two in.
In the UK I understand that distances are much farther between the transformer and the residence. It seems to me unless there are points along the run of cable feeding the residence that ground rods are installed, it wouldn't make a difference.
The neutral is tied to the chassis of the meter box here in the USA as well as the main service panel. After the main service panel the ground (earth) are kept separate. Some places now require an emergency disconnect on the outside for fire department, etc. I'm not sure how that changes thing concerning where the earth and neutral split off.