High frequency from AC tig welder affects digital ammeter?

AI Thread Summary
High-frequency AC TIG welders can cause inaccuracies in digital ammeters, as indicated by a serviceman's findings that showed a discrepancy between digital and analog readings. The digital ammeter recorded over 150 amps, while the analog meter indicated only 105 amps under similar conditions. The high-frequency signal may not be a pure sine wave, potentially confusing clamp meters and leading to erroneous readings. Despite the engineer's insistence on the digital reading's accuracy, the discussion suggests that the analog meter may provide a more reliable measurement. Ultimately, the issue remains unresolved, highlighting the complexities of measuring current in high-frequency welding applications.
paceplane
Messages
2
Reaction score
0
I need a solution to the question, Which clamp-around-the-cable ammeter (digital or analog) can be trusted in measurement of current draw by a high-frequency AC tig welder? High-frequency AC is a requirement of welding aluminum, and an electrician measured 150+ amps at full power welding aluminum. A serviceman brought into find the problem told us, after checking the machine, that high frequency creates error in digital ammeters and his analog meter indicated 105 amps in a duplicate situation. We might have left it at that but are being told (by an engineer) that the digital reading was correct and we have to take the welder offline. Help!
 
Engineering news on Phys.org
This has nothing to do with analog and digital. Both can be constructed to show the correct current. Did you check the specifications of your meter.

If the serviceman is from the welder's company I would tend to trust him.
 
The power supplied to the welder can be measured for a limiting result, which I hope will satisfy the engineer.
 
The Wiki Current_clamp page has some interesting info.

If you are running AC for Al, with a high-freq starter signal, I'd bet the high-freq is not a sine wave and might confuse the clamp meter a bit. It could also induce more signal due to being coupled better than good-ole-60hz. But it should only run at startup and not affect a continuous reading. It's possible that your welding AC is not a sine wave as well, so you would have to adjust the reading to the waveform. In fact a square wave might give you 1.4 the reading you'd expect from a sine.

If your other reading was made with an in-line meter calibrated for real RMS, I would trust it a bit more.

However I don't follow why the equipment should be taken out of service. Is it welding correctly as set, or can't you "dial it down"? Is it fully automated and not current limiting as it should?
 
There's so much noise around one of these machines, you may have to fall back on a very fundamental measurement.
First, I'd attempt to get through the applications help people at the equipment manufacturer. Behind the thin line of question answer's is a group that have had to address this issue.

If that doesn't work, I'd try wiring in a current shunt with a non-electronic meter.
 
Thank you for the answers. High frequency does remain past the start because of stabilization ([URL="[URL]http://www.lincolnelectric.com/knowledge/articles/content/alum2.asp"] and I believe due to the difference in exhibited measurements it is a digital meter issue. Sure we can dial it down, the test was done at maximum power in an attempt to register a spike or overload on a recording ammeter at the building entrance. While we may not have a definitive answer to the question, the ammeter did not see it out there. Indications seem to be that the digital meter was incorrect; but the engineer is not accepting it. Sense and politics are often at odds. Thank you all for your input and help.
 
Last edited by a moderator:
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'How Does Jaguar's 1980s V12 Dual Coil Ignition System Enhance Spark Strength?'
I have come across a dual coil ignition system as used by Jaguar on their V12 in the 1980's. It uses two ignition coils with their primary windings wired in parallel. The primary coil has its secondary winding wired to the distributor and then to the spark plugs as is standard practice. However, the auxiliary coil has it secondary winding output sealed off. The purpose of the system was to provide a stronger spark to the plugs, always a difficult task with the very short dwell time of a...