Induction Motor Torque-Speed Graph: Rated Power & Full Load

In summary, we discussed the torque-speed graph for an induction motor. It was noted that the torque at 0% synchronous speed is roughly 150 times that of full load torque and the motor only reaches 100% full load torque at roughly 95% of its synchronous speed, depending on the rated slip. We also explored the concept of full load torque and its relationship to rated power, as well as the four general speed-torque curve shapes for induction motors. It was mentioned that full load torque represents the safe operational torque, and that temporary overloading may occur for loads with high starting torque. Finally, it was suggested to listen to an electric motor start and observe how it crosses over peak torque into the stable region, as this can aid
  • #1
fonz
151
5
In terms of a torque-speed graph, for an induction motor the torque at 0% synchronous speed is roughly 150x that of full load torque and the motor only reaches 100% full load torque at roughly 95% of it's synchronous speed (depending on the rated slip).

http://www.kalleload.net/uploads/dnyxjypnneix.jpg

If full load torque by definition is the torque required to produce rated power at rated speed then what is rated power?

Also what is actually considered full load? how is the load determined? My understanding is that looking at this graph you can, by knowing how much a load will slow down the rotor speed determine the torque the motor will produce to speed it back up am I wrong?

Regards
Dan
 
Engineering news on Phys.org
  • #2
""If full load torque by definition is the torque required to produce rated power at rated speed then what is rated power?""

Nameplate horsepower, 2 * pi * torque * rpm / 33,000

Normal operation is to right of that dot on your curve.

If motor operates to left of that dot it is overloaded and will burn up.

There are four general speed-torque curve shapes for induction motors, A through D.

Something like an elevator which requires lots of torque to get it started would likely use a D curve motor. Extreme starting torque but pretty bad speed regulation.
A low inertia load like a centrifugal pump might use an A or B motor. Modest starting torque but fairly low slip hence ~constant speed.

This AN887 from microchip is a good one, see page eleven.
ww1.microchip.com/downloads/en/appnotes/00887a.pdf
 
  • #3
jim hardy said:
""If full load torque by definition is the torque required to produce rated power at rated speed then what is rated power?""

Nameplate horsepower, 2 * pi * torque * rpm / 33,000

Normal operation is to right of that dot on your curve.

If motor operates to left of that dot it is overloaded and will burn up.

There are four general speed-torque curve shapes for induction motors, A through D.

Something like an elevator which requires lots of torque to get it started would likely use a D curve motor. Extreme starting torque but pretty bad speed regulation.
A low inertia load like a centrifugal pump might use an A or B motor. Modest starting torque but fairly low slip hence ~constant speed.

This AN887 from microchip is a good one, see page eleven.
ww1.microchip.com/downloads/en/appnotes/00887a.pdf

So essentially what full load torque is telling you is that that is the safe operational torque. So if a load requires high starting torque you allow for temporary overloading of the motor assuming it is capable of getting up to near synchronous speed at which point it will be in the region of 'Full Load'?

And so to determine full load torque and so rated power, these are actually defined by what is considered safe operation i.e. operating the motor without it producing higher torque at lower speeds. So rated power would be the safe operational torque x rated speed

Cheers
Dan
 
  • #4
Yes.. Once you are aware of this, listen to an electric motor start.
Good example is workshop grinder, a fairly high inertia load..
It hums and slowly accelerates the wheels until they're nearly up to speed then you hear it "Whirr" as it snaps that last little bit up to full speed.
That's when it crossed over peak torque into the stable region.

I really advise that little experiment - for me, "feeling" something makes the equations come easier.
You'll encounter "slip" in your motor courses and that intuitive feel helps you manipulate the formulas.

And your mind will picture the speed-torque curve every time you hear an electric motor start.
 
  • #5
jim hardy said:
Yes.. Once you are aware of this, listen to an electric motor start.
Good example is workshop grinder, a fairly high inertia load..
It hums and slowly accelerates the wheels until they're nearly up to speed then you hear it "Whirr" as it snaps that last little bit up to full speed.
That's when it crossed over peak torque into the stable region.

I really advise that little experiment - for me, "feeling" something makes the equations come easier.
You'll encounter "slip" in your motor courses and that intuitive feel helps you manipulate the formulas.

And your mind will picture the speed-torque curve every time you hear an electric motor start.

Excellent thanks!
 

FAQ: Induction Motor Torque-Speed Graph: Rated Power & Full Load

What is an induction motor torque-speed graph?

An induction motor torque-speed graph is a visual representation of the relationship between the motor's torque (rotational force) and speed (rotational velocity) under different operating conditions.

What is rated power in relation to an induction motor torque-speed graph?

Rated power is the maximum amount of power that an induction motor can consistently produce without overheating. It is typically represented on the torque-speed graph as a horizontal line.

How is full load indicated on an induction motor torque-speed graph?

Full load is indicated on an induction motor torque-speed graph as the point where the motor's torque and speed intersect, representing the maximum load the motor can handle while still maintaining its rated power output.

How does a change in load affect the torque-speed graph of an induction motor?

A change in load will cause the torque-speed graph of an induction motor to shift. If the load increases, the graph will shift to the right, indicating a decrease in speed and an increase in torque. If the load decreases, the graph will shift to the left, indicating an increase in speed and a decrease in torque.

What factors can cause variations in an induction motor torque-speed graph?

Several factors can cause variations in an induction motor torque-speed graph, including changes in voltage, frequency, temperature, and the motor's design and construction. In addition, load variations and mechanical issues such as friction and wear can also affect the graph.