Induction Water Heaters: Are They Worth It?

In summary, the main question is whether induction water heaters have any benefits over traditional electric resistance coils. On Quora, someone argues that resistance coils are a near perfect conversion of electricity to heat, making induction heating unnecessary. However, induction cooktops are more efficient due to less waste heat between the coil and pan. This raises the question of why induction heating is not used in water heaters. Some argue that there is no advantage to the greater complexity of induction heating compared to a submerged resistive heater. However, others point out that heat pumps are more efficient than resistive elements, but they have different requirements and limitations. Ultimately, the efficiency of a heating system depends on the specific device and its specs.
  • #36
Hi! To your Question, Both are electrical heaters with 100% efficiency, but they have varying use and they differ in the way they produce heat. Induction heater, in general, are not used to heat water. Instead, a conventional heating element is a more viable option. In conventional Heater, the current is made to flow through the resistance wire by applying a potential difference while in induction heater, the current is made to flow with the tune of external exciting electromagnetic wave. if you are interested you can go to https://resources.mrheater.in/2019/09/how-induction-heater-works.html for a brief understanding on how an induction heater works.
 
Engineering news on Phys.org
  • #37
Heatpump HW heaters do have limitations, specifically the maximum hot side temperature is the problem, from memory its difficult for them to exceed 50-60C output temp without multi stage pumps, basically good for low grade heat at best.

So they are perfect for areas that are warm already, but almost no better than a resistor if the cold side temp drops too much, good luck making them work if your outside air is -20C! As the delta T grows, COP -> 1. At COP 1 a heat pump is a very mechanically complicated resistor!

Induction water/fluid heaters do exist, but generally I've seen them used in applications where heat density is a problem, eg burning the material you want to heat. So for example in milk processing, you want to heat all the fluid to a temp (say pasteurization), but not have a energy density so high that the fluid in contact with the heat source exceeds some limit or burns. Restive elements are also sold with different "densities", if you've ever home brewed properly this would be familiar!

1588428118423.png

http://waterheatertimer.org/watt-density.html
 
  • Like
Likes anorlunda
  • #38
Anyone who has used a Metcal soldering iron understands how spectacularly induction heating can deliver lots of power without exceeding a fixed (Curie) temperature.
The other capability of an inductive heater is lack of penetration of the pressure vessel. Most of the appliances rely on coupling to ferromagnetism so if the vessel is not ferromagnetic there is little surface heating.
 
  • #39
BWV said:
Makes sense, thanks
I understand that in theory an induction boiler can put the induction coil and the magnetic metal plates inside the tank just like the heating element in an electric boiler. The induction coil doesn't heat up, just the iron in the plates heats up. the plates don't touch the induction coil, so the space allows water to completely surround the plates. as a result they could be just as efficient as a resistive coil. The improved efficiency could come from use of a continuous flow heater that uses an Iron pipe to heat the water on demand, giving instantaneous heat, and eliminating losses due to storing heated water for a long period. Unfortunately the iron pipe may have a relatively short lifespan.
 
  • #40
If you are talking in terms of the proportion of electrical energy supplied that provides water heating then you should really include the efficiency of RF equipment to provide the RF power. That makes the simple resistive heating solution the winner.
 
  • Like
Likes DaveE, hutchphd and Bystander
  • #41
FJT2 said:
The improved efficiency could come from use of a continuous flow heater that uses an Iron pipe to heat the water on demand, giving instantaneous heat, and eliminating losses due to storing heated water for a long period. Unfortunately the iron pipe may have a relatively short lifespan.
Welcome to PF.
You may never beat an immersed resistive element, but you might come a close second.
Why not replace the iron with a thin walled bronze tube that acts as a shorted turn ?
What range of operating frequency would you consider. Maybe down to 50/60 Hz ?
Can you pre-heat water by cooling the primary induction coil and the frequency generator ?
 
  • #42
As @sophiecentaur and @Baluncore already pointed out RF heating is not as efficient as simple resistive heating due to the extra energy being drained in charging discharging the capacitance of the heating element and driving the overall reactance of the circuit.

I guess we could go further and say that even among resistive heating elements the absolute highest efficiency would be for one being fed by DC current as AC even at low frequencies still have some losses due to reactance of the of element and wires, but those are so tiny that I think it would be hard to even measure them.
 
  • #43
artis said:
... as AC even at low frequencies still have some losses due to reactance of the of element and wires, but those are so tiny that I think it would be hard to even measure them.
The reactance does not cost real watts, only imaginary VAR.

When you need to limit current, such as in or with a solenoid, it is better to use AC with inductance than DC with resistance. That is because the inductive reactance does not generate heat.

To heat something there need to be real watts developed in a resistive element.
 
  • Like
Likes hutchphd
  • #44
Baluncore said:
That is because the inductive reactance does not generate heat.
Not by itself but the extra current associated with it does in the form of heat generated within the wire. Isn't this the main reason utilities tend to care about controlling the grid power factor, apart from voltage stability ?
 
  • Like
Likes sophiecentaur
  • #45
Baluncore said:
The reactance does not cost real watts, only imaginary VAR.
The wasted I2R power is dissipated elsewhere. "Zere ist no escape Breetish Tommy".
But my initial objection to induction heating was based on what you can buy for cooking etc.. But a beefy transformer could be very local to the heating coil so the low voltage parts of the circuit could involve less loss.
Total cost and scale should also be considered - as in the arguments for Electric Cars - (even down to the transformer and non-mass production of parts).
 
  • #46
Profanity edited out of post by the Mentors
I absolutely love this thread. It is one of the clearest demonstration of the complexity of "energy efficiency" discussions on one end, and of how something as trivial as heating water is in fact, a pretty deep and somewhat convoluted thing.
I am one of the few human beings alive having visited multiple electric water heater factories (these guys don't joke around their industrial secrets!) I have been amazed at how complex and counterintuitive heating water can be.
In strictly electric heating, there's no doubt that resistive wins, if for no other reason that there's little else to measure it against and for most of the reasons listed below. In no way does this mean it's the best or the most efficient, but merely that "it's the best we have for the money".
The conductive heat loss is not insignificant and (for most north-american models) hovers around 90W h. So efficiency should also relate to conservation. Or storage. Whatever energy buzzword you want to tack on there.

Efficiency also means having a durable, reliable equipment. And truth be told, the vast majority of EWH elements have grown to be absolute garbage over the past decade, leading to a record number of failures. These are generally not noticed in 2-elements tanks, or at least, not as much.

It's also helpful to know that US-made and Canadian-made EWH are not the same: they do not answer to the same efficiency standards and while they look similar there are key differences in their designs, not the least of which the number of elements and the temperature set point.

Finally, take other means "more efficient" means with a grain of salt: heat-pump EWH are incredibly efficient. They are also the worse possible idea in nothern climates... Geography counts a lot for "efficiency" and one needs to consider that the current resistive type might not be perfect, but it is the sum of all compromises and currently the one that serves us the best. Can we do better ? I sure hope we can :)

As for the OP's question, well, there are people (yours trully being one of 'em) working on induction-based water heating, not out of efficiency concerns, but out of public health concerns. Legionnaire's disease is far more rampant in EWH than most like to admit, and for areas where only electric is an option that are unfortunate to have that particular bacteria in abundance, there needs to be cheaper, more efficient solutions. That's part of what we're working on.
 
  • #47
ZeFrenchman said:
As for the OP's question, well, there are people (yours trully being one of 'em) working on induction-based water heating, not out of efficiency concerns, but out of public health concerns. Legionnaire's disease is far more rampant in EWH than most like to admit, and for areas where only electric is an option that are unfortunate to have that particular bacteria in abundance, there needs to be cheaper, more efficient solutions. That's part of what we're working on.
Welcome to PF.

Can you say more about how inductive heating can help cut down on the bacteria that cause Legionnaire's disease? It seems like you are right that it can be a problem for resistive WH designs:

https://plumbingperspective.com/does-your-hot-water-heater-protect-you-from-legionnaires-disease
 
  • #48
berkeman said:
Welcome to PF.

Can you say more about how inductive heating can help cut down on the bacteria that cause Legionnaire's disease? It seems like you are right that it can be a problem for resistive WH designs:

https://plumbingperspective.com/does-your-hot-water-heater-protect-you-from-legionnaires-disease
The prime issue with EWH and Legionnaire's is the configuration of the pressure vessel: with the resistive element a few inches from the bottom, there is a layer of cold water that simply never gets heated. And before someone screams equilibrium, the fact of the matter is that an EWH will typically never rest long enough (at least 3-4 days, in the best of cicumtances) to reach that state. Stratification is well known in WH but it is more problematic in electric, as that bottom layer will never get heated. The bottom is also, unfortunately, where the sludge of biofilm gets deposited, providing a superb environment for both areobic and anaerobic critters. Add to that a broken lower element, and you have yourself a petri dish of Legionella pneumophilae...

I'll add as a political statement that US-made EWH are somewhat worse in that fashion than Canadian-made EWH: in the US, an EWH is asked to "deliver hot water". So it makes sense to have 1 or 2 elements closer to the top of the tank, to provide faster recovery and more deliverability. This also means that the "cold zone" at the bottom is waaaay cold, a problem compounded by the fact that most state mandate 50°C as a storage setpoint. So, a perfect growth environment if contaminated.

Canadian-made EWH are tested to "keep water hot", meaning they want their bottom element closer to the bottom to promote uniformity, at the cost of a slower recovery time. As well, federal law mandates that water be stored no lower than 60°C.
Now, I'm cynical enough to accept that this is by accident, rather than design, but the problem exists nevertheless and the fact that EWH are now being promoted to the rank of energy storage devices in homes means we need to take a long look at that problem that went unnoticed or ignored for decades.

Gas-fired WH circumvent the issue by roasting the biofilm to a crisp with each cycle, so we are trying to achieve a similar effect with in induction-fired WH, where we can eliminate that cold bottom layer. The alternative of course is high-temperature WH, but that's a different beast and these make sens in different settings (think solar heating, energy storage, et al). Also, HTWH bring a load of new issues to the table (mixing valves, pressure vessel material, insulation, etc) and that's some distance out in left field from the original topic :)
 
  • Informative
Likes hmmm27, Bystander, DaveE and 1 other person
  • #49
And on the topic of tankless WH: they certainly do help the bacteria growth issue, but unless they are gas fired, they should be considered an abomination to our not-so-modern North American power grid: it just can't take the strain of toasting your bread, making your coffee AND charging your car, let alone heating your shower at the same time... That dynamic alone warrants that we look into different EWH solutions, even at the cost of apparent efficiency, if it means displacing load on the power grid.

It's another direction to that topic, but it ties well into the conversation.

Full disclaimer: the reasoning above is only sound in my world, the frozen hell of Hoth. Not so much in warm-weather geography or where wind/sun/thermal might be available on the cheap.
 
  • #50
@ZeFrenchman or should I greet you by "Salut!"?

What you say is interesting. Where I live we use a lot of electric "boilers", almost every other home has one, as the only other option to heat water is from the heating furnace that heats the house to pass through circulation through an accumulation boiler, which is also another popular way, the third is to use natural gas.
Honestly I have never heard of a single outbreak in the past couple of decades , well I have heard about them but in fact not in association with the boilers, rather in places where water has been stagnant for a long time, like cases where owners go for a long trip or the flat/house isn't inhabited for some time.
Could it be that it is more prevalent for standing water?
I myself have a electric boiler which works exactly like you described, vertical pressure vessel, heating element resistive and placed at the bottom.

One other important thing is to clean them regularly. I clean myself either once a year or twice , lately the water quality has become better so once is enough.

I am not sure with this one so correct me but I would think the filtration of the city water supply before it is even pumped into pipelines for distribution to houses is also important, in Europe we in general tend to have strict controls over that to prevent microorganisms from building up in the pipes.
But as I said I have mostly only heard about the disease with respect to long standing water , wherever water is used regularly I have never seen a problem with it.

But it seems your logic is correct, a heating supply that heats the water and surrounding container evenly to high temp is better than one which only partially heats to high temp while leaving other parts to lower temps where bacteria can thrive, combine that with a local badly filtered supply coming from a lake or ground/river and you potentially have problems
 
  • Like
Likes russ_watters
  • #51
artis said:
@ZeFrenchman or should I greet you by "Salut!"?

What you say is interesting. Where I live we use a lot of electric "boilers", almost every other home has one, as the only other option to heat water is from the heating furnace that heats the house to pass through circulation through an accumulation boiler, which is also another popular way, the third is to use natural gas.
Honestly I have never heard of a single outbreak in the past couple of decades , well I have heard about them but in fact not in association with the boilers, rather in places where water has been stagnant for a long time, like cases where owners go for a long trip or the flat/house isn't inhabited for some time.
Could it be that it is more prevalent for standing water?
I myself have a electric boiler which works exactly like you described, vertical pressure vessel, heating element resistive and placed at the bottom.

One other important thing is to clean them regularly. I clean myself either once a year or twice , lately the water quality has become better so once is enough.

I am not sure with this one so correct me but I would think the filtration of the city water supply before it is even pumped into pipelines for distribution to houses is also important, in Europe we in general tend to have strict controls over that to prevent microorganisms from building up in the pipes.
But as I said I have mostly only heard about the disease with respect to long standing water , wherever water is used regularly I have never seen a problem with it.

But it seems your logic is correct, a heating supply that heats the water and surrounding container evenly to high temp is better than one which only partially heats to high temp while leaving other parts to lower temps where bacteria can thrive, combine that with a local badly filtered supply coming from a lake or ground/river and you potentially have problems
Et salut à toi ;)

Yes, geography matters a great deal when it comes to the Legionella conversation, since areas see both various water heating technologies and exposure to the bacteria. But last we checked, not a single water utility (in North America anyway) filtered or otherwise treated water against Legionella pneumophila, a bacteria found in many water ways around the world. Frankly, I'm not certain they could even if they wanted to...

Standing water does increase biofilm, thus risk, but isn't a requirement to bacteria growth in water heaters, mostly because of the advantage provided by the mild water temperature. France has seen its fair share of challenges with this in the early 00's if memory serves.

The challenge in under-reporting and the associated issues in sampling (See Dr Janet Stout on that topic, great work) is exactly that: under reporting. Whenever an outbreak appears, it drives ressources and energy to finding the source, often times an HVAC cooling tower or some public water feature. But when people, usually a single person, shows up at the hospital with Legionaires and often enough dies from it, no one ever investiguates.

And unfortunately, once corrected for under reporting, the stats can be a lot grimmer: Dr.Michel Plante (Hydro Quebec, Canada) reported recently that he figured 7 people died yearly from Legionaires contracted from their EWH (which makes up the majority of WH in that area). Some argue that his studies take a few shortcuts, but the fact remains that somewhere between "no problem" and "we'll all die from a hot shower" lies a poorly documented and understudied problem.
 
Last edited by a moderator:
  • #52
ZeFrenchman said:
no one ever investiguates
My best friend is retired from the US Public Health Service. He spent almost all his time in recent decades running to every outbreak to investigate.
 
  • Like
  • Wow
Likes russ_watters and berkeman
  • #53
My son is a licensed plumber. He says that the plumbing code in his state specified 120F (50C) as the maximum legal hot water temperature. Scalding burns are possible if hotter.

However, the legionnaires literature here says that hot water tank temperatures must not be lower than 60C (140F) to prevent growth of the bacteria.

Both can be satisfied with a mixer between tank and faucet that blends hot water with cold water to guarantee water no hotter than 120F at the faucet, regardless of tank temperature. But I've never seen a residence with such a mixer.

My son also said that using up your hot water, prevents it from being stagnant. Problems occur if hot water is stored weeks or months below 60C with no circulation. Hot tubs have that situation more often than hot water heaters.
 
  • Like
  • Informative
Likes OmCheeto, russ_watters and berkeman
  • #54
All is lost without the technology to contain and heat water.
You know you are civilised, when you can make a hot cup of tea.
 
  • Haha
Likes anorlunda
  • #55
anorlunda said:
My best friend is retired from the US Public Health Service. He spent almost all his time in recent decades running to every outbreak to investigate.
And his general conclusions are?
 
  • #56
Tom.G said:
And his general conclusions are?
Baluncore said:
All is lost
 
  • Wow
Likes Tom.G
  • #57
Well, that escalated quickly... ;)
 
  • #58
anorlunda said:
My best friend is retired from the US Public Health Service. He spent almost all his time in recent decades running to every outbreak to investigate.
To clarify: Legionnaires disease is a reportable disease in most countries with a solid public health system. This means that there generaly are investigations for reported cases, but they are generally centered around reports with more than one case for a general area as it often points to a community source (think of a HVAC cooling tower on top of a building blowing bacteria in the wind...). As literature points out however, investigating individual cases and the technical difficulty of sampling water heaters makes it nearly impossible to identify and link bacterial sources to an individual's disease.

Technological advances in DNA field analysis might help this in the future.
 
  • Like
Likes anorlunda
  • #59
anorlunda said:
My son is a licensed plumber. He says that the plumbing code in his state specified 120F (50C) as the maximum legal hot water temperature. Scalding burns are possible if hotter.
Funny enough, the consensus around the scalding temperature seems to be a correlated with litigation: a very cynical research collaborator once told me: "burn victims cost a fortune, dead people can't sue". A bit harsh, but it does seem to represent the industry's desire for lower water temperature vs preventing bacteria growth in systems. That particular aspect isn't much of an issue for residential, but it seems to be responsible for many outbreaks in institutional settings.
anorlunda said:
Both can be satisfied with a mixer between tank and faucet that blends hot water with cold water to guarantee water no hotter than 120F at the faucet, regardless of tank temperature. But I've never seen a residence with such a mixer.
True and it's certainly part of the solution. We have a number of consumer-grade high-temperature water heaters on trial here and they all have a built-in mixing valve. It does look promising.
anorlunda said:
My son also said that using up your hot water, prevents it from being stagnant. Problems occur if hot water is stored weeks or months below 60C with no circulation. Hot tubs have that situation more often than hot water heaters.
Also very, very true about hot tubs or whirlpools. They are certainly guilty of harboring nasty critters (I'm also told that it would explain in great part their disapearance from hotels and such). For the water heater, using it up might not do much unfortunately, since the pressure vessel doesn't "circulate" per se. Depending on make an model, some areas of the tank can remain fairly undisturbed, specially at the bottom, where evil lurks...
 
  • Informative
Likes DaveE
  • #60
Baluncore said:
You know you are civilised, when you can make a hot cup of tea.
On a campfire, in a clay pot?
 
  • #61
The risk of legionella is certainly not zero, but it's pretty speculative to say that there is a high risk that isn't documented. Without evidence, it's just a guess. The CDC does list water heaters, and I see sources speculating on the impact of buildings going vacant due to COVID, but I'd like to see real research/stats into sources of actual infection.

I'm in HVAC and of course it is a big concern in cooling towers and air conditioner condensate, but as others suggest I'm not even seeing a logical reason why it would be a significant risk for water heaters, much less documented evidence of the risk.

Further, legonnaire's is a lung disease. You get it by breathing the bacteria, not drinking it. It's obvious how a cooling tower or air conditioner would promote inhalation, but less obvious/efficient for, say, a drinking fountain.

But as I said, I'm an engineer, not an epidemiologist.
 
Last edited:
  • Like
Likes Astronuc
  • #62
I would like to add a new factors in this discussion of water heating to remind everyone to remember minority use cases and not just mainstream use cases. The topic of heating water can be very broad.

I live in an RV with 1500 watts electric service. To use the AC I need to shut the hot water off.

I was considering a DIY solar HW heater project.
1652200531834.png

But that needs a circulation pump, plus a way to prevent overheating/overpressurization, and a way to drain it when I leave for the winter to prevent freezing, or to fill it with antifreeze and use an intermediate heat exchanger. The complexity adds up fast. My DIY skills and DIY tools are very limited.

Instead, I intend to use the existing water heater's solutions for all those problems. I plan to get a 200 watt solar panel, plus an inverter. I'll swap the 1200w resistive heating element for a 150w element. Then I can disconnect the entire system from the grid and feed it from the inverter. No parallelization of inverter and grid. No mains electric. No safety problems with rewiring the internals of a water heater. I'm not concerned with fast HW recovery, or about running out of HW during the night.

We also lived on a sailboat for 12 years. We had no HW tank. In those years, we found that a sun shower was a delightful source of hot water for showers. It heats up in only 30 minutes at midday. And showering on deck in a bathing suit with the bright sunlight and open air feels good. In places like The Bahamas, fresh water is scarce. The Sun Shower also had the benefit of saving fresh water. 4-6 liters was ample for one shower.
1652201066064.png
 
  • Like
  • Informative
Likes OmCheeto, DaveE, russ_watters and 1 other person
  • #63
anorlunda said:
I'll swap the 1200w resistive heating element for a 150w element.
You may want to check what the maximum water temperature will be with that 150W heater. You could end up shooting yourself in the foot if the water is maintained around body temperature -- ideal temperature for the nasties to grow.

Try to measure the water temperature drop over a period of time. That, along with the water volume, unit conversions, and some arithmetic, will yield rate of heat loss at present ambient temps.

EDIT:
Oops! I missed the post where that was mostly addressed.
The conductive heat loss is not insignificant and (for most north-american models) hovers around 90W h.

Cheers,
Tom
 
Last edited:
  • #64
But I still can't imagine that the losses in the induction 'amplifier' can be ignored compared with 'no loss' with a resistor within the water.

I was wondering whether a heat pump arrangement could be used to heat some circulating water to a safe temperature and then using that heat to heat up the next lot. I think perhaps two reservoirs of water would be needed for the system to work without actually mixing the previously heated water with the not-yet heated water.

These things make me feel so old. Legionnaire's disease was not heard of when I was a lad. Suddenly, everyone was getting it.
 
  • #65
Tom.G said:
Try to measure the water temperature drop over a period of time. That, along with the water volume, unit conversions, and some arithmetic, will yield rate of heat loss at present ambient temps.
That would be a useful experiment. Thanks Tom. Actually, I have the same situation in two RVs, but one of them has a 20 gallon tank electric, and the other one has a small tank maybe 5 gallons electric/propane. The two may give very different results.
 
  • #66
russ_watters said:
The risk of legionella is certainly not zero, but it's pretty speculative to say that there is a high risk that isn't documented. Without evidence, it's just a guess. The CDC does list water heaters, and I see sources speculating on the impact of buildings going vacant due to COVID, but I'd like to see real research/stats into sources of actual infection.

I'm in HVAC and of course it is a big concern in cooling towers and air conditioner condensate, but as others suggest I'm not even seeing a logical reason why it would be a significant risk for water heaters, much less documented evidence of the risk.

Further, legonnaire's is a lung disease. You get it by breathing the bacteria, not drinking it. It's obvious how a cooling tower or air conditioner would promote inhalation, but less obvious/efficient for, say, a drinking fountain.

But as I said, I'm an engineer, not an epidemiologist.
It's actually fairly well documented. The part I complain about is the lack of awareness about said studies and documentation. ASHRAE has documented the phenomenon extensively, albeit mostly in institutional settings. Special Pathogen Laboratories and their various commercial counterparts have also produced a lot of reports on the topic. I believe Dr Janet Stout's team might be the only one that has extensively looked at it from the residential perspective, in English anyway. There is extensive research that has been done in Quebec, as the state-owned utility decided to sell its water heater rental business in a hurry back in the early 00's, citing - internally of course - a "reputational risk" associated with, well, people dying from using their water heaters. While heavily poticized, that story has yielded a lot of good data. All in French of course :)

The bottom line is that 1 in 3 is contaminated, and 1 in 5 is set a temperature that is too low or has a defective bottom element. Where you are correct in saying about a guess, it's that last line between that data and the reported yearly cases in Legionaires (and to be precise, those that occur in winter, where no cooling tower can be blamed, at least here in the northern climates). That's the part that really needs a better focus methinks.

As for the infection path, it's the shower. To a lesser extent, faucets in general, but mostly either shower head or unsufficiently heated water sprayed in the shower. ASHREA's 188 committee is and has discussed this fairly extensively.

I'll try to come up with the references and links I mention here in a comprehensive list, but I also realize I've completely hijacked this thread, now way beyond what the OP asked. I'll probably start another one.
 
  • Informative
  • Like
Likes Astronuc and berkeman
  • #67
sophiecentaur said:
Interesting idea.
Most jewellery is made of metals with high conductivity and such items are small, so the I2R heating would be small. I could imagine a 'retro' iron bangle could be a problem but even that would probably have too small an area to link to the induction field and would be too far away from the induction coil.
artis said:
@sophiecentaur well I think unless someone is a hardcore metal chain fan I think induction cooking is safe.
Unless you happen to have an embedded pacemaker. People with pacemakers need to stay away from induction appliances.
 
  • #68
gwnorth said:
Unless you happen to have an embedded pacemaker. People with pacemakers need to stay away from induction appliances.
"Man dies from hugging his water heater" is a headline I don't think we'll see soon.

https://pubmed.ncbi.nlm.nih.gov/16635999/
 
  • #69
This has been an over-long thread, imo and that may be due to the use of the word "efficient", which could perhaps be replaced usefully with "effective". Then we would know better what to be discussing.
 
  • #70
ZeFrenchman said:
It's actually fairly well documented. The part I complain about is the lack of awareness about said studies and documentation. ASHRAE has documented the phenomenon extensively, albeit mostly in institutional settings. Special Pathogen Laboratories and their various commercial counterparts have also produced a lot of reports on the topic. I believe Dr Janet Stout's team might be the only one that has extensively looked at it from the residential perspective, in English anyway. There is extensive research that has been done in Quebec, as the state-owned utility decided to sell its water heater rental business in a hurry back in the early 00's, citing - internally of course - a "reputational risk" associated with, well, people dying from using their water heaters. While heavily poticized, that story has yielded a lot of good data. All in French of course :)

The bottom line is that 1 in 3 is contaminated, and 1 in 5 is set a temperature that is too low or has a defective bottom element. Where you are correct in saying about a guess, it's that last line between that data and the reported yearly cases in Legionaires (and to be precise, those that occur in winter, where no cooling tower can be blamed, at least here in the northern climates). That's the part that really needs a better focus methinks.

As for the infection path, it's the shower. To a lesser extent, faucets in general, but mostly either shower head or unsufficiently heated water sprayed in the shower. ASHREA's 188 committee is and has discussed this fairly extensively.

I'll try to come up with the references and links I mention here in a comprehensive list, but I also realize I've completely hijacked this thread, now way beyond what the OP asked. I'll probably start another one.

ZeFrenchman, your hijack of the thred I found fascinating! Sorry to the original poster. In my search of cooling rod materials for nuclear reactors, I landed here!
 
Last edited by a moderator: