Is Replacing a 25 kVAr Unit with Two 12.5 kVAr Units More Efficient?
Replacing a 25 kVAr unit with two 12.5 kVAr units can enhance efficiency based on site demand data, which indicates that peak requirements rarely exceed 30 kVAr and often only need 12.5 kVAr. The recommendation stems from the analysis of interval data, suggesting that smaller units provide better power factor correction for varying loads. Economic justification for this change largely depends on how the energy supplier bills for power factor; utilities may charge for capacitive power factor, influencing the decision. If the utility does not impose such charges, the cost-effectiveness of the new arrangement may not be justified. Ultimately, the decision should be based on a thorough analysis of energy costs and power factor billing practices.
AbdullahS
TL;DR Summary
Advice needed on Power Factor Correction Unit upgrade
Hi all,
The power factor correction unit for one of the buildings that I am working on needs maintenance. The service report recommends replacing the existing 25 kVAr unit with 2 x 12.5 kVAr units as "the demand on your site according to the data supplied shows us that at most there is only 30kVAr required at peak demand and quite often only requires 12.5kVAr".
This has been recommended after the analysis of interval data. The following graph shows the KVAr at the site for a period of 3 months.
Could you please advice if replacing the larger bank with two 2 smaller capacitor banks justified? If so, what is the reason? Shouldn't the old one do the job even when the kVAr requirement is low?
A bit of background about myself:
I am a mechanical engineer who is working in sustainability industry. I do have basic knowledge of reactive power but not detailed enough to answer questions such as these.
Thanks in advance.
Regards,
Abdullah
Whether the change is a good economic decision (or not) depends primarily on how your energy supplier bills for Power Factor. In the simplest case, Power Factor correction systems add capacitance to 'offset' the inductive character of most loads. A 'too large' correction will leave your power factor 'too capacitive.' 2 smaller systems would allow closer to ideal (net zero) correction for a range of loads. As I understand it, some utilities charge for capacitive PF, and some don't - if yours does bill for capacitive PF, you'll need to compare the 'do nothing' cost to the cost of the new arrangement. If they don't bill for capacitive PF, you probably can't (economically) justify the change.
Likes berkeman
Thanks @Dullard!
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...