tsutsuji said:At unit 2 the problem was not running out of water. The problem was the RCIC stopping for some not well identified reason :
The RCIC still needs battery power for operating valves and this could have run out. Another possibility is that, since the RCIC uses the suppression chamber pool as its heat sink, which is also heated by venting from the RPV, the suppression chamber pool became too hot to condense steam, which would stop the RCIC turbine.
Also, we should remember that not all units had an RCIC: Unit 1 only had an isolation condenser and perhaps not by coincidence, is assumed to have suffered meltdown only about 5 hours after station blackout, 2-3 days before the other units.
Great suggestions in http://sustainableenergytoday.blogspot.com/2011/07/post-47-tv-asahi-interview-on-bwr.html" :
Assured containment cooling: A secure means of cooling the primary containment pressure suppression pool and drywell atmosphere under SBO conditions. A number of options are possible, but the use of diesel-driven RHR pumps and drywell coolers powered by backup power systems are options.
Had there been a way of using temporary sea-water pumps to cool the suppression chamber or containment, the RCIC could have operated longer and containment venting would have been much less urgent, as steam could have continually been condensed inside.
Also, if the designers of the RCIC had run a generator off its steam turbine and not just a water pump, the dependence on batteries for operating RCIC valves would not have been its Achilles heel.