- #36
jim hardy
Science Advisor
Gold Member
Dearly Missed
- 9,832
- 4,895
sophiecentaur said:It is, afaiaa, forbidden to connect the neutral to Earth in your house because it would interfere with this floating situation. I have no company Earth conductor and there must be a local Earth somewhere. I hope it is more than just the water system.
Hmmm interesting.
In US we have to provide a low impedance all metal path for fault current back to the transformer winding from which it came. That path is to be independent of Earth ground, because Earth is likely a few ohms not the fraction of an ohm you get from an all metal path. It is also independent of Neutral, the return path for load current.* see edit below...
That path can be wire, metallic conduit, or metal raceway.
That path has recently come to be called in our electrical code the "Bonding conductor" , and it carries fault current back to its source, the service transformer,
as opposed to the "Grounding conductor" which ties the bonding conductors (and neutral conductor) to Earth ground and should carry only small amounts of current.
The revised terminology has caused much confusion in US electrical code circles.
*edit it is still common practice though, on utility side of meter, to use a single conductor to provide return path for both both Fault and neutral currents. My house has three wires coming in from pole to meter. But i must run four conductors to my new guest house, two hots a neutral and the equipment bonding conductor. Since i ran plastic conduit out to it i ran a fourth wire for bonding .
You Brits can easily get by with three wires since you have only one 'hot', i'd think. But where's your low impedance fault return path in a two wire feed ?
old jim