NEC 408.3.E: 3-Phase Busbar Arrangement

  • Thread starter Thread starter MitYeltu
  • Start date Start date
Click For Summary
NEC 408.3.E specifies that in a 3-phase busbar arrangement, the phases must be labeled A, B, and C in a consistent order, with B having the highest voltage to ground in delta-connected systems. This has raised confusion regarding the balance of voltages in a 3-phase system, as it is typically expected to be balanced barring unbalanced impedances. The discussion highlights that in a High Leg Delta configuration, it is indeed impossible for all three phases to maintain the same voltage to ground due to the grounding method used. Additionally, it is noted that the correct terminology when discussing busbars should refer to them as "legs" rather than "phases." Overall, the conversation emphasizes the need for clarity in understanding the implications of these configurations in electrical systems.
MitYeltu
Messages
8
Reaction score
0
NEC 408.3.E reads as follows

The phase arrangement on
3-phase buses shall be A, B, C from front to back, top to
bottom, or left to right, as viewed from the front of the
switchboard or panelboard. The B phase shall be that phase
having the higher voltage to ground on 3-phase, 4-wire,
delta-connected systems. Other busbar arrangements shall
be permitted for additions to existing installations and shall
be marked.

Have I missed the boat on this? A 3-phase system with a higer voltage on phase B than on phases A and C? I don't understand this. I thought a 3-phase system was, barring unbalanced impedances, balanced. What did I miss here?
 
Engineering news on Phys.org
MitYeltu said:
Have I missed the boat on this? A 3-phase system with a higer voltage on phase B than on phases A and C? I don't understand this. I thought a 3-phase system was, barring unbalanced impedances, balanced. What did I miss here?
Nothing. You are right. I have no idea why they said B is higher.
 
With High leg Delta configuration, ground is connected to the center tap of one of the transformers. It is then impossible to have all three legs at the same voltage in reference to ground. Which one you want to call A, B, or C is whatever someone decides.
-
When referring to buses, the terminology should be legs, not phases. A phase is a pair of conductors. Ideally all three phases will have the same voltage.
 
  • Like
Likes Asymptotic
Thread 'I thought it was only Amazon that sold unsafe junk'
I grabbed an under cabinet LED light today at a big box store. Nothing special. 18 inches in length and made to plug several lights together. Here is a pic of the power cord: The drawing on the box led me to believe that it would accept a standard IEC cord which surprised me. But it's a variation of it. I didn't try it, but I would assume you could plug a standard IEC cord into this and have a double male cord AKA suicide cord. And to boot, it's likely going to reverse the hot and...

Similar threads

  • · Replies 26 ·
Replies
26
Views
3K
  • · Replies 17 ·
Replies
17
Views
6K
  • · Replies 3 ·
Replies
3
Views
3K
Replies
10
Views
15K
Replies
23
Views
6K
  • · Replies 4 ·
Replies
4
Views
2K
  • · Replies 8 ·
Replies
8
Views
2K
Replies
11
Views
2K
  • · Replies 2 ·
Replies
2
Views
2K
  • · Replies 11 ·
Replies
11
Views
2K