Sorry for bad title(little informative regarding my question), however I came across the following question given as an exam question at some university.
Question:
"A synchronous generator is running overexcited with excitation voltage Ef = 1.40 p.u and connected to the network at voltage of 1 p.u. This generator has synchronous reactance of 1.20 p.u., and delivering active power of 0.50 p.u. to the network. In the network, there is 1% increase in real power due to power drop from uncontrolled network connected renewable power source. Therefore, the prime mover (i.e. turbine) input is increased by 1%. The excitation or voltage controller of synchronous generator is not responding to this change. Explain how the reactive power delivery from the synchronous generator will change under this condition"
So, the Q delivered by the generator per phase is:
[itex]Q = \frac{E_fV_t}{X_d}cos(\delta)-\frac{V_{t}^{2}}{X_d}-V_{t}^{2}(\frac{1}{X_d}-\frac{1}{X_q})sin^2(\delta)[/itex] (1)
So according to this equation the Q will not change due to increase in turbine input.
However if we take a look at this equation:
[itex]P = \frac{E_fV_t}{X_d}sin(\delta)-\frac{V_{t}^{2}}{X_d}-V_{t}^{2}(\frac{1}{X_d}-\frac{1}{X_q})sin(2\delta)[/itex] (2)
An increase of P will cause an increase in [itex]V_t[/itex], and an increase of [itex]V_t[/itex] will increase the reactive power delivered by the sync. generator according to equation (1)
Can someone tell me if this is the right way of thinking or if I am missing something please tell me.
Best Regards
Question:
"A synchronous generator is running overexcited with excitation voltage Ef = 1.40 p.u and connected to the network at voltage of 1 p.u. This generator has synchronous reactance of 1.20 p.u., and delivering active power of 0.50 p.u. to the network. In the network, there is 1% increase in real power due to power drop from uncontrolled network connected renewable power source. Therefore, the prime mover (i.e. turbine) input is increased by 1%. The excitation or voltage controller of synchronous generator is not responding to this change. Explain how the reactive power delivery from the synchronous generator will change under this condition"
So, the Q delivered by the generator per phase is:
[itex]Q = \frac{E_fV_t}{X_d}cos(\delta)-\frac{V_{t}^{2}}{X_d}-V_{t}^{2}(\frac{1}{X_d}-\frac{1}{X_q})sin^2(\delta)[/itex] (1)
So according to this equation the Q will not change due to increase in turbine input.
However if we take a look at this equation:
[itex]P = \frac{E_fV_t}{X_d}sin(\delta)-\frac{V_{t}^{2}}{X_d}-V_{t}^{2}(\frac{1}{X_d}-\frac{1}{X_q})sin(2\delta)[/itex] (2)
An increase of P will cause an increase in [itex]V_t[/itex], and an increase of [itex]V_t[/itex] will increase the reactive power delivered by the sync. generator according to equation (1)
Can someone tell me if this is the right way of thinking or if I am missing something please tell me.
Best Regards