The relay control circuit for driving the forward and reverse terminals of a gate motor is designed to prevent simultaneous activation through electrical interlock, using normally closed switches to ensure mutual exclusivity. Concerns were raised about handling voltage transients from small induction motors, with discussions on the effectiveness of R/C snubber circuits versus bi-directional TVS diodes for transient suppression. It was noted that if a fuse blows, the system continues to operate but without transient suppression, leading to potential silent failures. The design also considers the need to manage arcing across relay contacts due to high voltage spikes when switching the motors on and off. Overall, the focus is on ensuring reliable operation while minimizing electrical interference and protecting the system from transient damage.
neilparker62
Science Advisor
Homework Helper
Insights Author
Messages
1,191
Reaction score
683
Would like to check if the following relay control circuit work for driving forward and reverse terminals of a gate motor will work? Relays are connected for 'electrical interlock' meaning it should not be possible for both fwd and rvs terminals to be activated at the same time. Physically that is implemented as a jumper wire between the relay commons. If the fwd n/o is closed, the right hand motor will be connected and vv for the reverse. If both fwd and rvs are somehow activated at the same time, both n/c s will be open and there will be no connection to either terminal.

What is the "conventional wisdom" on dealing with transients from small induction motors such as these ? Are we still using standard R/C snubber circuits or are the bi-directional TVS diodes a better option. Or maybe even both ?

Design notes / recommendations on fuses and TVS diodes below are from Chatgpt.


1746680869129.webp


Design Notes
Motors: 230 V AC, 0.5 HP induction motors.
Motor windings: 10 ohm resistance, 90 mH inductance.
TVS Diodes: SMCJ440CA — bidirectional, 440 V clamping.
Fuses: 500 mA fast-blow, 600 V AC rated — placed in series with each TVS diode.
Purpose: Suppress voltage transients across motor windings during switching by relays.
 
Engineering news on Phys.org
The first thing I noticed is that if you blow one of those fuses, the system will still operate, but the voltage transients will be entirely unsuppressed. You will have a silent failure. On the other hand, this motor looks like it's 1/4HP or less. So those transients are more likely to show up as EMF interference than actual circuit damage.

The second thing is that supposedly, you are trying to protecting other devices that share the same power source as this motor - or perhaps suppress EMF. And you are depending on the impedance/resistance of the power lines to this motor system to make sure that most of the transient power is absorbed through the diodes and not transmitted. This may or may not be good enough. If it isn't, you may want to loop the live power line just before it reaches the switches to provide a bit more impedance.

The third thing: I know you're using break before make from your discussion. But I can't tell whether those extra lines in your schematic are intended to show that.
 
Last edited:
  • Informative
Likes neilparker62
Where is the phase shift capacitor that generates the rotating field?

If you switch from forward to reverse without waiting for the armature to stop, you will generate a high current pulse, and a physical shock to the motor.
 
  • Informative
Likes neilparker62
.Scott said:
The third thing: I know you're using break before make from your discussion. But I can't tell whether those extra lines in your schematic are intended to show that.
If you mean these:

1746721802759.webp


They are the normally closed switched on the relays. Current paths to the respective motors are as shown below. If both relays are activated at the same time , both normally closed switches will be open. So the red and green current paths are mutually exclusive. In effect the relay connections are implementing an XOR gate.

1746722749184.webp
 
Baluncore said:
Where is the phase shift capacitor that generates the rotating field?

If you switch from forward to reverse without waiting for the armature to stop, you will generate a high current pulse, and a physical shock to the motor.
The relays are driven from program logic. A motor opening a gate will be stopped for a period before the reverse motor/winding is activated to close the gate.
 
.Scott said:
The first thing I noticed is that if you blow one of those fuses, the system will still operate, but the voltage transients will be entirely unsuppressed. You will have a silent failure. On the other hand, this motor looks like it's 1/4HP or less. So those transients are more likely to show up as EMF interference than actual circuit damage.

The second thing is that supposedly, you are trying to protecting other devices that share the same power source as this motor - or perhaps suppress EMF. And you are depending on the impedance/resistance of the power lines to this motor system to make sure that most of the transient power is absorbed through the diodes and not transmitted. This may or may not be good enough. If it isn't, you may want to loop the live power line just before it reaches the switches to provide a bit more impedance.
Noted - re silent failure. Thanks for pointing it out. We'll have to figure out how to deal with that situation.

Re protection - no other devices are connected. We are just trying to deal with arcing across the relay contacts caused by high voltage transient spikes when the motors are turned off/on.
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...