Storing Natural Gas from Well in Propane Tank?

In summary, the speaker has a natural gas well that runs at 11psi but has low volume. They are considering storing additional gas in a propane tank instead of drilling deeper. The current flow from the well only provides enough gas for hot water and a gas range. The speaker's annual gas bill is around $1,200 and they are looking for a solution to reduce their reliance on the gas company. They are considering using a compressor and drying tank, but it is expensive and not guaranteed to work. The expert suggests using a 50 gallon tank to store enough gas for a day, but more information is needed to make a sound decision.
  • #1
jimoferie
4
0
Hi experts!

As you will see I am NOT one but I have a rather unique problem in search of a solution.

I have a natural gas well that runs 11psi but has little volume because it is only 412 feet deep. Rather than pay thousands to drill to approx 850 feet to improve volume, I thought it might be possible to store additional natural gas from the well in a propane tank.

Current flow from the well provides enough gas to run the hot water tank and gas range only all year. I had the well bailed of water last summer. But, when I turned on the boiler this winter, the flow depleted the well in just one heating cycle. The boiler runs at 145-degrees farenheit. The thermostat is set at 68-degrees all winter. We are back to running the boiler off the gas company supply. Our annual gas company bill averages $1,200.00 with the latest (2005/2006) hikes.

We are in the Northeast. We use an average 1,000 cubic feet of gas company gas in a 12-month period at 4oz gas company line pressure. The gas company supply is shut off June/July/August/September.

If a tank is possible, how large a tank would be necessary to store enough gas well gas to be virtually free of the gas company supply?

Any help will be appreciated.

jimoferie
 
Engineering news on Phys.org
  • #2
Well if one uses about 1000 cuft of natural gas (mostly methane) from the gas company, then to be virutally free, one needs about 1000 cuft of gas from the well. The size of the tank would depend on demand, but the maximum size would be 1000 cu ft or ~7500 gallons for storage at atmospheric pressure. As you indicated the gas is supplied from the gas company at 4 oz or 1/4 psig (or about 14.95 psia). Integrating the production rate - consumption rate over a year should give some idea of the storage volume required. Find the point of maximum surplus and that is the size of the tank.

Bear in mind natural gas is mostly methane, as opposed to propane or butane.
 
  • #3
Astronuc said:
Well if one uses about 1000 cuft of natural gas (mostly methane) from the gas company, then to be virutally free, one needs about 1000 cuft of gas from the well. The size of the tank would depend on demand, but the maximum size would be 1000 cu ft or ~7500 gallons for storage at atmospheric pressure. As you indicated the gas is supplied from the gas company at 4 oz or 1/4 psig (or about 14.95 psia). Integrating the production rate - consumption rate over a year should give some idea of the storage volume required. Find the point of maximum surplus and that is the size of the tank.

Bear in mind natural gas is mostly methane, as opposed to propane or butane.

I really am a "dummy" when it comes to Physics & Math. How does one (figure) integrate the "production rate - consumption rate" over a year?
I chose a propane tank because they can be found rather inexpensively in our area, even though the psi from the well has never been above 11psi in the 10 years we have been using it. Refurbished tanks can be had between $500 & $750. To re-drill the well to 850 feet would be nearly $6,000.00.

A well driller said I could try a compressor and drying tank to suck more gas out of the well at a cost of $800.00 for the setup but there is no guarantee that the well won't fill again with water. Bailing the well costs $800.00 alone.

I certainly have a dilemma!

jimoferie
 
  • #4
If you use 1000 cubic feet of gas in a year, that is the volume the gas will fill at atmospheric pressure and temperature.

So in one day, you will use roughly 2.7 cubic feet of gas. To store that amount of gas (enough for a day) and still have roughly 1/4 psig when starting at 11 psig, you need aproximately 3.7 cubic feet of volume or about a 28 gallon tank.

Get a 50 gallon tank and allow it to fill to 11 psig and you should be good as long as you are regulating the pressure down to 1/4 psig to feed to your appliances.
 
  • #5
Q_Goest said:
If you use 1000 cubic feet of gas in a year, that is the volume the gas will fill at atmospheric pressure and temperature.

So in one day, you will use roughly 2.7 cubic feet of gas. To store that amount of gas (enough for a day) and still have roughly 1/4 psig when starting at 11 psig, you need aproximately 3.7 cubic feet of volume or about a 28 gallon tank.

Get a 50 gallon tank and allow it to fill to 11 psig and you should be good as long as you are regulating the pressure down to 1/4 psig to feed to your appliances.

Thanks for staying with this problem. I really appreciate it. I apologize for not having all the information to make a sound decision. The Gas Company bill shows CCF as "One hundred cubic feet of gas; a measure of quantity".

Let me give you our latest gas bill info and a historical perspective.

In the last 33 days (approx 16 days in February and 17 days in March) we used 174 cubic feet of gas company gas at a cost of $286.00 for a 1,000 sq. ft. well-insulated ranch. That's an average of 5.27 ccf per day. We live by Lake Erie. It has been colder than normal.

Here is a breakdown of the last 12 months:
2005: Jan/Feb 28 days:176 ccf . Feb/March 30 days:177 ccf . March/April 28 days: 114 ccf . April/May 35 days:72 ccf . Gas Off: May/June . June/July . July/Aug . Aug/Sept . Sept/Oct 27 days: 17 ccf
Oct/Nov 29 days: 61 ccf . Nov/Dec 31 days: 144 ccf . Dec'05/Jan'06 34 days: 153 ccf . Jan/Feb 27 days: 129 ccf . For all of 2005 we used 996 ccf, for all of 2004 (a warm Winter) we used 864 ccf.

Problem: The well will drop to nearly zero from 5psia on the well gauge when running the boiler off the well for just one cycle to bring the boiler temp to 145 degrees. The wall thermostat stays at 68 degrees. The boiler eats the gas pretty fast. Now, when it gets down to zero, I shut off the well to allow it to build back up. It took 21 days to build back up to 8-1/2 psia on the well guage. I switched the well back on today to handle the water tank and gas range again.

I have so many questions: Because it takes 21 days to recover just 8-1/2 psia maybe I need a much much bigger tank? Do I need a tank that can store much more than 177 cubic feet if the boiler burn rate is 5.27 ccf per 24 hours of boiler operation?

Maybe this is just not economically practical?

Thanks again for looking at this.
jimoferie
 
  • #6
The well will drop to nearly zero from 5psi(g) on the well gauge when running the boiler off the well for just one cycle to bring the boiler temp to 145 degrees. The wall thermostat stays at 68 degrees. . . . It took 21 days to build back up to 8-1/2 psia on the well guage.
The well has a certain volume in it that's able to provide for this surge of gas you need. The volume your well has was sucked dry in a matter of minutes or hours. It took a few weeks for the well to bring the pressure in that volume back up. The conclusion from what you just said is that the flow rate of gas coming from the well is an order of magnitude or more lower than you need. It doesn't matter what volume you put in the system. From what you just said here, the well is incapable of providing sufficient flow regardless of the volume. Putting in a 50 gallon volume might suffice for a day or so but obviously the well would never be able to fill it in that amount of time, it would take weeks or even months to fill that volume to a few psi.
 
  • #7
Q_Goest said:
The well has a certain volume in it that's able to provide for this surge of gas you need. The volume your well has was sucked dry in a matter of minutes or hours. It took a few weeks for the well to bring the pressure in that volume back up. The conclusion from what you just said is that the flow rate of gas coming from the well is an order of magnitude or more lower than you need. It doesn't matter what volume you put in the system. From what you just said here, the well is incapable of providing sufficient flow regardless of the volume. Putting in a 50 gallon volume might suffice for a day or so but obviously the well would never be able to fill it in that amount of time, it would take weeks or even months to fill that volume to a few psi.

Thanks Q_Goest.

I figured as much too. Every 21 days the well would recover only 8 psi or so. The boiler needs more than 5 ccf for one day's heating cycle. It's impossible. I would need a HUGE tank, maybe 10,000 gallons. It would be cheaper (but a gamble) to re-drill the well deeper. My only other option is to try a compressor to literaly suck more gas from the well's underground supply formation. That's an $800 deal by itself.

Anyway, thanks so much for your input. I will keep this post open for a week or so in case you (or someone else) has a better idea.

jimoferie
 

Related to Storing Natural Gas from Well in Propane Tank?

1. How is natural gas stored in a propane tank?

Natural gas is compressed and stored in a propane tank using high-pressure pumps. The gas is compressed to around 250 times its original volume, allowing for efficient storage in the tank.

2. What is the difference between storing natural gas and propane in a tank?

The main difference is in the pressure and volume of the stored gas. Propane needs to be stored at a much higher pressure than natural gas, which means it requires a stronger and more durable tank. Additionally, propane has a higher energy content per volume compared to natural gas.

3. How long can natural gas be stored in a propane tank?

The length of time that natural gas can be stored in a propane tank depends on various factors such as the tank size, pressure, and temperature. Generally, it can be stored for a few months to a year, but it is recommended to use it within a few months for optimal efficiency.

4. Can natural gas be converted into propane for storage?

Yes, it is possible to convert natural gas into propane through a process called liquefaction. This involves cooling the natural gas to a very low temperature (-260°F) until it turns into a liquid state, which can then be stored in a propane tank. However, this process is expensive and not commonly used.

5. Are there any safety concerns when storing natural gas in a propane tank?

Special precautions and safety measures must be taken when storing natural gas in a propane tank, as it is a highly flammable and potentially dangerous substance. Regular maintenance and inspections of the tank are necessary to ensure its safety. It is also important to follow proper storage and handling procedures to minimize any potential risks.

Similar threads

  • Mechanical Engineering
Replies
3
Views
1K
Replies
25
Views
3K
  • DIY Projects
2
Replies
39
Views
9K
Replies
13
Views
2K
  • Sci-Fi Writing and World Building
Replies
6
Views
2K
  • General Discussion
Replies
2
Views
2K
Replies
3
Views
2K
Replies
4
Views
3K
Back
Top