How Does Transmission Line Length Affect Voltage Loss?

In summary: You don't need λ to find the resistive losses in your power cable. Transmission line effects do not enter into this calculation, as long as the motor is consuming the power that is sent to it over the power cable. Think of it as a well-matched load termination -- there will be very little reflected power, even if your power cable were... 1/5 of a wavelength long.In summary, the conversation discusses the potential voltage loss in a system where a 120V 60Hz generator is connected to a 1000km wire with resistance R, leading to a motor down a well. The conversation delves into the calculation of wavelength and voltage using the speed of light and frequency,
  • #1
btb4198
572
10
Ok I do not know if I am right about this but :
if you have an AC 120 V 60Hz generator connected to a wire of Length L(1000KM) and Resistance R going to a motor down a well, to know if you will have Voltage loss you do

λ = C / F
C is the speed of Light = 299 792 458 m/s
F is the 60Hz
λ = 299 792 458 (m/s) / 60 Hz = 4996540.966666667 m
= 1000 Km / 4996540.966666667m = 0.20013845711889121639354535604153 = 20%
20% < 10% so there will be voltage loss.
and the end Voltage( Voltage to the Motor) will be Ve
Ve = 120 V Cos( 2 pi (60) 1000E3/ 299 792 458 ) = 120V ( 0.99975916026658575202469779578012) =
Ve = 119.97109923199029024296373549361 V
is that right ?
it seems small ...

Also should R and C play a part in the Voltage loss? I feel like I am going something wrong.
You loss Voltage because of power/ heat in the wire right ? so I2R?
so I feel like I should use R to get Ve ( Voltage at the motor)
 
Engineering news on Phys.org
  • #2
you postulate a 1/5 wavelength transmission line.

Indeed transmission line effects do happen on extremely long lines.

try this link starting about page 23.

https://ece.uwaterloo.ca/~raelshat/COURSES_dr/eleb7/NewNotes/Power%20System%20Components_Part1.pdf
 
Last edited by a moderator:
  • #3
jim hardy said:
you postulate a 1/5 wavelength transmission line.

Indeed transmission line effects do happen on extremely long lines.

try this link starting about page 23.

https://ece.uwaterloo.ca/~raelshat/COURSES_dr/eleb7/NewNotes/Power%20System%20Components_Part1.pdf
Jim Hardy,

I looked at your link, but It is not answering my questions.
did I solve for the Ve ( Voltage at the motor) right ? if not how should I have?
also should I use R and I so solve for Ve?
R is The distributed resistance
e1e1d3d40573127e9ee0480caf1283d6.png
of the conductors is represented by a series resistor (expressed in ohms per unit length).
 
Last edited by a moderator:
  • #4
btb4198 said:
Ok I do not know if I am right about this but :
if you have an AC 120 V 60Hz generator connected to a wire of Length L(1000KM) and Resistance R going to a motor down a well, to know if you will have Voltage loss you do

λ = C / F
C is the speed of Light = 299 792 458 m/s
F is the 60Hz
λ = 299 792 458 (m/s) / 60 Hz = 4996540.966666667 m
= 1000 Km / 4996540.966666667m = 0.20013845711889121639354535604153 = 20%
20% < 10% so there will be voltage loss.
and the end Voltage( Voltage to the Motor) will be Ve
Ve = 120 V Cos( 2 pi (60) 1000E3/ 299 792 458 ) = 120V ( 0.99975916026658575202469779578012) =
Ve = 119.97109923199029024296373549361 V
is that right ?
it seems small ...

Also should R and C play a part in the Voltage loss? I feel like I am going something wrong.
You loss Voltage because of power/ heat in the wire right ? so I2R?
so I feel like I should use R to get Ve ( Voltage at the motor)

Why are you running 120Vrms for 1000km? That is a very lossy setup. And it shouldn't have much to do with the wavelength, etc. It will be dominated by IR losses
 
  • #5
berkeman said:
Why are you running 120Vrms for 1000km? That is a very lossy setup. And it shouldn't have much to do with the wavelength, etc. It will be dominated by IR losses

1000Km is just an example ...
in the real world the oilwell are no more than 743.2m (9000 feet). But the motor would be at the bottom of the well connected to a pump.

anyhow,
did I do Ve right ?
 
  • #6
btb4198 said:
anyhow,
did I do Ve right ?

I don't think so, but I didn't really follow what you were trying to do. Once you mentioned the speed of light, I kind of zoned out reading the post... :woot:

To calculate the voltage loss across the cable, you need the total resistance of the cable, and the current flowing in the cable. If you know the wire gauge, you can use Google to find the resistivity in Ohms per thousand feet or similar dimensions. For a 1000m run of cable, you will have 2000m of wire (out and back). From the resistivity and cable length, you get your total resistance.

From the motor power, you get the input current: P = Vrms * Irms, assuming a reasonable power factor for the motor. Use that Irms * Rtotal to calculate how much Vrms loss you get across the cable. :smile:
 
  • #7
berkeman said:
I don't think so, but I didn't really follow what you were trying to do. Once you mentioned the speed of light, I kind of zoned out reading the post... :woot:

To calculate the voltage loss across the cable, you need the total resistance of the cable, and the current flowing in the cable. If you know the wire gauge, you can use Google to find the resistivity in Ohms per thousand feet or similar dimensions. For a 1000m run of cable, you will have 2000m of wire (out and back). From the resistivity and cable length, you get your total resistance.

From the motor power, you get the input current: P = Vrms * Irms, assuming a reasonable power factor for the motor. Use that Irms * Rtotal to calculate how much Vrms loss you get across the cable. :smile:

The motor run on 120V, I do not care to know the power, just to know if 120V is making it to the motor down the well.
why did you say you zoned out reading the post after I mention the speed of light ?
you need C to find λ
 
  • #8
You don't need λ to find the resistive losses in your power cable. Transmission line effects do not enter into this calculation, as long as the motor is consuming the power that is sent to it over the power cable. Think of it as a well-matched load termination -- there will be very little reflected power, even if your power cable were near λ long.

I don't care if you don't care to know the power. :smile: You need the Irms that is being fed to the motor to calculate the Vrms loss.

So for example, if the motor is 10hp, that's about 7500W, which is 7500W / 120Vrms = 62.5Arms. (that's a lot of current)

If you use 00 AWG cable (0.079 Ohms per 1000 feet), and the cable is 2000 feet long, that is 4000 feet of wire, which is 4 * 0.079 = 0.316 Ohms. So your V = I*R drop is about 62.5Arms * 0.316 Ohms = 20V. So your 120V starting voltage becomes about 100Vrms at the motor for a 2000 foot long 00 AWG power cable.

What is your motor power? What gauge are you planning on using for your power cable?NOTE -- I edited my post to fix a math error, in case you saw the longer version of it before I deleted it and fixed it.
 
  • #9
berkeman said:
You don't need λ to find the resistive losses in your power cable. Transmission line effects do not enter into this calculation, as long as the motor is consuming the power that is sent to it over the power cable. Think of it as a well-matched load termination -- there will be very little reflected power, even if your power cable were near λ long.

I don't care if you don't care to know the power. :smile: You need the Irms that is being fed to the motor to calculate the Vrms loss.

So for example, if the motor is 10hp, that's about 7500W, which is 7500W / 120Vrms = 62.5Arms. (that's a lot of current)

If you use 00 AWG cable (0.079 Ohms per 1000 feet), and the cable is 2000 feet long, that is 4000 feet of wire, which is 4 * 0.079 = 0.316 Ohms. So your V = I*R drop is about 62.5Arms * 0.316 Ohms = 20V. So your 120V starting voltage becomes about 100Vrms at the motor for a 2000 foot long 00 AWG power cable.

What is your motor power? What gauge are you planning on using for your power cable?NOTE -- I edited my post to fix a math error, in case you saw the longer version of it before I deleted it and fixed it.

WHy 4 * 0.079 = 0.316 Ohms ? and not 4000 * 0.079 ?
and why do I not need λ?
I am sorry, I thought λ is used for transmission lines and that this was a transmission line ...
is it not a transmission line ?
 
  • #10
btb4198 said:
WHy 4 * 0.079 = 0.316 Ohms ? and not 4000 * 0.079 ?

That's the math error that made me delete and fix my post. The resistivity is 0.079 Ohms per 1000 feet, not per foot. :smile:

btb4198 said:
and why do I not need λ?
I am sorry, I thought λ is used for transmission lines and that this was a transmission line ...
is it not a transmission line ?

No, transmission line effects do not come into play here. The wavelength in free space at 60Hz is about 300,000,000m/s / 60Hz = 5 million meters. That matters for long power transmission lines, but not for 1000m of cable. And again, your motor is absorbing most of the power sent to it over the power cable, so there is not much lost in reflection from the motor. Just stick with calculating the I*R losses in the cable for this situation. :smile:
 
  • #11
(λ) 20% < 10% so there will be voltage loss.

what does that mean ? I too tuned out because to me it's nonsensical unless you are trying to treat it like a "transmission line" as in radio and TV.
And your inequality sign points the wrong way ? 20% is > 10% .

At line lengths approaching 1/4 wavelength , that treatment becomes appropriate. Yours is 1/5 wavelength. So i gave you a link to that treatment of 60 hz power transmission lines. It's a real phenomenon.

A question well stated is half answered.
 
  • #12
berkeman said:
The wavelength in free space at 60Hz is about 300,000,000m/s / 60Hz = 5 million meters.

jim hardy said:
Yours is 1/5 wavelength.

Oops, did I make another math error?
 
  • #13
berkeman said:
Oops, did I make another math error?
more likely i made it.

Let's see c= 3e8 m/sec
divided by 60hz

equal 5e6 meters = 5,000km
and he said 1,000km ?
i think he's at 1/5 wavelength. That's why i answered the wrong question.
another "Red Herring" . No harm intended.

Power system guys do have to take into account that radio wave like behavior even at their measly 60 hz .
It's un-economic to let energy radiate into space because a long transmission line is acting like an antenna.
I think that's part of the reason for "transposing" the phases on long lines, to make them sort of a twisted pair.

Next time you drive along a long power line, like a hundred mile one, watch the lines and you'll see them roll the phases every few miles - i think like twenty. But don't take that number as an authoritative estimate, just from my rusty old memory .
You can see it along FPL's 500 KV line parallel to US27 between Clewiston and Miami. And that's a nice drive.

In the days of analog telephone over copper wire pairs on poles we rolled the pair according to the frequency of the telephone carriers. A 20 khz line carrying five conversations would be rolled at every pole, a straight voice line only every ten or twenty poles. old jim
 
  • #14
jim hardy said:
equal 5e6 meters = 5,000km
and he said 1,000km ?

Oops, I had 1000m in my head, not 1000km. You are correct.

So to the OP, you will get about 0.1Vrms at the end of your 1000km power cable. If you really want to go that far, you need to do what the power companies do, and use step-up and step-down transformers to minimize IR losses in your long power cable. So this is for deep drilling applications?
 
  • Like
Likes davenn
  • #15
I don't know of anything that drills 1000 km deep
at that depth you are well into the Earth's molten mantle

I suspect he really meant 1000m (1km) ( rereading he did say just an example)
a note to @btb4198 it is better to keep things realistic with your posed questions/problems :smile:deepest depths drilled are as listed from wiki ...

The Kola Superdeep Borehole (Russian: Кольская сверхглубокая скважина, Kolskaya sverkhglubokaya skvazhina) is the result of a scientific drilling project of the Soviet Union in the Pechengsky District, on the Kola Peninsula. The project attempted to drill as deep as possible into the Earth's crust. Drilling began on 24 May 1970 using the Uralmash-4E, and later the http://en.wikipedia.org/w/index.php?title=Uralmash-15000&action=edit&redlink=1 series drilling rig. A number of boreholes were drilled by branching from a central hole. The deepest, SG-3, reached 12,262 metres (40,230 ft) in 1989 and still is the deepest artificial point on Earth.[1]

In terms of true depth, it is the deepest borehole in the world. For two decades it was also the world's longest borehole, in terms of measured depth along the well bore, until surpassed in 2008 by the 12,289-metre-long (40,318 ft) Al Shaheen oil well in Qatar, and in 2011 by 12,345-metre-long (40,502 ft) Sakhalin-I Odoptu OP-11 Well (offshore the Russian island Sakhalin).[2]

so a bit over 12km a VERY long way from 1000 kmDave
 
Last edited by a moderator:
  • Like
Likes berkeman
  • #16
Thanks Dave! :smile:
 
  • #17
berkeman said:
Oops, I had 1000m in my head, not 1000km. You are correct.

So to the OP, you will get about 0.1Vrms at the end of your 1000km power cable. If you really want to go that far, you need to do what the power companies do, and use step-up and step-down transformers to minimize IR losses in your long power cable. So this is for deep drilling applications?

The Well Is only about 1000m (3200Ft) deep that was my bad. I have a FVD (Altivar 71) that powers a pumper: 120V and 4 HP.

so when I buy the wire I can get the R' (Ohms per 1000 feet) ?

Also Transmission line seem to only be use for high F and very very long distance...
but I should just use
V= IR
so I would have
P = iv
I = 2982.799488 W / 120 V = 24.8566624A
so using 00 AWG cable (0.079 Ohms per 1000 feet), 0.079 * (3.28084) * 2 = 0.51837272 ohms
V ( Voltage Drop) = 24.8566624( 0.51837272 ) = 12.88499579289728V

um... is that wrong ?
 
Last edited:
  • #18
btb4198 said:
um... is that wrong ?
it'd sure be easier for me to read if you rounded to three digits, slide rule accuracy.

It looks okay so far as voltage drop for the current you calculated.
Glad to see you doubled resistance to account for the round trip , it's common to forget that .

You'll want to get the actual current for the pump motor. You just divided 4hp's worth of watts by 120 volts and that's very optimistic..
The motor has a "power factor" so it'll draw probably 25% more current than you figured
and since most motors will will draw a lot more current when starting than when running
your wire must deliver enough voltage for the pump motor to start.

i tried to find the manual for Altivar 71 VFD but only could get to a DC braking unit.
so I don't know how the VFD behaves. I've never used one. Surely its manual tells how to size the cables.

When you don't have a wire table handy
here's a handy "Rule of Thumb":
#10 wire is 1 ohm per thousand feet and that's easy to remember
every three gages that doubles
so every gage changes by cube root of two
so #13(an unusual size) is two ohms/thousand
and #16 is 4 ohms/thousand
and #7 is a half ohm/thousand
#4 a quarter

here's a table, any search engine will turn one up for you
http://en.wikipedia.org/wiki/American_wire_gauge
http://hyperphysics.phy-astr.gsu.edu/hbase/tables/wirega.html

as you see the "Rule of Thumb" gives a reasonable approximation

hang in there - it becomes easier as your familiarity grows.

old jim
 
Last edited:
  • Like
Likes davenn
  • #19
is it called Voltage drop or Resistive Losses ?
 
  • #20
btb4198 said:
is it called Voltage drop or Resistive Losses ?

We have wire Resistive Loss as a constant and a Voltage Drop on that wire that's a function of the voltage/current ratio for the power delivered at the load. Higher source voltage for the same power at the load (resistance increase for lower wire currents) gives a smaller 'Voltage drop' as a percentage of the total source voltage delivered to the load.
If we were to increase voltage while maintaining the same wire current by increasing load resistance to keep the delivered power the same, we see the same effect of reduction in 'Voltage Drop' as a percentage of the total source voltage delivered to the load.
 
Last edited:
  • #21
btb4198 said:
is it called Voltage drop or Resistive Losses ?
As Sophie says, "Classification is the enemy of understanding."
what you calculated is the drop due to resistive loss.
In short runs that's usually all that's necessary. Rule of thumb is 3%.

Long runs have enough capacitance and inductance to warrant including them, so you'd use
Voltage drop = I X Z where Z = R + jXL -j XC ..

Several posters here are hinting at the benefits of transmitting at higher voltage.
Can you get that pump in 240 volts ?
 
  • Like
Likes nsaspook
  • #22
jim hardy said:
As Sophie says, "Classification is the enemy of understanding."
what you calculated is the drop due to resistive loss.
In short runs that's usually all that's necessary. Rule of thumb is 3%.

Long runs have enough capacitance and inductance to warrant including them, so you'd use
Voltage drop = I X Z where Z = R + jXL -j XC ..

Several posters here are hinting at the benefits of transmitting at higher voltage.
Can you get that pump in 240 volts ?

Yes, I have an Altivar 71 VFD that does 240V and 10HP. What do you mean by long runs? The Pumps run 24/7.
 
  • #23
btb4198 said:
Yes, I have an Altivar 71 VFD that does 240V and 10HP. What do you mean by long runs? The Pumps run 24/7.

That's jargon for a long wire.:DD How long is relative, to a power guy it's across states, to others it's down the street or a 1000m well.
 
Last edited:
  • Like
Likes jim hardy
  • #24
Thanks Mr Spook

indeed
btb:
when I'm wearing my home handyman hat a long run is a 50 foot extension cord
when I'm with my power system friends a long run is from Miami to the Georgia line.

i think for your run of less than a mile, resistance will be responsible for the vast majority of your voltage drop.

i got only 20 microhenries per thousand feet guessing at 1/2 inch separation of 0.36 inch wires.

Surely capacitive current will be small compared to 4hp of load.
Might upset GFCI's though.

old jim
 
  • #25
This will demonstrate how run length voltage drop is relative to wiring, current and supply voltage.
I've got two sets (remote RPV Voltage/RPV Current, main MPV Current/PV Voltage) of small solar panel arrays separated by 30 feet of 8 gauge wire feeding a battery pack that's currently running a small AC unit in the shop. The displayed information is from the Web page of my PIC32 controller.
If the line voltages were much higher then the displayed 'Voltage Drop 3.56VDC' won't matter much but it's a nominal 12vdc system so that drop is a high percentage of the supply voltage and a major problem in getting max power from those panels. Lucky for me I've a large run of scrapped 000 copper wire to double up that 8 but I've got to trench 30 feed of dirt to put it in, one day.

17408619366_b55fcc0571_c_d.jpg
 

FAQ: How Does Transmission Line Length Affect Voltage Loss?

1. What is transmission line voltage loss?

Transmission line voltage loss is the decrease in voltage that occurs as electricity is transmitted through a power line from a power plant to a consumer. This loss is caused by factors such as resistance in the wires, temperature changes, and electromagnetic effects.

2. Why does transmission line voltage loss occur?

Transmission line voltage loss occurs due to factors such as resistance in the wires, temperature changes, and electromagnetic effects. These factors cause energy to be dissipated as heat, resulting in a decrease in voltage along the power line.

3. How does transmission line length affect voltage loss?

The longer the transmission line, the greater the voltage loss. This is because the resistance in the wires and the effects of temperature and electromagnetism have a greater impact over longer distances. Therefore, longer transmission lines tend to have higher voltage losses than shorter ones.

4. What are some ways to reduce transmission line voltage loss?

One way to reduce transmission line voltage loss is by using thicker wires with lower resistance. Additionally, using materials with lower resistance, such as aluminum instead of copper, can also help reduce voltage loss. Another method is to use power transformers along the transmission line to boost the voltage periodically, compensating for the loss.

5. How does transmission line voltage loss affect the efficiency of a power system?

Transmission line voltage loss reduces the efficiency of a power system, as the energy that is lost in the form of heat cannot be used by the consumer. This means that more electricity must be generated to compensate for the losses, resulting in higher costs for both the power provider and the consumer. Reducing voltage loss can help improve the efficiency of a power system.