The discussion focuses on the earthing requirements outlined in AS2067, specifically regarding the connection of Earth cables from a high voltage (HV) substation to a remote transformer. It raises concerns about the necessity of this connection given the distance, questioning the potential risks of Earth Potential Rise (EPR) during faults. Participants note that earthing may only be required when the substation and transformer are co-located, and reference is made to IEC 61936 for guidance on avoiding transferred potential. The conversation highlights the challenges posed by paywalls in accessing the full standard details. Understanding these earthing requirements is crucial for ensuring safety in high voltage installations.
victorgoh1981
Messages
1
Reaction score
0
I have a question about the earthing requirement in AS2067. Figure B5 and B4 show that the Earth cables from the HV substation should connect to the Earth bar of the remote transformer. Since the HV substation is far away from the remote transformer, we do not need to equalize the potential. why do we need to connect the Earth between them? The Earth conductor could transfer the EPR (Earth Potential Rise) from the HV substation to the transformer location in the event of an Earth fault. That could create a dangerous situation for the people near to transformer. Could anyone help me to answer this question? Thanks
 
Engineering news on Phys.org
What country are you in? What is your interest in this question? Are you studying to take an advancde electrician certification exam?
 
He's talking about Australian Standard® Substations and high voltage installations exceeding 1 kV a.c. , https://www.saiglobal.com/PDFTemp/Previews/OSH/AS/AS2000/2000/2067-2008.pdf

But the majority of the document is behind a paywall.

1644590974034.png
 
Last edited:
victorgoh1981 said:
... Since the HV substation is far away from the remote transformer, ...
Maybe that is a false assumption.
The earthing may be required only when they are co-located.
With the paywall it is difficult to examine the exact text.
 
I have not a copy of this Australian Standard but as it noted in the Preface it is based on IEC 61936 which is included now in EN 50522/2010.

In this standard at item 6 Measure to avoid transferred potential you may know how to proceed to avoid potential transfer from high to low voltage system or to communication.
 
From the attached sketch you can see that if the shield of the medium voltage cable is grounded [earthed] only at one end at the ungrounded end the potential will be A, but if it grounded at both ends the potential will be B. We can do so that B could be less than maximum permissible.
 

Attachments

  • Potential transferred from Substation.jpg
    Potential transferred from Substation.jpg
    38.7 KB · Views: 150
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...

Similar threads

Replies
10
Views
3K
Replies
19
Views
3K
Replies
4
Views
2K
Replies
6
Views
3K
Back
Top