Understanding AS2067 Earthing Requirements: A Closer Look at Figure B5 and B4

  • Thread starter victorgoh1981
  • Start date
In summary: This is because the potential difference between the grounded medium and high voltage cables will be less than the potential difference between the grounded high voltage cable and the Earth.Summary:According to the Australian Standard, the Earth must be connected between the HV substation and the remote transformer in order to avoid potential transfer.
  • #1
victorgoh1981
1
0
I have a question about the earthing requirement in AS2067. Figure B5 and B4 show that the Earth cables from the HV substation should connect to the Earth bar of the remote transformer. Since the HV substation is far away from the remote transformer, we do not need to equalize the potential. why do we need to connect the Earth between them? The Earth conductor could transfer the EPR (Earth Potential Rise) from the HV substation to the transformer location in the event of an Earth fault. That could create a dangerous situation for the people near to transformer. Could anyone help me to answer this question? Thanks
 
Engineering news on Phys.org
  • #2
What country are you in? What is your interest in this question? Are you studying to take an advancde electrician certification exam?
 
  • #3
He's talking about Australian Standard® Substations and high voltage installations exceeding 1 kV a.c. , https://www.saiglobal.com/PDFTemp/Previews/OSH/AS/AS2000/2000/2067-2008.pdf

But the majority of the document is behind a paywall.

1644590974034.png
 
Last edited:
  • Informative
Likes berkeman
  • #4
victorgoh1981 said:
... Since the HV substation is far away from the remote transformer, ...
Maybe that is a false assumption.
The earthing may be required only when they are co-located.
With the paywall it is difficult to examine the exact text.
 
  • #5
I have not a copy of this Australian Standard but as it noted in the Preface it is based on IEC 61936 which is included now in EN 50522/2010.

In this standard at item 6 Measure to avoid transferred potential you may know how to proceed to avoid potential transfer from high to low voltage system or to communication.
 
  • Informative
Likes Tom.G
  • #6
From the attached sketch you can see that if the shield of the medium voltage cable is grounded [earthed] only at one end at the ungrounded end the potential will be A, but if it grounded at both ends the potential will be B. We can do so that B could be less than maximum permissible.
 

Attachments

  • Potential transferred from Substation.jpg
    Potential transferred from Substation.jpg
    38.7 KB · Views: 115

FAQ: Understanding AS2067 Earthing Requirements: A Closer Look at Figure B5 and B4

What is AS2067 and why is it important?

AS2067 is a standard set by the Australian government that outlines the requirements for earthing systems in electrical installations. It is important because it ensures the safety and proper functioning of electrical systems, protecting both people and equipment from potential hazards.

What is Figure B5 and B4 in AS2067?

Figure B5 and B4 are diagrams included in AS2067 that illustrate the recommended earthing arrangements for different types of installations. These figures provide guidance on how to properly design and install earthing systems to meet the requirements of the standard.

What are the main differences between Figure B5 and B4?

The main difference between Figure B5 and B4 is the type of installation they are intended for. Figure B5 is specifically for installations with a single source of supply, while Figure B4 is for installations with multiple sources of supply. Additionally, Figure B5 includes more detailed illustrations for specific types of installations, such as overhead lines and underground cables.

How can I ensure compliance with AS2067 for earthing requirements?

To ensure compliance with AS2067, it is important to carefully follow the guidelines outlined in the standard. This includes understanding the requirements for different types of installations, properly designing and installing earthing systems, and regularly testing and maintaining the systems to ensure they continue to meet the standard.

Are there any exceptions to the earthing requirements outlined in AS2067?

Yes, there are some exceptions to the earthing requirements in AS2067. These exceptions are outlined in the standard and may apply to specific types of installations or circumstances. It is important to carefully review the standard and consult with a qualified professional to determine if any exceptions apply to your specific situation.

Similar threads

Replies
10
Views
3K
Replies
19
Views
2K
Replies
1
Views
2K
Replies
11
Views
4K
Replies
21
Views
2K
Replies
3
Views
985
Replies
6
Views
2K
Back
Top