Utilities penalize customers for low power factor because it indicates inefficient energy use, leading to increased current draw without corresponding real power output. This excess current causes higher energy losses in the distribution system, necessitating larger infrastructure and increasing operational costs for the utility. Reactive power does not perform useful work, yet it still contributes to the overall load, resulting in penalties for industrial and commercial users. The additional current leads to joule heating losses and voltage drops, which are not compensated for by the utility. Overall, maintaining a higher power factor is essential for reducing costs and improving system efficiency.
XPTPCREWX
Messages
101
Reaction score
0
Why is it that the utility will penalize a customer for a low power factor.

I can't imagine why they would penalize you if a purely reactive load puts all its power back into the mains.
 
Engineering news on Phys.org
Because it doesn't put all its power back into the grid. Reactive power has no capacity to do work because the voltage and current are out of phase with each other. So essentially, when you take reactive power, you are taking generator capacity (apparent power) that isn't showing up on your meter (real power).
In an electric power system, a load with low power factor draws more current than a load with a high power factor for the same amount of useful power transferred. The higher currents increase the energy lost in the distribution system, and require larger wires and other equipment. Because of the costs of larger equipment and wasted energy, electrical utilities will usually charge a higher cost to industrial or commercial customers where there is a low power factor.
http://en.wikipedia.org/wiki/Power_factor
 
A purely reactive load still draws current and gives rise to undesirable joule heating losses and voltage drops in the power distribution network conductors and components (such as transformer windings). That loss is not recoverable. Allowing very low power factor conditions to prevail could require the system to have much bigger conductor sizes to reduce the losses and voltage drop - thereby increasing the capital cost.
 
XPTPCREWX said:
Why is it that the utility will penalize a customer for a low power factor. I can't imagine why they would penalize you if a purely reactive load puts all its power back into the mains.
You are correct. A low power factor puts more current in the lines. The utility charges you only for real power, not the reactive part. The extra current in their lines just loads them down with extra I2R losses, which you do not pay for. On the other hand, they may pay YOU for some capacitive power factor. You could put a synchronous capacitor on line (a salient pole synchronous motor w/o load).
 
Because power is wasted in the wires carrying current to the load. Do a search on this. It has been covered here on PF numerous times.

Edit: WOW. Three posts within minutes of each other.
 
had a feeling that, that was the reason, but wasn't sure...thanx
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...