The discussion focuses on understanding reactive power measurements from a smart meter connected to a resistor load bank. The user observed a negative reactive power value, indicating a capacitive load, which raised questions about the accuracy and setup of their measurement system. Clarifications were sought regarding whether the system was single or three-phase, as well as the specifications of the smart meter being used, an ABB A44. The measurements indicated discrepancies in expected current values and the nature of reactive power as the load changed. Ultimately, the conversation highlights the complexities of measuring reactive power accurately in different configurations.
Sebastian Neo
Messages
5
Reaction score
0
Hi,

I was doing some test with the load bank today and I obtain a value which I don't quite understand.
I supply a 400V Line to Line, 50Hz to a smart meter and to the resistor load bank. The measured value by the smart meter was 500W and -40Var with a current of 0.71A. As the current increases, the real power increases and the reactive power decreases further.

I know that there is no such thing as ideal load but to have a negative reactive power does not make any sense.

Please kindly advice. Thank you
 
Engineering news on Phys.org
:welcome:

Negative VARs just means a capacitive load.

What doesn't make sense is so many VARs of either sign with just a smart meter and a resistor bank. There must be more to the story, something else in the setup that you didn't mention.
 
the setup was quite simple. I am taking supply from the main power grid into my microgrid and to my smart meter which is connected to the resistor bank.
That's all for my setup
 
A couple of thoughts:

1. Can i assume single phase ?

500 watts and 40 vars is only 501.6 VA
what is the advertised accuracy of your smart meter ? Do your discrepancies fall outside its guaranteed performance?

2. With single phase 501.6VA at 400 volts is 1.254 amps not 0.71,
however
1.254 divided by √3 = 0.723, within 2% of what you report measuring.
So was my assumption of single phase perhaps wrong?

3. There's an ambiguity in your description.
Sebastian Neo said:
As the current increases, the real power increases and the reactive power decreases further.
By 'decreases' do you mean becomes a larger negative number as in moving toward -50, -60, -70 vars?

4. If this is three phase recall that when PF = 1 the line current and line-line voltage are displaced by 30 degrees, which at first glance looks like a PF of about 0.87. That's why there's a two wattmeter method for measuring three phase power.
If you are trying to measure three phase power with a single phase "smart meter", it sounds to me like everything is behaving pretty much as it should.

5. So, what's your "smart meter" ? Got a link to its instruction manual ? And a sketch of your hookup?
 
jim hardy said:
A couple of thoughts:

1. Can i assume single phase ?

500 watts and 40 vars is only 501.6 VA
what is the advertised accuracy of your smart meter ? Do your discrepancies fall outside its guaranteed performance?

2. With single phase 501.6VA at 400 volts is 1.254 amps not 0.71,
however
1.254 divided by √3 = 0.723, within 2% of what you report measuring.
So was my assumption of single phase perhaps wrong?

3. There's an ambiguity in your description.

By 'decreases' do you mean becomes a larger negative number as in moving toward -50, -60, -70 vars?

4. If this is three phase recall that when PF = 1 the line current and line-line voltage are displaced by 30 degrees, which at first glance looks like a PF of about 0.87. That's why there's a two wattmeter method for measuring three phase power.
If you are trying to measure three phase power with a single phase "smart meter", it sounds to me like everything is behaving pretty much as it should.

5. So, what's your "smart meter" ? Got a link to its instruction manual ? And a sketch of your hookup?
By 'decreases' do you mean becomes a larger negative number as in moving toward -50, -60, -70 vars?
Yes, that's what i meant.

I am using ABB A44 meter.

544W is total power for all 3 phase. single phase voltage is 230V. Current for Phase A is 0.71A. Power for 1 phase is 178W.

Total reactive power is -38.94. Phase A reactive power is -15.55 Var, Phase B is -4.92 Var and Phase C is -18.46 VAr
 
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...