What percentage of heat is generated from LED lighting?

AI Thread Summary
LED lighting, with a total wattage of 80, is significantly more efficient than incandescent lighting, converting about 30% of energy into light and 70% into heat. Most of the heat generated will rise to the ceiling or roof space, and ultimately, all the energy will convert to heat in the room. The exact percentage of heat gain can depend on the configuration of the fixtures, particularly if they are above ceiling level, as some heat may not return to the room. While specific studies or publications on heat gain percentages from LED lighting are scarce, a safe assumption is that nearly all of the wattage will contribute to heat. Understanding these dynamics is crucial for effective HVAC system design and room temperature management.
Howlin
Messages
51
Reaction score
0
Hi all,

If in a room, a lighting design was carried out and the room will contain 4 no, LED luminaries with a total wattage of 80.

My query relates to what would a reasonable figure or percentage be to use as heat gain from the light. Of the 80 watts, how much of it would go into heat?

I am unable to find it in either a CIBSE guide or an Ashrea guide.

Your help would be gratefully welcomed.
 
Engineering news on Phys.org
An incandescent filament is less than 5% efficient at producing light.
An LED is about 10 times better than an incandescent filament.
An LED is therefore less than 50% efficiency.

Most of the 80 watt supplied will appear as heat. Heat rises.
Most of that heat will appear in the ceiling, roof space or in the floor of the room above.

The light radiated by the LED will also become heat if it is absorbed in the illuminated room.
 
Hi Baluncore,

Thank you for the reply.

Do you know of any studies or publications that indicate an appropriate percentage heat gain percentage from LED lighting?

I have found some but they don't mention what percentage of the say 80 watts would be lighting and what % would be heat gain.
 
In the end, it will all become heat.
Assume 30% immediately becomes light, and 70% heat in the luminaire.
Unless the light radiates through a window, it too will quickly become heat, making all 80 watt heat.
The answer will probably depend on why you ask the question.
 
  • Like
Likes russ_watters
Howlin said:
Of the 80 watts, how much of it would go into heat?
All of it. The type of light isn't relevant.
 
Baluncore said:
In the end, it will all become heat...

The answer will probably depend on why you ask the question.
There's one common scenario where how much of the heat gets into the room or HVAC system can depend on configuration: above ceiling fixtures(protruding). If the heat from the driver goes into the ceiling space instead of the room, it may not all find it's way back into the room or HVAC system.

That should be discussed in the ASHRAE handbook somewhere an/or be a check box in load calc software, but I don't have a specific reference off the top of my head. "All of it" is the safe assumption.

[edit] oops, you pretty much covered that in the other post.
 
Last edited:
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
While I was rolling out a shielded cable, a though came to my mind - what happens to the current flow in the cable if there came a short between the wire and the shield in both ends of the cable? For simplicity, lets assume a 1-wire copper wire wrapped in an aluminum shield. The wire and the shield has the same cross section area. There are insulating material between them, and in both ends there is a short between them. My first thought, the total resistance of the cable would be reduced...
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...