Why Anchoring Battery Racks to Floor & Wall is Not Recommended

  • Thread starter Thread starter MitYeltu
  • Start date Start date
  • Tags Tags
    Battery Wall
AI Thread Summary
Anchoring battery racks to both the floor and wall is discouraged due to the potential for relative movement during earthquakes, which can lead to structural failure of the rack. The National Electrical Safety Code (NESC) suggests this practice to prevent damage during seismic events. If the wall and floor shift independently, a dual anchoring could result in tearing apart the rack. Conversely, a robust rack could impede wall movement, potentially damaging the building itself. Understanding these dynamics is crucial for ensuring safety in earthquake-prone areas.
MitYeltu
Messages
8
Reaction score
0
I am working on putting a new battery rack into a substation. I was re-reading the NESC and came across section 143. This section suggests it is not recommended to anchor my rack to both the floor and the wall. Can anyone explain why this is not recommended?
 
Engineering news on Phys.org
If you are in an earthquake zone, the wall and floor could move relative to each other in minor quakes.
This could tear your rack apart if it was connected to both of them.
 
vk6kro said:
If you are in an earthquake zone, the wall and floor could move relative to each other in minor quakes.
This could tear your rack apart if it was connected to both of them.

Brilliant. I learn something new every dang day here on the PF.
 
That makes sense. I hadn't thought about that, but I agree now that I have. Now, don't be angry for my asking it this way, but, is that the NESC reason for not attaching it to both? I have not seen that specified anywhere.
 
It could work the other way, too.

If the rack was very strong, it could stop part of the wall moving and cause damage to the building.
 
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Hey guys. I have a question related to electricity and alternating current. Say an alien fictional society developed electricity, and settled on a standard like 73V AC current at 46 Hz. How would appliances be designed, and what impact would the lower frequency and voltage have on transformers, wiring, TVs, computers, LEDs, motors, and heating, assuming the laws of physics and technology are the same as on Earth?
Thread 'Electromagnet magnetic field issue'
Hi Guys We are a bunch a mechanical engineers trying to build a simple electromagnet. Our design is based on a very similar magnet. However, our version is about 10 times less magnetic and we are wondering why. Our coil has exactly same length, same number of layers and turns. What is possibly wrong? PIN and bracket are made of iron and are in electrical contact, exactly like the reference design. Any help will be appreciated. Thanks. edit: even same wire diameter and coil was wounded by a...