Why do 3 phase balanced faults cause such high fault currents?

AI Thread Summary
Three-phase balanced faults can cause high fault currents primarily due to the higher capacity of three-phase supplies and the limited reactance of the source. The fault current magnitude is influenced by the proximity of the fault to the source and the resistance and reactance of conductors involved. Resources like books by Paul M. Anderson and J. Lewis Blackburn are recommended for deeper understanding of power system faults. The configuration of the circuit, such as Delta versus Wye, also affects ground-fault behavior. Understanding these factors is crucial for analyzing fault currents effectively.
Ian_Brooks
Messages
127
Reaction score
0
Not a homework question, Just trying to get more information about it. Its hard to find a textbook or a site that explains this well.

thanks
 
Engineering news on Phys.org
I don't think that they do as a result of being 3 phase except that a short from phase to phase will draw a higher current than phase to neutral. It may be just a case that 3 phase supplies tend to be higher capacity supplies.
 
It should be remembered that three phase fault current is limited only by the the reactance of the source and perhaps additionally the R and X of any conductors between the source and the fault point. The closer the fault to the source, the higher one should expect the fault current magnitudes to be.
If your interest in power system faults is strong, try searching for books by Paul M. Anderson, J. Lewis Blackburn, and Walt Elmore. (there are others as well, these just came quickly to mind.)
 
thanks a lot guys.

I'll be sure to check those books out.

Its funny how I feel like I haven't learned anything from my college classes.

How's glover and sarma by the way?
 
subtech said:
It should be remembered that three phase fault current is limited only by the the reactance of the source and perhaps additionally the R and X of any conductors between the source and the fault point. The closer the fault to the source, the higher one should expect the fault current magnitudes to be.
If your interest in power system faults is strong, try searching for books by Paul M. Anderson, J. Lewis Blackburn, and Walt Elmore.
(there are others as well, these just came quickly to mind.)

Protective Relaying: Principles and Applications, Third Edition (Power Engineering) (Hardcover)
by J. Lewis Blackburn (Editor), Thomas J. Domin (Editor)
https://www.amazon.com/gp/product/1574447165/?tag=pfamazon01-20

Is this the Lewis Blackburn book you were referring to? I'll check to see if my college library has it.
 
Fault currents are highly dependent on the configuration of the circuit's ground reference. Have you studied the differences between Delta and Wye configurations to see how ground-faults can differ?
 
I used to be an HVAC technician. One time I had a service call in which there was no power to the thermostat. The thermostat did not have power because the fuse in the air handler was blown. The fuse in the air handler was blown because there was a low voltage short. The rubber coating on one of the thermostat wires was chewed off by a rodent. The exposed metal in the thermostat wire was touching the metal cabinet of the air handler. This was a low voltage short. This low voltage...
Thread 'How Does Jaguar's 1980s V12 Dual Coil Ignition System Enhance Spark Strength?'
I have come across a dual coil ignition system as used by Jaguar on their V12 in the 1980's. It uses two ignition coils with their primary windings wired in parallel. The primary coil has its secondary winding wired to the distributor and then to the spark plugs as is standard practice. However, the auxiliary coil has it secondary winding output sealed off. The purpose of the system was to provide a stronger spark to the plugs, always a difficult task with the very short dwell time of a...