Decreasing evaporator airflow in an air conditioner leads to lower low pressure side saturation temperatures and higher temperature differentials (delta T). With reduced airflow, the air moving over the evaporator cools more effectively, resulting in a higher delta T. The lower mass airflow means fewer air molecules interact with the coil, causing a decrease in air velocity and a lower bypass factor. This results in a cooler coil temperature as less heat is absorbed from the air, which in turn lowers the suction pressure. Consequently, the overall efficiency of the air conditioning system is affected, demonstrating the intricate relationship between airflow and performance.
sevensages
TL;DR Summary
Why does lower evaporator airflow cause lower low pressure side Saturation temperature on an air-conditioner?
The other day I read on a website that a lower evaporator airflow causes lower low pressure side saturation temperatures and higher delta T on an air-conditioner. Now I think I know why a lower evaporator airflow would cause a high delta T. If there is less air moving over the evaporator, the evaporator would be able to cool the (small) amount of air that goes through the evaporator more quickly and effectively. But I cannot figure out why a lower evaporator airflow would cause the low pressure side saturation temperature to be lower.
Why does low evaporator airflow cause the low pressure side saturation temperature to be lower on an air-conditioner?
Copied from:
https://hvacrschool.com/impacts-of-decreasing-evaporator-air-flow/
“What Happens When Airflow is Decreased?
In this theoretical system, when the airflow is decreased and all else stays the same, the following things will occur:
  • Mass airflow will decrease, meaning fewer molecules are moving across the coil.
  • Air velocity will decrease, meaning the air is moving over the fins and tubing more slowly.
  • The bypass factor decreases; more air molecules will be touching the metal as a ratio.
  • Air temperature decreases (to a point) due to the air moving more slowly across the coil with less bypass factor.
  • Coil temperature decreases because less overall heat is being picked from the air.
  • Coil drops further below the dewpoint, causing more moisture to be removed from the air, increasing dehumidification.
  • Suction pressure decreases because less heat energy being picked up means less pressure, and as the superheat falls, the TXV also further throttles the flow of refrigerant through the coil.
  • The compression ratio increases as the suction pressure drops, meaning the compressor moves less refrigerant as the refrigerant density entering the compressor falls.
  • Coil TD increases as indicated by the colder coil in relation to the return air.”
Here's a video by “driving 4 answers” who seems to me to be well versed on the details of Internal Combustion engines. The video does cover something that's a bit shrouded in 'conspiracy theory', and he touches on that, but of course for phys.org, I'm only interested in the actual science involved. He analyzes the claim of achieving 100 mpg with a 427 cubic inch V8 1970 Ford Galaxy in 1977. Only the fuel supply system was modified. I was surprised that he feels the claim could have been...
Thread 'Turbocharging carbureted petrol 2 stroke engines'
Hi everyone, online I ve seen some images about 2 stroke carbureted turbo (motorcycle derivation engine). Now.. In the past in this forum some members spoke about turbocharging 2 stroke but not in sufficient detail. The intake and the exhaust are open at the same time and there are no valves like a 4 stroke. But if you search online you can find carbureted 2stroke turbo sled or the Am6 turbo. The question is: Is really possible turbocharge a 2 stroke carburated(NOT EFI)petrol engine and...