Why the efficiency of air core transformer changes (up and down)

In summary, the efficiency of air core transformers can change both upwards and downwards due to a variety of factors. These include changes in the core material, variations in voltage and current, and fluctuations in temperature. Additionally, the design and construction of the transformer can also impact its efficiency. Understanding these factors and their effects on efficiency is crucial for optimizing the performance of air core transformers.
  • #36
jim hardy said:
pythagoras' theorem X = √Z2 - R2)
Did you mean Z2 - R2) ?
 
Engineering news on Phys.org
  • #37
Tom.G said:
Did you mean Z2 - R2) ?
Yes musta hit subscript instead of super?

found a few others...

Thanks Tom ! i appreciate the help .

old jim
 
Last edited:
  • #38
UtsavRaj, be careful not damage your primary coil. You mentioned in an earlier post that the coil was getting hot.

There is a warning in: http://int.frederiksen.eu/Admin/Pub...iles/exp/137000/137710-EN-The-transformer.pdf

It says:
"When the core is not in place in the primary coil, the
current can get so high that the coil overheats and the
plastic coil former is damaged. The coils used have
these maximum currents:
462510 200 windings Max. 2 A
462520 400 windings Max. 1 A
462525 800 windings Max. 0.5 A"

Be sure to make your measurements at those high currents quickly and then turn the voltage down.
 
  • Like
Likes jim hardy
  • #39
The Electrician said:
There is a warning

Good Catch !
 
  • #40
jim hardy said:
the impedance is √(resistance2 + reactance2)

I think the OP will have difficulty making this measurement on his "air" core setup. The reactance of his primary coil will be so small compared with the resistance, that (with the equipment he has) he won't be able to see the difference between Z and R.

I have an old Radio Shack filament transformer that I keep around because the laminations weren't varnished so they can be removed. This makes it handy for measurements of various parameters with and without an iron core:

Transf1.jpg
'

You can see the green rubber bands holding everything together.

With the core in place, the primary impedance measured at the primary @ 60 Hz with .5 volt excitation is shown in 3 different formats herewith:
Transf2.jpg


Here the reactance is the first (top) value, and resistance is the second value.
Transf3.jpg


Here's the impedance and phase angle.
Transf4.jpg


In the second analyzer image, we see that the reactance and resistance are the same order of magnitude.
 
  • #41
Now here's the same transformer with the core removed:

Transf5.jpg


And here are the same 3 images showing the primary impedance @60 Hz with an "air" core:

Transf6.jpg


Transf7.jpg

Notice the phase angle is nowhere near 90 degrees. The primary impedance is nearly a pure resistance.
Transf8.jpg


In the second analyzer image, we see that the reactance is much smaller than the resistance. Also, note that the resistance without the core is quite different than it was with the core. That's because the core loss becomes part of the measured AC resistance.

My transformer has primary and secondary wound on the same bobbin, but the principle will apply to the OP's setup. I don't think the OP will be able to see the difference between Z and R when the core is absent.

The coefficient of coupling in the OP's setup is abysmal as is the efficiency. He's going to get a good lesson in the importance of an iron core in transformers!
 
Last edited:
  • #42
The Electrician said:
He's going to get a good lesson in the importance of an iron core in transformers!
By hands- on ! That's wonderful.

@UtsRavj - where is your school? I'm delighted to hear somebody still teaches hands-on electronics .
 
  • #43
The Electrician said:
UtsavRaj, be careful not damage your primary coil. You mentioned in an earlier post that the coil was getting hot.

There is a warning in: http://int.frederiksen.eu/Admin/Public/DWSDownload.aspx?File=/Files/Files/exp/137000/137710-EN-The-transformer.pdf

It says:
"When the core is not in place in the primary coil, the
current can get so high that the coil overheats and the
plastic coil former is damaged. The coils used have
these maximum currents:
462510 200 windings Max. 2 A
462520 400 windings Max. 1 A
462525 800 windings Max. 0.5 A"

Be sure to make your measurements at those high currents quickly and then turn the voltage down.

That's the first concern me and my teacher had when it got really hot - the insulation and wire could melt that's why i did the experiment really quickly and with one minute break (so the temp doesn't affect my experiment.) Thank you for your advice.

The Electrician said:
My transformer has primary and secondary wound on the same bobbin, but the principle will apply to the OP's setup. I don't think the OP will be able to see the difference between Z and R when the core is absent.
So are you saying that Impendance would be equal to resistance (mathematically speaking)

jim hardy said:
@UtsRavj - where is your school? I'm delighted to hear somebody still teaches hands-on electronics .
It is in Singapore. I chose this topic as part of my essay.

UPDATE ABOUT THE GRAPHS
I will most likely post all the updated information tomorrow afternoon. (SGT)

Thank you for your time everyone.

 
  • #44
UtsavRaj said:
So are you saying that Impendance would be equal to resistance (mathematically speaking)

Yes, for the case where there is no iron core.

The current in the primary of a transformer has two main components. One part of the current is due to the secondary current being "reflected" to the primary. This is the current that supplies power to the load on the secondary; it's the "useful" part of the primary current. The other part of the primary current is the "magnetizing" current. It is only there because the inductance of the primary requires it; laws of physics and all that. But since the magnetizing current must pass through the resistance of the copper wire of the primary, it causes losses (heating mostly) in the wire. These losses reduce the efficiency of the transformer. If the magnetizing current could be reduced, the losses would be reduced and the efficiency increased.

Since the magnetizing current is only there to energize the primary inductance, it would be reduced if the inductance of the primary were increased. That's what the iron core does.

Looking at the images of the measured impedance of my transformer, you can see that when the iron core is present the inductance of the primary is about 1.59 henries. When the core was removed, the inductance was only .012 henries, more than 100 times less. This means that the magnetizing current would be 100 times less when the core is in place.

The main purpose of an iron core is to reduce magnetizing current. It also increases the coupling between primary and secondary, especially in an arrangement like your transformer where the primary and secondary are not wound on the same bobbin.
 
  • #45
Primary counter-emf could hardly be less than emf induced in an open circuit secondary since it's the same flux
well, same flux on a bifilar winding anyway where primary and secondary wires are so very close that hardly any flux fails to link both .
He has a lot more leakage though

His data shows maybe 30 to 1 ratio primary to secondary voltage
so i expect detectable inductive reactance even if just a few % with air core

old jim
 
  • #46
Consider the OP's table of primary and secondary voltages. The OP is keeping way too many digits for a lot of his values. I make Baluncore's suggested changes to the first 3 secondary voltages. Then calculate the ratio of primary to secondary voltages for all 12 pairs. It appears that the 6th and last are different enough from 30 that they could reasonably be considered outliers, so I delete them. I'm left with 10 pairs and calculating the ratio of primary to secondary voltage I get these 10 values:

{33.3, 30.8, 28.9, 29.9, 31.3, 27.7, 27.6, 27.7, 27.3, 27.9}

Now subtract 30 from each value, divide by 30 and multiply by 100 to get a percent deviation from 30. I get a list like this:

{11.0%, 2.67%, -3.67%, -.33%, 4.33%, -7.67%, -8.0%, -7.67%, -9.0%, -7.0%}

That's quite a bit of variance. The OP might just barely be able to claim an accuracy of around 10%.

Let's say we applied 1 amp to the primary and expected about 1 volt across it due to IR drop in the primary and 1/30 volt due to inductive reactance.

If the resistive voltage and reactive voltage added arithmetically, we would expect a drop due to 1 amp of 1 + 1/30 or 1.033 volts, compared to just 1 volt due to the resistive drop. Given the variance in the OP's measurements, stray voltages due to placement of his voltmeter leads around the magnetic fields present, and other error sources, I wouldn't bet on his ability to see the difference.

But resistive and reactive voltages don't add like that. They add like SQRT(1^2 + .0333^2) which would give 1.00055 volts. I'm fairly certain the OP can't distinguish that from 1.00000 volts with the equipment and setup he has.
 
  • #47
Ahh the beauty of graph paper !
Plot deviation vs current - is it random, IR drop, or heating ?

As you said earlier - when he gets iron i there he'll be amazed

if we can give him a feel for inductance at this early stage in his education, what a boost it'll be .
 
Last edited:
  • #48
Once he gets the iron in, measuring the inductance should be possible even with his less than ideal setup.

UtsavRaj, would you please measure the resistance of your coils with a DVM; also the resistance of your bulb load, and post the results here.

Do you know what the rated voltage of the bulb is?
 
  • #49
First of all, i am very sorry that i did not reply for this long. It was a medical emergency with one of my close relatives which have subdued for now.

The Electrician said:
UtsavRaj, would you please measure the resistance of your coils with a DVM; also the resistance of your bulb load, and post the results here.
Do you know what the rated voltage of the bulb is?
jim hardy said:
Make the same plot, secondary volts(unloaded, no bulb) versus primary current with iron core.
I doubt you'll be able to push even an amp through primary.

The result would only come after 11th August because by then my school will open.
jim hardy said:
Plot deviation vs current - is it random, IR drop, or heating ?
I do not get this.

UPDATE ON GRAPH
I will definitely tomorrow.

IRON CORE
The Electrician said:
Once he gets the iron in, measuring the inductance should be possible even with his less than ideal setup.
I have already done that.

The methods is
UtsavRaj said:
The method went like this:
  • Powerpack attached to rheostat
  • rheostat attached to digital ammeter
  • Digital ammeter attached to Transformer coil (primary winding)
  • Transformer coil attached back to powerpack.
  • The digital voltmeter attached in parallel to the primary coil.
  • The secondary winding was attached to another Digital ammeter.
  • The digital ammeter attached to a bulb.
  • Bulb attached back to the secondary winding.
  • Another digital voltmeter attached in parallel to secondary winding.
  • All wires were copper wires.
  • All the voltage and current readings were taken from the respective devices and recorded.

The picture of the transformer:
jim hardy said:
eleventhggrader4-jpg.103117.jpg

More Details
Screen Shot 2016-07-18 at 9.42.04 PM.png


Screen Shot 2016-07-18 at 9.42.16 PM.png
Screen Shot 2016-07-18 at 9.42.32 PM.png
Screen Shot 2016-07-18 at 9.48.09 PM.png

Explanation for trend:

Sudden increase:
  • The induced magnetic field becomes stronger due to permeability of iron core which provides magnetic flux densities 10000 times that of air.high permeability means that the most of magnetic field is concentrated in the iron core and therefore allows a better inductance.n iron core is often used to provide a low-reluctance path for the magnetic flux
  • The resistance of a given piece of wire depends on three factors: the length of the wire, the cross-sectional area of the wire, and the resistivity of the material composing the wire. All of the factors remain the same. Therefore, coil have a steady resistance.
  • Copper losses are low as resistance is the same and the current is low.
  • The iron core Magnetic Stray losses at minimum although it increases with negligible with higher voltage.
  • At this point, the hysteresis and eddy currents are minimal (also because of insulated Iron core).
  • As weak magnetic field produces weak eddy currents and hysteresis.
  • Magnetostriction is low as well
  • Electric hum low due to less magnetic stray.

At higher voltage the increase becomes less.
  • More consistent value:
  • Magnetostriction increases due to a strong magnetic field.
  • Copper losses increases because of increase in current (A big source of energy loss).
  • Eddy Current becomes a bigger problem because of increase in magnetic field that causes bigger current being made in the iron core.
  • Hysterosis also increases. (Don’t exactly know)
  • Magnetic stray loss is still negligible but increases.
  • The induced magnetic field becomes stronger.
  • Electric hum a little bit due to more magnetic stray (which causes friction and therefore energy loss).
Is this explanation of trend right or am i wrong or less somewhere?Some questions i have:
  • Does Hysteresis increases with increase in voltage and current?
  • How does magnetising current affect iron core in efficiency?
  • "To maximize flux linkage with the secondary circuit, an iron core is often used to provide a low-reluctance path for the magnetic flux. The polarity of the windings describes the direction in which the coils were wound onto the core. Polarity determines whether the flux produced by one winding is additive or subtractive with respect to the flux produced by another winding" Can this explain anything about the Iron as well as Air core efficiency?
  • "In lower frequencies (mains) the efficiency is a lot worse, because an air core will have an enormous magnetizing current that will cause losses by heat on the wires." Why high magnetizing current for air core?

As always, thank you for your time.

 
  • #50
Screen Shot 2016-07-18 at 6.03.29 PM.png


UtsavRaj said:
Explanation for trend:

Sudden increase:
  • The induced magnetic field becomes stronger due to permeability of iron core which provides magnetic flux densities 10000 times that of air.high permeability means that the most of magnetic field is concentrated in the iron core and therefore allows a better inductance.n iron core is often used to provide a low-reluctance path for the magnetic flux
  • The resistance of a given piece of wire depends on three factors: the length of the wire, the cross-sectional area of the wire, and the resistivity of the material composing the wire. All of the factors remain the same. Therefore, coil have a steady resistance.
  • Copper losses are low as resistance is the same and the current is low.
  • The iron core Magnetic Stray losses at minimum although it increases with negligible with higher voltage.
  • At this point, the hysteresis and eddy currents are minimal (also because of insulated Iron core).
  • As weak magnetic field produces weak eddy currents and hysteresis.
  • Magnetostriction is low as well
  • Electric hum low due to less magnetic stray.

At higher voltage the increase becomes less.
  • More consistent value:
  • Magnetostriction increases due to a strong magnetic field.
  • Copper losses increases because of increase in current (A big source of energy loss).
  • Eddy Current becomes a bigger problem because of increase in magnetic field that causes bigger current being made in the iron core.
  • Hysterosis also increases. (Don’t exactly know)
  • Magnetic stray loss is still negligible but increases.
  • The induced magnetic field becomes stronger.
  • Electric hum a little bit due to more magnetic stray (which causes friction and therefore energy loss).
Is this explanation of trend right or am i wrong or less somewhere?

This is for the graph above.
 
  • #51
In your chart check the primary voltage of 6.59 volts. The corresponding primary current appears to be about 10 times too large. Same thing for primary voltage of 11.11 volts. These two points on the graph appear to be outliers.

If you fix those two values your graph will look much better; although the very first two voltage values look questionable too.
 
  • #52
The Electrician said:
In your chart check the primary voltage of 6.59 volts. The corresponding primary current appears to be about 10 times too large. Same thing for primary voltage of 11.11 volts. These two points on the graph appear to be outliers.

If you fix those two values your graph will look much better; although the very first two voltage values look questionable too.
Why does it have to be a straight line again?
 
  • #53
All currents and voltages should be proportional to each other if we can neglect nonlinear effects (e. g. heating-induced things).
 
  • #54
UtsavRaj said:
Why does it have to be a straight line again?
Primary current is the MMF that pushes flux.
Secondary voltage is a measure of the resulting flux.

What is the formula that relates flux to current ? Which terms in that formula might be nonlinear ?
 
  • #55
UtsavRaj said:
screen-shot-2016-07-18-at-6-03-29-pm-png.103412.png

UtsavRaj said:
Explanation for trend:

Sudden increase:
  • The induced magnetic field becomes stronger due to permeability of iron core which provides magnetic flux densities 10000 times that of air.high permeability means that the most of magnetic field is concentrated in the iron core and therefore allows a better inductance.n iron core is often used to provide a low-reluctance path for the magnetic flux
  • The resistance of a given piece of wire depends on three factors: the length of the wire, the cross-sectional area of the wire, and the resistivity of the material composing the wire. All of the factors remain the same. Therefore, coil have a steady resistance.
  • Copper losses are low as resistance is the same and the current is low.
  • The iron core Magnetic Stray losses at minimum although it increases with negligible with higher voltage.
  • At this point, the hysteresis and eddy currents are minimal (also because of insulated Iron core).
  • As weak magnetic field produces weak eddy currents and hysteresis.
  • Magnetostriction is low as well
  • Electric hum low due to less magnetic stray.

At higher voltage the increase becomes less.
  • More consistent value:
  • Magnetostriction increases due to a strong magnetic field.
  • Copper losses increases because of increase in current (A big source of energy loss).
  • Eddy Current becomes a bigger problem because of increase in magnetic field that causes bigger current being made in the iron core.
  • Hysterosis also increases. (Don’t exactly know)
  • Magnetic stray loss is still negligible but increases.
  • The induced magnetic field becomes stronger.
  • Electric hum a little bit due to more magnetic stray (which causes friction and therefore energy loss).
Is this explanation of trend right or am i wrong or less somewhere?
Or do we need more info?
Thank you

jim hardy said:
Primary current is the MMF that pushes flux.
Secondary voltage is a measure of the resulting flux.

What is the formula that relates flux to current ? Which terms in that formula might be nonlinear ?
Are you asking me or mfbd?
 
  • #56
UtsavRaj said:
Why does it have to be a straight line again?
Are you asking me or mfbd?
I thought you were asking me about the graph in post 49.
Perhaps i responded to the wrong question.

old jim
 
  • #57
jim hardy said:
I thought you were asking me about the graph in post 49.
Perhaps i responded to the wrong question.

old jim
The question i was asking you sir was the explanation in post 55

Thank you for your time everyone
 
  • #58
The Electrician said:
In your chart check the primary voltage of 6.59 volts. The corresponding primary current appears to be about 10 times too large. Same thing for primary voltage of 11.11 volts. These two points on the graph appear to be outliers.

If you fix those two values your graph will look much better; although the very first two voltage values look questionable too.
Screen Shot 2016-07-21 at 5.22.29 PM.png

Sorry, the graph is actually this one
 
  • #59
can please everyone tell me whether the explanation i gave at post 55 is right or wrong or not enough info?
 
  • #60
The Electrician said:
One part of the current is due to the secondary current being "reflected" to the primary.
I do not get this
jim hardy said:
What i wanted to see is -
Is measured flux linear with current ?
This tells us whether it behaves like a solenoid or not?

Thank you for your time
 
  • #61
An explanation on magnetising current and it's losses please. I cannot find anything about it for some reason.
 
  • #62
UtsavRaj said:
This tells us whether it behaves like a solenoid or not?
Tells us how closely it approximates the ideal properties of inductance

recall definition of inductance, L = ##\frac{NΦ}{I}##
 
  • #63
try http://www.rfcafe.com/references/po...nsformer-october-1960-popular-electronics.htm

from an old magazine article he thankfully saved

Core Losses
transformer-theory-oct-1960-popular-electronics-13_small.jpg
Since the iron core itself, as well as the coils, is cut by the expanding and contracting magnetic field, a current is induced here, too. As this eddy current flows in the core, it steals energy from the primary circuit and dissipates it as useless heat. The eddy current flows at right angles to the magnetic flux. It can be reduced by substituting several thin layers of iron for the solid core. These thin layers - laminations - are separated by layers of glue which electrically insulate the laminations from each other. In practice, a small eddy current is set up separately in each lamination, but the total loss is much less than for a solid-core transformer.

Still another core loss is caused by the alternating current itself. Since this current reverses its direction 120 times a second, the iron core - in effect, an electromagnet - must continually reverse its polarity. And since the minute magnetic elements in the core tend to resist this change, power must be expended to realign them. This is called hysteresis loss. Engineers reduce it by building transformer cores of steels which change magnetic polarity with comparative ease, so that less power is consumed in making the switch.

http://uknowledge.uky.edu/cgi/viewcontent.cgi?article=1537&context=gradschool_theses
https://www.bing.com/search?q=transformer+core+loss+scholarly&pc=MOZI&form=MOZTSB
 
  • #64
UtsavRaj said:
"One part of the current is due to the secondary current being "reflected" to the primary."

I do not get this.

This is the essence of what a transformer does.

Google for the search phrase "How transformers work.". You'll find links to several YouTube videos.

In an ideal transformer where there is no loss in the core (and the core has infinite permeability) or in the resistance of the wire making up the primary and secondary, there would be no current drawn by the primary when the secondary is unloaded. If a load were then connected to the secondary, current would be drawn by the primary and that would be supplying power to the secondary load. We say that the secondary load is "reflected" to the primary. The transformer with a load on the secondary would behave as though a load was in parallel with the primary terminals. The magnetic coupling of primary to secondary allows power to be transferred from primary to secondary even though there is no direct electrical connection between the copper wire of the primary and the copper wire of the secondary--the connection is only by means of the magnetic flux that links both windings. This "reflected" load current would be the only current in the primary.

BUT, in a real transformer some current is drawn by the primary even when there is no load on the secondary. This current supplies the losses (in the iron core and the resistance of the copper wire of the primary) and the reactive current drawn by the finite inductance of the primary (the permeability of a real iron core is not infinite as was the case with the ideal transformer). This current is called the "exciting current", and it's still part of the primary current even when there is a load on the secondary. The primary current drawn when there is a load on the secondary consists of two parts--the exciting current and the reflected load current from the secondary load.
 
  • #65
Before I comment I need to:
1. See a definitive data set with the decimal points in the correct places.
2. Know what colour (temperature) the filament lamp glows at the highest currents.
3. Know the primary exciting current when there is no filament of other load present.
Without that there will be confusion.
 
  • #66
UtsavRaj said:
An explanation on magnetising current and it's losses please. I cannot find anything about it for some reason.
Magnetising current is reactive current. It is not real power therefore it is not a real loss, apart from primary series resistance which is very small.
 
  • #67
Screen Shot 2016-08-01 at 6.28.50 PM.png

Screen Shot 2016-08-01 at 6.29.59 PM.png

Screen Shot 2016-08-01 at 6.47.05 PM.png

these graphs are all for the Iron core transformer.
As I thought the effency-voltage graph looked like an inverse-inverse relationship (1/x =1/y) (The last graph with no title)
But shouldn't it go through origin?
Baluncore said:
Before I comment I need to:
1. See a definitive data set with the decimal points in the correct places.
2. Know what colour (temperature) the filament lamp glows at the highest currents.
3. Know the primary exciting current when there is no filament of other load present.
Without that there will be confusion.

2. yellow
3. Cannot be checked due to the school being closed.
Data for Air core
Screen Shot 2016-08-03 at 3.26.32 PM.png


Data for Iron core
Screen Shot 2016-08-03 at 3.26.25 PM.png


jim hardy said:
from an old magazine article he thankfully saved
thank you
 

Attachments

  • Screen Shot 2016-08-01 at 6.30.25 PM.png
    Screen Shot 2016-08-01 at 6.30.25 PM.png
    16.6 KB · Views: 430
  • Screen Shot 2016-08-01 at 6.36.48 PM.png
    Screen Shot 2016-08-01 at 6.36.48 PM.png
    26.2 KB · Views: 419
  • #68
Also, I was looking at what variables i had to control.
I know that the number of coil is controlled by me along with the temperature by using therostat and also the small breaks i took after the wire got too heated.
But when i thought that i controlled the impendance by using 50Hz AC Current and the same wire for all experiment; I remember that my graph says different impendance so i thought someone may help me clarify this.
Anything else that i controlled by using my method?The method went like this:
  • Powerpack attached to rheostat
  • rheostat attached to digital ammeter
  • Digital ammeter attached to Transformer coil (primary winding)
  • Transformer coil attached back to powerpack.
  • The digital voltmeter attached in parallel to the primary coil.
  • The secondary winding was attached to another Digital ammeter.
  • The digital ammeter attached to a bulb of 2 ohms.
  • Bulb attached back to the secondary winding.
  • Another digital voltmeter attached in parallel to secondary winding.
  • All wires were copper wires.
  • All the voltage and current readings were taken from the respective devices and recorded.
Same equipments was used for alll trials and experiment.
 
  • #69
On side note:
I had some medical emergency in my family and that's why i had not been active.

I am sorry.
 
  • #70
..
UtsavRaj said:
As I thought the effency-voltage graph looked like an inverse-inverse relationship (1/x =1/y) (The last graph with no title)
But shouldn't it go through origin?
i'm really confused.

Graph 1 says it's efficiency vs voltage but it doesn't look much like the last graph(untitled)
did you swap axes or something ?

How can you get to origin plotting Pout/Pin ? Origin for that ratio has zero in denominator, and you know one has to be wary of any ratio with a denominator that's infinitesimal. One arranges his experiments to avoid them.

old jim
 