Why isn't Reactive Power defined as Q = S - P ?

In summary, the conversation discusses the definitions and uses of instantaneous, average, apparent, and reactive power in an AC circuit. While the definitions for average and apparent power are straightforward, there is confusion and debate over the definition of reactive power and whether it should be simply defined as the difference between apparent and average power or if it should be represented as a complex number. Ultimately, the decision to define reactive power as a complex number is due to its ability to contain more information about the power in the system, but it can be counterintuitive to understand.
  • #1
vintageplayer
28
3
The instantaneous power in an AC circuit is given by: p = i(t)⋅v(t) = VrmsIrmscosφ + VrmsIrmscos(2ωt -φ).

The average power P = VrmsIrmscosφ is often a useful quantity to know. For example, it can tell me the work being done by a motor.

The apparent power S = VrmsIrms is also a useful quantity to know. For example, it can tell me the maximum work the motor could potentially do (when the current and voltage are in phase φ=0).

However... the reactive power Q = VrmsIrmssinφ = sqrt(S2 - P2) doesn't really tell me anything useful. All I know is that it is some unintuitive measure of the difference between the apparent and average power. Why isn't reactive power simply defined as Q = S - P instead?
 
Engineering news on Phys.org
  • #2
vintageplayer said:
Why isn't reactive power simply defined as Q = S - P instead?
Because P and Q have perpendicular directions. Thus Pythagoras must be used.
upload_2016-1-20_17-14-21.png
 
  • #3
vintageplayer said:
The instantaneous power in an AC circuit is given by: p = i(t)⋅v(t) = VrmsIrmscosφ + VrmsIrmscos(2ωt -φ).

The average power P = VrmsIrmscosφ is often a useful quantity to know. For example, it can tell me the work being done by a motor.

The apparent power S = VrmsIrms is also a useful quantity to know. For example, it can tell me the maximum work the motor could potentially do (when the current and voltage are in phase φ=0).

However... the reactive power Q = VrmsIrmssinφ = sqrt(S2 - P2) doesn't really tell me anything useful. All I know is that it is some unintuitive measure of the difference between the apparent and average power. Why isn't reactive power simply defined as Q = S - P instead?
The definition you give is fine; the reactive power is the energy stored in the system.
 
  • #4
Hesch said:
Because P and Q have perpendicular directions. Thus Pythagoras must be used.
View attachment 94557
This is circular reasoning. We defined it to be that way!
 
  • #5
vintageplayer said:
Why isn't reactive power simply defined as Q = S - P instead?
Q = S - P →
S = P + Q , which doesn't make sense.

A phase shifted current, I / φ, can be represented by the complex value , I / φ = I*cos φ + j*I*sin φ.

Thus S = V * I = V * ( I*cos φ + j*I*sin φ ) = P + jQ ,
j = 1 / 90°

So the only "definition" comes from the complex representation of the phase shifted current, I / φ.
 
  • Like
Likes cnh1995
  • #6
When you study generators
peaks of reactive current and 'real' current occur with rotor directly or perpendicular to stator winding
so it was kinda natural for the old timers' thought processes to go with that complex representaion
figuring it out the first time from physical hands-on is different from trying to back into it from algebra.
 
  • #7
Hesch said:
Q = S - P →
S = P + Q , which doesn't make sense.

S = VrmsIrms
P = VrmsIrmscosφ
Q = VrmsIrms - VrmsIrmscosφ

Then S = P + Q would make sense. This definition for reactive power is more intuitive because you can easily tell how much power in Watts is being stored, and how much power you are using for useful work. For example, 100VAr would mean you are missing out on 100W of extra useful power.

Hesch said:
Thus S = V * I = V * ( I*cos φ + j*I*sin φ ) = P + jQ ,

You're right that it comes out naturally with: VI* = S = P + jQ as long as you define reactive power to be Q = VrmsIrmssinφ. The single complex number contains a lot of information: P = Re{VI*}, Q = Im{VI*}, S = mag{VI*}, φ = arg{VI*} which is probably why Q was defined this way. On the other hand, you're now stuck with an ugly definition for reactive power. For example, 100VAr does not tell you how much power is being stored in Watts.

jim hardy said:
When you study generators
peaks of reactive current and 'real' current occur with rotor directly or perpendicular to stator winding
so it was kinda natural for the old timers' thought processes to go with that complex representaion
figuring it out the first time from physical hands-on is different from trying to back into it from algebra.

Do you have an example (or link to one) of this?
 
  • #8
vintageplayer said:
you're now stuck with an ugly definition for reactive power.
How would you calculate:

100 [W] + 100 [VAr] = 200 [unit ?] ?
 
  • #10
Cosider a box floating in space in the absence of gravity.
images?q=tbn:ANd9GcQ1sW3msIIspdmpLHaidthYPq4WO7htWvFErlwPd7Ii8GadbHVq.jpg

If you give some velocity 'v' to the block at an angle Φ, it will move horizontally with velocity vcosΦ and vertically with velocity vsinΦ. If you know the vertical velocity vsinΦ and horizontal velocity vcosΦ and you are asked to find the total velocity v, would you say it is vsinΦ+vcosΦ? No, because velocity is a vector, you MUST consider it's direction and therefore, the angle it makes with the reference. Hence, you'll have to use Pythagoras theorem here for vector addition. Similarly, voltage and current are PHASORS. Hence, you must consider phase angles as Hesch has demonstrated in #2 and #5. VrmsIrmscosΦ is the power dissipated in the circuit, hence, VrmsIrmssinΦ turns out to be the reactive power in the circuit. Apparent power is the phasor addition of the powers and not simple arithmatic addition.
Also, you can verify this by drawing some waveforms. Take a simple RL ac circuit with some convenient component values and plot the waveforms of active power(power dissipated in R) and reactive power(power absorbed by L)separately for a complete cycle and then calculate their corrosponding average values.
 
Last edited:
  • Like
Likes Hesch
  • #11
Once, I supervized installation of meteting equipment on Power Substation 220KV in Bashkortostan (Russia). Our device showed that nearby plant consumes only 0.5MW of active power but generates 10MVAR of reactive power (due to heating inductors that were switched off just before the measurement).
As for the question then let's look at the speed in horizontal and vertical directions. No one would mechanically sum them. Formula
V=SQRT(Vh*Vh+Vv*Vv)
is almost obvious.
The situation with active and reactive powers is essentially the same. They are (in specific meaning) orthogonal to each other.
Sorry, haven't read previous answers carefully.
 
  • #12
But is it not true that power is a scalar quantity and does not therefore have a phase angle, as do voltage and current?
 
  • #13
If {Vn} and {In} are series of samples (voltage and current) then
P - active power is a sclar multiplication P=ΣVn*In
and thus is a scalar value while voltage and current are vectors. Though RMS values of both voltage and current are scalar values (length of respective vectors).
 
  • #14
tech99 said:
But is it not true that power is a scalar quantity and does not therefore have a phase angle, as do voltage and current?
Yes. Power must be a scalar quantity because Energy is scalar and power is energy per unit time. Imo, "reactive Power" is really an oxymoron which has been introduced into the vernacular for convenience. In a purely reactive component, energy is stored and not dissipated so the 'lost power' must be there because of resistive components in the supply impedance. If people stick with volts and current for their calculations then they can't go wrong and will get the right answers (arithmetic permitting).
 
  • #15
Agree, so it seems incorrect to show vector diagrams of P and Q.
 
  • #16
tech99 said:
Agree, so it seems incorrect to show vector diagrams of P and Q.
I'm not a Power Engineer so I would have to be more careful with my 'shorthand', which is what that diagram is. I would do any calculations the 'formal' way and stand a better chance of getting the right answer. A PQ vector diagram has got to be wrong but it 'may' be forgiveable if the people who use it are aware that they are being sloppy.
 
  • #17
Phasors aren't vectors I've been told by folks who are better at maths than i..

I'd have to go back to Steinmetz - i think it was he who came up with idea of complex numbers to represent AC current...
 
  • #18
tech99 said:
Agree, so it seems incorrect to show vector diagrams of P and Q.

Assume a voltage Vcos(wt) across an impedance of R + jX = Z∠φ

The total instantaneous power is:
p(t) = v(t).i(t) = Vcos(wt).Icos(wt - φ) = VI.cos(wt).[cos(wt)cosφ + sin(wt)sinφ] = (VI/2)cosφ[1 + cos(2wt)] + (VI/2).sinφ.sin(2wt)

The expression above is the total power consumed, and it does not tell you the power consumed by the resistor, or the power consumed by the reactance. The power consumed by the resistor is actually NOT (VI/2)cosφ[1 + cos(2wt)], nor is the power consumed by the reactance (VI/2).sinφ.sin(2wt).

To find the power consumed by the individual resistor and reactance, you have to find the voltage across these individually (e.g. by voltage divider).
vR(t) = (VR/Z).cos(wt - φ) = Vcosφcos(wt - φ)
vX(t) = (VX/Z).cos(wt + 90 - φ) = Vsinφcos(wt + 90 - φ)

Hence:
pR = vR(t).i(t) = Vcosφcos(wt - φ).Icos(wt - φ) = (VI/2).cosφ.[1 + cos(2wt - 2φ)]
pX = vX(t).i(t) = Vsinφcos(wt + 90 - φ).Icos(wt - φ) = (VI/2).sinφ.sin(2φ - 2wt)

Note that adding these two terms together gives the total instantaneous power above (after some further trig identities).

The average power consumed is P = VrmsIrmscosφ.
The peak power consumed by the reactance is Q = VrmsIrmssinφ.

Although both of these quantities are scalars and mean different things (P is the average power, and Q is the peak power consumed by the reactance), you can artificially construct a vector of magnitude VrmsIrmsand angle φ. The x-component of this vector will be the average power P, and the y-component will be the reactive power Q.

I could also define another scalar quantity, Q = S - P, and call it the "reactive power", but it would not be the peak power consumed by the reactance. If you want the "reactive power" to be the peak power consumed by the reactance, then it must be equal to VrmsIrmssinφ.
 
  • #19
vintageplayer said:
(P is the average power, and Q is the peak power consumed by the reactance),
If we are trying to get to the bottom of something as fundamental as this, we could at least get the basics right. How can any power be "consumed" by a reactance? The Current and Volts are in quadrature. The reason that Power Factor is relevant is that the I and V are greater when there are reactive elements in the circuit. The excess current is passing through the Resisitive components of the supply circuit, which 'consume' extra Power. Also, the extra Volts may be relevant.
There is more power consumed when the PF is not unity but there is no way it can be dissipated in reactances. Reactances can only store energy and return it (twice) per cycle. The 'Peak' power involved, (rate that energy is being stored, instantaneously) can be given a value but it is not very meaningful
 
  • #20
sophiecentaur said:
If we are trying to get to the bottom of something as fundamental as this, we could at least get the basics right. How can any power be "consumed" by a reactance?

Power is consumed by a reactance half the time, and released half the time. Just because on the average the power consumed is 0 doesn't mean a reactance doesn't draw power for half the cycle. The peak power it draws is equal to Q.

sophiecentaur said:
The 'Peak' power involved, (rate that energy is being stored, instantaneously) can be given a value but it is not very meaningful

That value is the "reactive power" Q agree?
 
  • #21
vintageplayer said:
That value is the "reactive power" Q agree?
You can give it a name and you can calculate it but how does that value contribute to understanding the AC losses in power engineering? What counts is the wasted mean power in the resistive parts of the supply circuit. You could just as easily talk about the "peak"power being dissipated in a resistive load but who does? If there were no resistance in the supply chain, your "reactive power" would be irrelevant because there would be no supply losses.
 
  • #22
A picture is generally wort a thousand words.
It was helpful for me to look at sinewaves:
draw two of them one above the other
label one Volts and the other Amps
draw a pair in phase,
a pair 180 degrees out of phase,
a pair 90 degrees out of phase and
a pair 45 degrees out of phase

then consider instantaneous power, product volts X amps

For the in phase sinewaves , product is always positive , P = volts X amps, which represents power factor of 1.0 (cos 0 degrees)
for the pair 180 out, product is always negative, power = volts X amps and one of them is always negative , power factor = -1.0 which is cosine 180 degrees

for the others , power is sometimes positive and sometimes negative , over a complete cycle it will average to VIcosθ,
that's what reactive power does - shuttle back and forth between source and load during subcycle intervals.
At 90 degrees observe positive and negative intervals are equal and their average power is zero, e power factor of zero which is cos 90 degrees. Nothing gets hot or does any work.
At 45 degrees - would someone less awkward copy and paste some sinewaves into Paint and post ? That's been done someplace on PF (i remember doing it) but i was unable to find, and paint frustrates me terribly.

You'll find P = VICosθ and Q = VISinθ , and Pythagoras Rules !
I think that visual exercise is a good learning tool. It'll cement the concept.

old jim
 
  • #23
sophiecentaur said:
You can give it a name and you can calculate it but how does that value contribute to understanding the AC losses in power engineering? What counts is the wasted mean power in the resistive parts of the supply circuit. You could just as easily talk about the "peak"power being dissipated in a resistive load but who does?

You might want to know the reactive power if you ever want to control the voltage on a power grid. Or size your capacitors for power factor correction. Or size your power cables efficiently. Also, peak power is an important design spec for almost all electrical devices...
 
  • #24
vintageplayer said:
You might want to know the reactive power if you ever want to control the voltage on a power grid. Or size your capacitors for power factor correction. Or size your power cables efficiently. Also, peak power is an important design spec for almost all electrical devices...
To correct for the power factor of your load you need to know its reactance and then you tune it out as near as you can, using another reactance network. When would you calculate 'Peak Power'? True, the Peak Voltage could be very relevant - but that actually corresponds to the maximum Energy (E = CV2/2) and not to the rate of energy supplied (Power). Sizing your power cables will affect the Resistance and not the Reactance and I've already been into that.
I realize that these terms are all down to usage and it is not likely that they will change. It doesn't make them correct though. "Make it Work' type Engineering is full of slightly dodgy terms and statements - from Water Analogies where they don't apply, to the expression "dB Volts". The field is littered with pitfalls because people got taught these things and pass them on. But Engineers do 'make things work' very successfully and we mostly stuff get away with approximate thinking and that magic stuff called 'experience'.
 
  • #25
aha found it

single phase volts, amps, and power
when volts and amps are in phase ie power factor = 1
observe instantaneous power is always positive

active-power.png
single phase volts, amps and instantaneous power
when volts and amps are out of phase by 90 degrees
observe instantaneous power no longer unipolar, in fact averages zero; cos(90degrees) = 0...
inductive-reactive-power.png


now
vintageplayer said:
The peak power it draws is equal to Q.
vintageplayer said:
That value is the "reactive power" Q agree?

no i don't agree.
do we have a definition of terms question here?
active-reactive-power.png


Where would you select peak power on that graph? Copy&paste into Paint and add an arrow...
I'd guess Q is average of the orange power wave .

those graphs came from http://www.electrical4u.com/electric-power-single-and-three-phase/11
 
  • #26
jim hardy said:
Where would you select peak power on that graph? Copy&paste into Paint and add an arrow...

For a purely reactive component p(t) = (VI/2).sinφ.sin(2φ - 2wt). Q is therefore the peak value of the AC power waveform.
inductive-reactive-power.png


When you have both resistive and reactive components, p(t) = (VI/2)cosφ[1 + cos(2wt)] + (VI/2).sinφ.sin(2wt). Q is the peak of the sine component, but there is no nice way to show it graphically without drawing the sinusoid components separately.

jim hardy said:
I'd guess Q is average of the orange power wave .
The real power P = (VI/2)cosφ is the average of the power wave, not Q.
 
  • #27
Why isn't reactive power simply defined as Q = S - P instead?

For the math side, let's presume a simple measure where S=33 and P=22.
Q = S - P
Q = 33-22
Q = 11

Whereas,
Q = sqrt(33x33 - 22x22)
Q = sqrt(1089 - 484)
Q = sqrt(605)
Q = 24.596
Certainly a nontrivial difference, imo.

However... the reactive power Q = VrmsIrmssinφ = sqrt(S2 - P2) doesn't really tell me anything useful. All I know is that it is some unintuitive measure of the difference between the apparent and average power.

I think we have to remember that S and P are not in phase with each other nor is either one a constant value, largely due to their interaction with each other.
If we relate this to a musical instrument amplification system, for example, being able to measure reactance and it's impact on the waveform at the output, can give us a better understanding of the "perceived" volume of the output.
 
  • #28
jim hardy said:
aha found it

single phase volts, amps, and power
when volts and amps are in phase ie power factor = 1
observe instantaneous power is always positive

active-power.png
single phase volts, amps and instantaneous power
when volts and amps are out of phase by 90 degrees
observe instantaneous power no longer unipolar, in fact averages zero; cos(90degrees) = 0...
inductive-reactive-power.png


now
no i don't agree.
do we have a definition of terms question here?
active-reactive-power.png


Where would you select peak power on that graph? Copy&paste into Paint and add an arrow...
I'd guess Q is average of the orange power wave .

those graphs came from http://www.electrical4u.com/electric-power-single-and-three-phase/11
Good pictures there but your statement here demonstrates the limits of such a graphical approach; you have to infer things that calculus and the complex Maths will automatically prove for you. Furthermore, you would really need to be drawing graphs showing the instantaneous Volts and Current on all R and X elements separately. That would give you some pictorial 'proof' of the situation.
Sorry - I can'tmanage to make the folloing red bits change into black!
It's pretty well accepted that complex notation for Impedance gives the answers for simple circuit questions like this. No one (??) would need to work out the power dissipated in a resistor with an AC applied voltage on a stepwise time basis - at least, not more than once. Likewise, complex arithmetic will give tha answers to all other questions in linear circuits. I would actually disaggree that a picture tells the whole story. Fact is that I am not particularly confident about my Maths; I always go through things several times before believing an an answer. But I basically BELIEVE in it and I accept the results of it. The answer to the main question in this thread is dead straightforward if you draw a realistic equivalent circuit of the system: Voltage Source -> Source R and Source X -> Load R and Load X. You just have to believe that Reactances cannot dissipate Power so wasted power has to go into the source resistance. Instantaneous Power is a totally incidental concept in this question and the calculations do not need to include Phasors, explicitly - why would anyone not believe in such well established procedures?
If the internal resistance and the resistance of supply cables is low enough, compared with the Load Resistance, then the only problem with a non unity PF is the excess volts.
 
  • #29
You just have to believe that Reactances cannot dissipate Power so wasted power has to go into the source resistance.

Wasted power implies that the actual output would be less than the expected average output, whereas an ideal reactance should have 0 resistance and effectively should increase the power output. In terms of sound amplification from a listeners perspective, reactance should make it sound louder.
 
  • #30
Wee-Lamm said:
You just have to believe that Reactances cannot dissipate Power so wasted power has to go into the source resistance.

Wasted power implies that the actual output would be less than the expected average output, whereas an ideal reactance should have 0 resistance and effectively should increase the power output. In terms of sound amplification from a listeners perspective, reactance should make it sound louder.
You have to be careful to specify the exact situation you are describing. You have to be making the right comparison between systems. There will always be wasted power in supply cables etc. That can reduced by reducing the quadrature current flowing through them (that what PF correction is for). . The presence of extra reactances will also alter the power delivered to the load but the consumer pays for what's used - so it's 'fair'.
Your example of audio amplification is the same. An amplifier with zero output impedance (ideal but not far from what you can achieve) will deliver more power to a speaker if there is correct tuning out of reactive elements in the speaker (same for a transmitting antenna).
 
  • #31
jim hardy said:
I'd guess Q is average of the orange power wave .

Well ! That was sure a false cue !

big ten-oops , what was i thinking

still I'm confused by your use of term PEAK. I'm accustomed to it meaning the top of a wave as opposed to average or RMS.
 
  • #32
There will always be wasted power in supply cables etc

I was ignoring line loss as it would be present whether there was an Inductance or Capacitance in the circuit or not, and would not change the formula, but only the values used.

We also know there are 2 types of Reactance that can be made to occur in an AC circuit, Inductance and Capacitance.

Inductance is aimed at maintaining a more constant current flow over a period of time, in that it creates a magnetic field in which it stores more energy as input voltage increase and releases more energy as input voltage decreases. This process of storing/releasing energy causes the current and voltage cycles to be 90 degrees out of phase and ultimately results in a current flow that rises and falls less dramatically than it would without inductor. Ignoring the heat loss of the materials used in the coil and core, the inductor itself does not result in a decrease in power but rather, it results in a higher overage output of power over time and there is less loss resulting from the cycling nature of ac current.

Capacitance is aimed at maintaining a more constant voltage output over a period of time, in that it creates a static electrical field in which it stores energy more rapidly as current increases, and releases energy as input current decreases. Capacitors are more prone to failure and leakage, and do tend to generate more loss through heat by virtue of the materials they are made of, but the act of storing the energy itself does not create a lost of power, it merely stores it to be released as voltage during a period of reduced current input. Capacitors do have the added benefit of blocking DC current while allowing AC to pass through, but that is trivial to this discussion.

In this regard, and ignoring losses that relate only to the materials used to make Inductors and Capacitors, the storage and release of energy itself 'should not' create a loss of power. I suggest that, when measured over a period of time, they each increase the amount of power, in presuming that 'Power' is the measure of how much work can be done by the energy being exchanged.



 
  • #33
sophiecentaur said:
Good pictures there but your statement here demonstrates the limits of such a graphical approach; you have to infer things that calculus and the complex Maths will automatically prove for you.

i like to work the math until i get same answer 3 times in a row
and i can see it agree with a picture

but i didn't do my due diligence for that post...
 
  • #34
jim hardy said:
still I'm confused by your use of term PEAK.
I'm not really in favour of 'Peak Power" as applied in this thread because it's been used in strange ways. The Energy going into and out of a reactance will vary during the cycle and there was the implication that its maximum value is somehow relevant. The "peak Power" into a Capacitor is not at the voltage peak, because that's when the energy is not increasing any more (P=dW/dt) and it's not at a zero crossing, where the current is at its max but the volts are zero. That'w why I have been objecting to the relevance of Power in a Reactance. What counts, surely, is Mean Power which is what gets things hot and costs the money. Power is something associated with Resistance (or the work done by an electric motor). The extra currents and volts, due to reactive load (and transmission) components will cost you because that current flows through actual resistances and can stress components beyond what they're designed for.
In any case, I think this thread has shown that the shorthand formula it started with, has no meaning and is not valid. Treating scalars as if they are vectors really can't ever make sense.
 
  • #35
Wee-Lamm said:
in presuming that 'Power' is the measure of how much work can be done by the energy being exchanged.
Power is defined as rate of energy transfer per unit time. If it's transferred in the load, it will be useful. If it's transferrend in the supply chain, it's loss and will cost everyone, unnecessasarily. A Power source with no resistance (impossible) will not dissipate any power. All generators have finite resistance; they are made with as low resistance as possible (at a cost). Likewise the cables.
I think you are getting too preoccupied with the mechanisms of Reactance for the purpose of this thread. The mathematical description of their behaviour with an AC signal is all that's needed here. The theory is quite good enough for this discussion.
 

Similar threads

  • Electrical Engineering
Replies
12
Views
3K
  • Electrical Engineering
Replies
2
Views
1K
  • Electrical Engineering
Replies
5
Views
2K
  • Electrical Engineering
11
Replies
359
Views
28K
Replies
4
Views
2K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
3K
Replies
3
Views
4K
  • Engineering and Comp Sci Homework Help
Replies
7
Views
5K
Replies
6
Views
1K
Back
Top