In summary, the conversation discusses the concept of power transfer in a transformer and how it relates to inductance and magnetic energy. The participants also touch on the idea of flux and its relationship to primary voltage. They also mention the role of sine waves and how they affect energy flow in a transformer. Finally, they consider the application of these concepts in flyback converters. Overall, the conversation highlights the complexity of understanding power transfer in transformers and the progress the participants have made in their understanding.
  • #211
next few pages from magamp book
wont be home today, will check in tonight
magampsch3 001.jpg
magampsch3 002.jpg
 
Engineering news on Phys.org
  • #212
two more

magampsch3 003.jpg
magampsch3 004.jpg
 
  • #213
and

magampsch3 005.jpg
 
  • #214
tim9000 said:
But even fundementally, even if we had perfect equipment, I still don't understand the tangent slope, or the red line slope, what the difference between the two means, or rather, specifically why the tangent to the curve is V / I, any more than the red line is Z.
Case-in-point see post # 205.
Similarly, I still don't see why the 200 and 400 turn V.s/N curves (which are have such similar B peaks) are so different from the the 840 Turn curve.

jim hardy said:
last point before I go to bed, I was thinking I should be able to get a load line of the mag amp using the inductance relation:
Z = 2*pi*freq* N2*A*µ / length = 2*pi*freq* N2*A*(B/H) / length

that's Zmagamp , 2pi X freq X inductance

which would have the same shape as the µ curve, which is proportional to the gradient of the B curve. ?? It's just a number not a curve unless you make something a variable
Yes, B/H would be varying.

Thanks for the scanned pages of the book! I'll have a good read of them tomorrow, what is the name of that book?

In post #192 I showed a VI curve for the 200 + 200 pair of series coils, their BH curve looks thus:
!!.PNG

It is clearly a different shape than the BH curve of the 200 and 840 coils on their own, and what's-more I can see that when I do B/H plot for the 200, 840 and 400 turn arrangements, that the series coils of total 400 turns has a lower peak μ (as you can even see by eye above). I'm hoping you have some thoughts?
Thank you

p.s
tim9000 said:
To add to the question you moved over threads and the graphs in post #198,
is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance or turns number'?

And I'm still confused as to why Z = ΔV/ΔI at a point, and not just V/I (which is the gradient from zero to point on curve)
i.e. what the difference in compared methods of plotting Z curve in posts #190 and #192 between tangent Z and direct Z = V / I
 
  • #215
is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance or turns number'?
I know I've gone on and on, about asking why Z is the tangent and not the direct line from zero and I think I have a better contextualisation of why that hasn't sat right with me. Think about this:
B is proportional to V, and H is proportional to I. The impedance is proportional to inductance which is proportional to permeability mu, which is equal to B/H. Therefore impedance is the same as V/I, not (delta V) / (delta I)...
 
Last edited:
  • #216
tim9000 said:
png.87834.png

It is clearly a different shape than the BH curve of the 200 and 840 coils on their own, and what's-more I can see that when I do B/H plot for the 200, 840 and 400 turn arrangements, that the series coils of total 400 turns has a lower peak μ (as you can even see by eye above). I'm hoping you have some thoughts?
Thank you
This is probably my most important point of interest at the moment, because when I create an expectation of impedance for a 400 turn curve using the mu curve from the 840 turn BH curve, it is different to if I use a mu from this curve to generate an impedance curve for a 400 turn. (as in Z = wL as a function of B/H)
I find it crazy they're not the same shape BH curve, I can't explain it.
 
  • #217
tim9000 said: ↑ But even fundementally, even if we had perfect equipment, I still don't understand the tangent slope, or the red line slope, what the difference between the two means, or rather, specifically why the tangent to the curve is V / I, any more than the red line is Z. Case-in-point see post # 205.

and here's 205
You may recall I've made mention that I'm still confused regarding ΔV/ΔI I can kinda see why it's the tangent on an actual BH curve because V/N = dΦ/dt However the VI curves I took my excitation V goes up only, it didn't waver, as did my current, now if I take V/N = Area*(B2-B1) points on the BH curve that V/N number will decrease as the curve flattens. So that V is what? the voltage on the core excluding coil? Regardless if I take Area*(B2-B1) / (current2 - current1) from the BH curve it will give me numbers which don't mean anything to me, don't look like impedances I recognise. As I've said if we were taking the direct V / I of the V vs. I curve I could see how that would give us the impedance of the mag amp, but I don't see why the tangent to the curve is relevant...[Anyway I posted some Z comparison curves before.] Thanks

hmm we must be on parallel but not congruent trains of thought .
or rather, specifically why the tangent to the curve is V / I,

i'm going back to basics.
cause i try to think through each question and i get confused,

This is a BH curve

BH.JPG


horizontal is ampturns per meter and since turns and meters are constant, it migt as well be amps
vertical is B, Teslas, if area is known it could as easily be Φ , Webers

If i sweep amps back and forth about zero, at line frequency, flux will sweep up and down the curve also at line frequency.

BHAC.jpg

Definition of inductance is flux linkages per amp, NΦ/I,
and every point in that red line segment has same ratio of N to I
so inductance L in that region is constant and given by slope of red lineWe don't have a flux meter so we'd have to jump through hoops to reproduce that curve.
But before we leave it let's recall way back from post 17
delta_bh-jpg.85302.jpg


nobody said we had to sweep about zero amps
we can push flux midpoint away from zero by adding dc amps(amp-turns), via same or another winding
and we observe that slope of ΔΦ / ΔI decreases as curve flattens out.

We don't have a flux meter but we do have a voltmeter.
since the core is enclosed by some turns,
the changing flux will induce voltage into those turns
so a voltmeter will report n * delta flux in webers per second
since n is constant, voltmeter will report rate of change of flux.
so an AC voltmeter would report our delta flux dimension at any operating point on the curve.
and an AC ammeter would report the delta I dimension
and the ratio of the two meters would give inductance

Now we make a big assumption that let's us move from that swept DC graph to an AC graph.
That assumption is we have sinewaves
sinewaves have the unusual distinction they don't change shape when they get integrated or differentiated, just their phase shifts 90 degrees and amplitude changes by ω, 2Πf .
That allows us to use AC volts as a measure of flux's magnitude not just its rate of change.
Volts = -n dΦ / dt
if flux is a sinewave sin(100Πt) then voltage is a cosine wave 100Πcos(100Πt)
so if we know volts instead of flux , we know flux has magnitude (volts /100pi)

That let's us plot volts versus amps using sinewave voltage excitation (which has to produce cosine flux assuming no IR drop)
And since we're using AC there's no negative, and we make a single quadrant graph like yours

from post 86
untitled2-png.86631.png


they look strikingly similar to one quadrant of the DC curve.
Since volts is proportional to flux (on account of our sinewave assumption)
we might as well use this plot with the caveats:
1. Current will distort from sinewave but the ammeter will report with accuracy good enough for our purposes...
2. The meters report RMS assuming sinewave form factor, so peak flux is maybe 41% more than our numbers suggest and current peaks may be much more than the numbers suggest. Remember those horrendous current peaks in post 92

To produce the numbers for those two plots you swept current and voltage about zero
so you extracted numbers from sweeps like these and plotted rms delta flux measured by volts versus rms delta amps

BHAC2.jpg

and what was plotted won't flatten out on the wings so severely as does the B curve
because we swept across the entire curve , through zero.
But it's the best we can do with meters.
Recall inductance out on the flat part is less than in the steep part because μrelative becomes so small.
so after we cross the knee BH flattens out
had we swept only between current 2 and current 3, Δvolts would be miniscule
and that's why impedance out on the wings is the slope.
Actually it's the slope over the range of current sweep .

BHAC3.jpg


So, for your plots with no DC, impedance is volts/amps because you swept symmetrically about zero
WITH DC, your AC meters will still report volts and amps over the range of sweep, maybe from red line 2 to red line 3
and their ratio volts/amps is the slope over that range of sweep
so maybe i just misunderstood your questions about slope.

this is from post 192

I thought this may be of help, I took extracts from my large data set where I was exciting the two series 200 turn coils, for values where the DC was off, remember V3 is the voltage across the Amp:
v3-vs-i-png.87462.png

is current really 0 to just 100 microamps ? I have to think you meant 100 milliamps...
and was this with a lamp load or just the coils across a supply ?
Lamp load will not allow big current peaks , the voltage will shift from coils to lamp during that part of wave, meaning we no longer have sinwave excitation voltage nor do we have cosine flux.

That's my best guess right now...

If you had no lamp load
then we must take a look at flux in the core again

TimsFluxWLoad.jpg
DC flux zero, Rlamp zero, windings in series aiding
reluctance of path should be sum of those legs
only imbalance will traverse center leg
...
if instead they're in series opposing
now flux takes the white path instead of red path
iirc center has 2x area of outers, so saturation should be sharp because B is same everywhere

gonna post this before it disappears
 
  • #218
tell us more about those 200 400 800 turn measurements
 
  • #219
I'm completely snowed under, I've been obsessing over (especially posts #215 and #216) this; and my Comsol simulation hurdle, I really need to start studying for my induction machines and AC windings topic test that's coming up.

I have this tendency to hear what I want to hear but I really am trying to understand where you're coming from, so sorry this is takng so long.
Please read this paragraph through including the quote and sentence below that, twice, so you take my meaning:
So there really isn't a ΔV/ΔI, infact Z*N = V/I = dΦ/dI ?
That is to say, 'the tangent to the BH curve IS the direct V/I curve value'?
However I don't understand how "and an AC ammeter would report the delta I dimension", unless 'delta I' is the same as = " H*length / N " because that's the conversion between BH and VI curves if I'm not mistaken?
You can see the big black current meter in the picture in post #93, I'm pretty sure it was a true rms ammeter, don't you think? So how would that show the current if it was very not sineusoidal?
This logic I would like to hear more about:
jim hardy said:
So, for your plots with no DC, impedance is volts/amps because you swept symmetrically about zero
WITH DC, your AC meters will still report volts and amps over the range of sweep, maybe from red line 2 to red line 3
and their ratio volts/amps is the slope over that range of sweep
I concur about that being the part where the sweep takes place, that area is caused by the BRMS adding and subtracting from the BDC, so it won't be too big and since it's in each leg and they're symmetrically opposite they should ballance out to just BDC shouldn't it?
{When you're looking at the VI curve Z = V/I, when you're looking at the BH curve Z*N = dΦ/dI }?? Unless you're saying that doesn't hold because the instruments measuring are inaccurate because of the non sinusoidal voltage and current?
jim hardy said:
is current really 0 to just 100 microamps ? I have to think you meant 100 milliamps...and was this with a lamp load or just the coils across a supply ?
That's quite right, I think a few posts later I made a correction of that it was A not mA. Also you can see it's BH curve in post #214. That was for the lamp in series with the 400 turns, with the DC control OC, V3 was the voltage just on the 400 turns, but the current was ofcourse going through amp and lamp-load.
R.E. post #216: It's like shunting between the two excited 200 turn coils (the centre leg), has lowered the peak permeability and increased the necessary H [A/m], making the BH Curve for 400 turns much more linear. And yes, as you say they are series adding so only imbalance will traverse the centre leg, so I'm not sure why the BH curve of my 400 turns is so different.
 
Last edited:
  • #220
Aha i woke up at 2am with a start
realizing my rusty math confused us back in post 202

Just to double check, V.s = V/(2*pi*freq) right??

of course it is despite my statement to contrary a few lines further down.
i woke up realizing volt-seconds is the integral of volts * dt, so flux IS volt- seconds because that's the integral of volts .

I mixed the definite and indefinite integrals.
Sine is always presented as swinging between -1 and +1
its integral, cosine, also swings between -1 and +1
and that's the indefinite integral which includes a constant of integration C, which we usually set to zero.
http://www.intmath.com/integration/integration-mini-lecture-indefinite-definite.php (they use K instead of C)
anyhow indefinite integral gives a function , definite integral gives a number
and i solved for number .
Definite integral of sinX can swing between -1&+1, between -2&0, between 0&+2, or any span of 2 in between
depending on where you start and finish.
I calculated from zero to pi which gives 2.

from 102 said:
In that last post, there is an implicit understanding of mine that flux = V.s/N and I'll throw some numbers in for colour: Take the knee point flux density; Vrms*√2*2 / (π*f*A*N) = 296*√2*2 / (π*50*0.00111*840) = Vpk*2 / (π*50*0.00111*840) = 5.7163 T But we previously determined using the EMF equ that the knee point was about 1T

this
Vrms*√2*2 / (π*f*A*N) = 296*√2*2 / (π*50*0.00111*840) = Vpk*2 / (π*50*0.00111*840) = 5.7163 T
needs 2pi not just pi in denominator
Vrms*√2*2 / ( 2π*f*A*N) = 296*√2*2 / (2π*50*0.00111*840) = Vpk*2 / (2π*50*0.00111*840) = 5.7163 2.858 T ,peak to peak, 1.01 RMS

This post is out of sequence i know,, just i have to resolve these details or i go nuts.

You were quite right. My rusty math misled me.

on to your 400 turn curves...
 
Last edited:
  • Like
Likes dlgoff
  • #221
tim9000 said:
That was for the lamp in series with the 400 turns, with the DC control OC, V3 was the voltage just on the 400 turns, but the current was ofcourse going through amp and lamp-load.
R.E. post #216: It's like shunting between the two excited 200 turn coils (the centre leg), has lowered the peak permeability and increased the necessary H [A/m], making the BH Curve for 400 turns much more linear. And yes, as you say they are series adding so only imbalance will traverse the centre leg, so I'm not sure why the BH curve of my 400 turns is so different.
tim9000 said:
This is probably my most important point of interest at the moment, because when I create an expectation of impedance for a 400 turn curve using the mu curve from the 840 turn BH curve, it is different to if I use a mu from this curve to generate an impedance curve for a 400 turn. (as in Z = wL as a function of B/H)
I find it crazy they're not the same shape BH curve, I can't explain it.
this curve ? Taken with lamp load?
v3-vs-i-png.87462.png


compared to this one, with no lamp load?

upload_2015-8-29_13-6-25.png
Let me take that lower one which goes to 500 ma
and stretch its horizontal axis to about same as upper one that goes only to 100 ma

200turnstretch.jpg

that places 100 ma on both plots at at about four fingers out on horizontal axis, on my screen
and 35 volts per coil about two fingers high

still , in your upper curve out past the knee current rises more slowly with voltage, which i'd attribute to load resistance reducing peak currents.
can you rescale your plot and see what it looks like?
 
  • #222
tim9000 said:
because when I create an expectation of impedance for a 400 turn curve using the mu curve from the 840 turn BH curve, it is different to if I use a mu from this curve to generate an impedance curve for a 400 turn.

Did they compare when we used all data with no lamps? That'd support premise of not much flux down center leg when exciting from outer legs in series aiding.I've blown up the picture of your big meter but can't read the fine print on the face.
Since the scales look nonlinear i suspect it's an iron vane movement which responds to the true RMS volts or amps..
Keep in mind as soon as we depart from sinewave, peak is no longer RMS X√2 .
 
  • #223
jim hardy said:
needs 2pi not just pi in denominator
Vrms*√2*2 / ( 2π*f*A*N) = 296*√2*2 / (2π*50*0.00111*840) = Vpk*2 / (2π*50*0.00111*840) = 5.7163 2.858 T ,peak to peak, 1.01 RMS

This post is out of sequence i know,, just i have to resolve these details or i go nuts.
I know what you mean about needing to resolve details and I'm glad for your attitude. I see what you're saying, however I'm still not sure I agree yet. so say the 'seconds' part is equal to 1/ω because if it was equal to 1/f, that would only be for a fixed point in time. Well we can see from the TX emf equ that Brms = V.s/NA so VRMS.s = VRMS/2πf = VRMS/ω = VPK/[√2*2*π*f] = 0.9422 webers thus 1.01 [Tesla] RMS
Using that logic of T = 1/ω for average volt-seconds:
Vave.s = 2*VPK/π * 1/ω = [2*VRMS*√2 / π] * [1 / 2*π*f] = [VRMS*√2] / [π2 * f] = 0.8483 webers thus 0.9098 T Average, which multiplied by 1.11 to convert to RMS by dividing by 2*√2/π is 1.0098 [Tesla] rms
So is the Average Volt-seconds more valid than the RMS, or vice-versa?

Next:
R.E:
jim hardy said:
this curve ? Taken with lamp load?
v3-vs-i-png.87462.png


compared to this one, with no lamp load?

View attachment 87965Let me take that lower one which goes to 500 ma
and stretch its horizontal axis to about same as upper one that goes only to 100 ma

View attachment 87964
that places 100 ma on both plots at at about four fingers out on horizontal axis, on my screen
and 35 volts per coil about two fingers high

still , in your upper curve out past the knee current rises more slowly with voltage, which i'd attribute to load resistance reducing peak currents.
can you rescale your plot and see what it looks like?
So does a true rms meter with an actual steel core inside still show the RMS of a non-sinusoidal current or voltage?
jim hardy said:
Keep in mind as soon as we depart from sinewave, peak is no longer RMS X√2 .
That's a good point, so it might still give me a good RMS reading but the value of the peak will be a mystery?
It actually occurred to me this morning that the difference might be the load attached and not the arrangement of the coils, so I think we're on the same page about this, but it seems SOOO strange to me that the external circuit via the current limiting of the bulbs, would or could limit or modify the inductance and permeability of the amp itself. I thought that as the shape of the curve would be a property of the core material alone.
jim hardy said:
still , in your upper curve out past the knee current rises more slowly with voltage, which i'd attribute to load resistance reducing peak currents.
can you rescale your plot and see what it looks like?
But this also looks like it's effecting the BH curve BEFORE the knee! As it rises slower
So the BH curve is only useful for telling the knee point value, everything else about the curve shape is variable? The more resistance in series with the amp, the less inductance I can get out of it? That's cruel.
Is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance (through cross-sectional area) or turns number'?
I can see that with an additional series resistance to the amp that, that is sucking away from the amp it's share of KVL's V.s
however I didn't anticipate that...what? I'd never be able to achieve the same V.s to get me to maximum inductance??
 
Last edited:
  • #224
tim9000 said:
I know what you mean about needing to resolve details and I'm glad for your attitude. I see what you're saying, however I'm still not sure I agree yet. so say the 'seconds' part is equal to 1/ω because if it was equal to 1/f, that would only be for a fixed point in time. Well we can see from the TX emf equ that Brms = V.s/NA so VRMS.s = VRMS/2πf = VRMS/ω = VPK/[√2*2*π*f] = 0.9422 webers thus 1.01 [Tesla] RMS
Using that logic of T = 1/ω for average volt-seconds:
Vave.s = 2*VPK/π * 1/ω = [2*VRMS*√2 / π] * [1 / 2*π*f] = [VRMS*√2] / [π2 * f] = 0.8483 webers thus 0.9098 T Average, which multiplied by 1.11 to convert to RMS by dividing by 2*√2/π is 1.0098 [Tesla] rms
So is the Average Volt-seconds more valid than the RMS, or vice-versa?

i need to chew on that. You ask tough questions.

Did you notice in the old textbook he subtly (and without announcing) switched from peak to mean amps ?
tim9000 said:
so I think we're on the same page about this, but it seems SOOO strange to me that the external circuit via the current limiting of the bulbs, would or could limit or modify the inductance and permeability of the amp itself.
i think we're heading for a consensus and i hope it's scientific truth

i am crcumspect of calculations because of the fact when we get to the knee, inductance changes every cycle and current depatrs from sinewave.
Recalling that for modest excursions past knee, saturation happens late in the half cycle so voltage collapse will distort voltage less markedly than current wavewave especially with some load to limit the current spike

volt_secSine2.jpg


tim9000 said:
So the BH curve is only useful for telling the knee point value, everything else about the curve shape is variable? The more resistance in series with the amp, the less inductance I can get out of it? That's cruel.

mmmm i think that's why they add diodes to make it self saturating. That's positive feedback, gives much higher gain.
tim9000 said:
But this also looks like it's effecting the BH curve BEFORE the knee! As it rises slower
?

i saw ~30 volts per coil at 50 ma on both graphs, but that's by eye
 
  • #225
What was the name of the Transducer book again?
So does a true rms meter with an actual iron vane inside still show the actual RMS of a non-sinusoidal current or voltage? But if it's not sineusoidal we're up the creek as to knowing what it's actual peak is?
jim hardy said:
"
tim9000 said:
But this also looks like it's effecting the BH curve BEFORE the knee! As it rises slower"
?

i saw ~30 volts per coil at 50 ma on both graphs, but that's by eye
Which graphs are you talking about? The 200 turn and 400 turn? Is that just a coincidence? Well what I mean about the load affecting the curve shape slower rise before saturation too, is:

These are the BH values calculated from V and I with no load for the 840 and 200 turn coils, but with the load on the 400 turn coil. The Voltage used to calculate B for the 400 turn was V3 directly over the amp, not the supply:
bh.PNG

You can see it's resulting curve at the bottom below (as I have posted previously) Zbulb is in Ohms:
Capture.PNG

However the curve above that uses Vexcitation (a.k.a V1) and Zamp and Zbulbs, to calculate a new value of H:
H = 400*(V1/(jwL-ZBulb))/0.31
to try to create a value of current as if there was no load bulbs, so it'd be recreated like the other data curves. You can see the shape is pulled back, so that it is steeper, however it seems to cross the 1 T point at over H = 120+
whereas before it was near 100 [A/m], and for the other 840 and 200 turn curves it was a bit over 50 [A/m]
The new permeability calculated with the new H still doesn't resemble the 200 or 840 turn coil. One other strange thing is that when I give the same treatment to calculating B400 turns, using voltage divider to calculate the voltage on the amp, rather than just using the measured voltage on the amp, it changes the shape of the curve a bit. but I don't know what to make of it, just adds more questions (it doesn't even get to 1 T):
b too.PNG


When I said "it seems SO strange to me that the external circuit via the current limiting of the bulbs, would or could limit or modify the inductance and permeability of the amp itself." and you said:
jim hardy said:
i am crcumspect of calculations because of the fact when we get to the knee, inductance changes every cycle and current depatrs from sinewave.
Recalling that for modest excursions past knee, saturation happens late in the half cycle so voltage collapse will distort voltage less markedly than current wavewave especially with some load to limit the current spike
I see in your sketch as the amp saturates and it's impedance collapses, so does the voltage on it, but as the current starts to spike the resistance of the bulbs surpresses it, but that's during saturation, what about before, when I want to get maximum gradient on the BH curve, and maximum inductance. Can you explain by what mechanism is actually stopping us from reaching that same permeability we thought the material of the core offered, anymore?
Those measurements were taken directly over and through the mag amp, how can something external to the amp do that to the magnetising characteristic? I just don't get it, I've been playing on Excel and there's no way I can transform the 840 BHcurve into something that fits my 400 turn recorded BH curve. (maybe if there was some sort of itterative set of equations to solve, that's the only thing I can think of)
Is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance (through cross-sectional area) or turns number'?
I can see that with an additional series resistance to the amp that, that is sucking away from the amp it's share of KVL's V.s
however I didn't anticipate that...what? I'd never be able to achieve the same V.s to get me to maximum inductance?
 
Last edited:
  • #226
I know one thought at a time, so feel free not to reply to this post for a while, because we've got enough on our plate already...too much:
jim hardy said:
from his page
upload_2015-8-3_9-24-29-png.86783.png


each of your outboard legs would see halfwave not full rectified
jim hardy said:
mmmm i think that's why they add diodes to make it self saturating. That's positive feedback, gives much higher gain.
What's happening to the dΦ/dt abovee compared to whole cycle? I assume it's the same?
I don't really understand the gain aspect, or you saying that "self saturating...positive feedback". How so?
I understand that there's a loss in re-orienting the grain of the steel, so feeding it in only one direction cuts out on the magneto-strictive waste, but how else is it positive feedback, how else is the grain improved and how is it self-saturating?
 
  • #227
tim9000 said:
What was the name of the Transducer book again?
"The Magnetic Amplifier" by J H Reyner

it's around in newer editions than mine, hopefully with clearer explanations
http://www.abebooks.co.uk/servlet/BookDetailsPL?bi=624551024&searchurl=tn=magnetic+amplifiers&sortby=20
https://www.amazon.com/dp/B0000CHQ4B/?tag=pfamazon01-20
http://biblio.co.uk/book/magnetic-amplifier-reyner-j-h/d/172384580

national library of Australia is aware of it
http://trove.nla.gov.au/work/18059418?selectedversion=NBD44524857

http://primo-direct-apac.hosted.exlibrisgroup.com/primo_library/libweb/action/search.do?vid=CSIRO&tab=csiro&fn=search&vl(freeText0)=magnetic+amplifier+reyner+j+h

http://natlib.govt.nz/items?i[century]=1900&il[subject]=Magnetic+induction
https://openlibrary.org/works/OL5414113W/The_magnetic_amplifier

pm me an address and i'll mail you mine, just please return it ? looking closer mine's 1950 (MCML)

i've not run across one with the excruciating graphical development this one has.

In my younger days i'd model it in Basic with a do loop...
Define setup voltspeak , Rload, core dimensions, Nturns,
L0 = Nturns2 * Area/Length
and initial voltage, current & flux
For millisec = 1 to 60000 ; a minute should show if model is stable
Murelative = f(flux) ; start with a two straight segment BH curve to debug Mu = min (mx+B)'s
Vsource = Vpeak*sin(milisec/10 * pi)
Vmagamp = Vsource - current * Rload
Lmagamp = L0 * Murelative
delta-I = Vmagamp/Lmagamp
delta-flux = delta-I * Lmagamp / Nturns ; check my physics here?
current = current + delta-I
flux = flux + delta-flux
...
print Vsource, Vmagamp, Flux, Current
...
Next milliisec

i normalized everything to be printed such that full scale is 132, set printer for 132 character line width,
turn variables into string variables,
each string is all spaces (ascii 20h?) and an asterisk(or other identifying character) in the nth place, insert linefeed
in the days of dot matrix printers with fanfold paper it gave great graphs, turn paper sideways as it feeds out..

Doubtless you do it with spreadshseets nowadays... i could never get Excel to work for me., when Windows quit supporting Qbasic i rescuscitated my TI99 .. but it's gone with last move. I may have another DOS machine with Qbasic in my near future, though

take above as an approach, not Gospel - I've never done exactly that simulation
 
Last edited:
  • #228
tim9000 said:
but it seems SOOO strange to me that the external circuit via the current limiting of the bulbs, would or could limit or modify the inductance and permeability of the amp itself.

I think what it modifies is what we see on our meters, and that affectes the graphs we plot from those meter readings.
Instant by instant that flux is somewhere, permeability is somewhere, current and voltage are somewhere
but we have to interpolate those "somewheres" through averageing or RMS'ing meters
tim9000 said:
Which graphs are you talking about? The 200 turn and 400 turn? Is that just a coincidence? Well what I mean about the load affecting the curve shape slower rise before saturation too, is:

These two graphs
v3-vs-i-png.87462.png


and
200turnstretch-jpg.87964.jpg


which i think are observed volts versus observed amps
tim9000 said:
These are the BH values calculated from V and I with no load for the 840 and 200 turn coils, but with the load on the 400 turn coil. The Voltage used to calculate B for the 400 turn was V3 directly over the amp, not the supply:
nice looking table, readable and organized.
For my plodding brain - how did you calculate B from volts? Just multiply?

And what's H on this graph just below the table? Some f(measured amps) ?
capture-png.88028.png


i confuse easy, thanks for patience

we have to be almost there.
 
  • #229
tim9000 said:
I see in your sketch as the amp saturates and it's impedance collapses, so does the voltage on it, but as the current starts to spike the resistance of the bulbs surpresses it, but that's during saturation, what about before, when I want to get maximum gradient on the BH curve, and maximum inductance. Can you explain by what mechanism is actually stopping us from reaching that same permeability we thought the material of the core offered, anymore?

I'm not convinced there is noticeable difference below the knee.
That was basis of my remark above, 'both curves are two fingers high on volt axis at four fingers out on current axis'
I could only resize the two graphs to same scale by stretching with Paint and you see the results.

So long as Vsupply remains too small to push flux into saturation region, current does not spike and bulb remains very minor player.

What were raw measured volts-per-coil at 30 ma with and without lightbulbs ?
I still haven't accepted there's a difference,
maybe i watch too much Lt Columbo...
 
  • #230
jim hardy said:
And what's H on this graph just below the table? Some f(measured amps) ?
So H is on the horizontal axis, H was just measured current*400/0.31
crtitical.png

Why was my meter telling me I was only getting 1289 Ohms out of the amp, when I should have been getting 2424 Ohm out of it?

jim hardy said:
These two graphs
v3-vs-i-png.87462.png


and
200turnstretch-jpg.87964.jpg


which i think are observed volts versus observed amps
Is this what you were trying to do (Z per turn or volts per amps per turn):
VperIN.PNG

I don't know what to make of it, they're both vastly different than the 840 turn one, so I don't see any value in the comparison. Ok I see what you're observing, interesting:
VvsI.PNG

They're both very different from the 840 turn curve though. See the peak permeability for the 200 turn coil was 0.0217 and the peak permeability for the 840 turn coil was 0.0269, I'd put the difference down to the 840 turn coil being better because the flux path was symmetrical. Anyway the fact remains that when I use the permeability of the 200 turn coil data, even though the V/N curve is the same vs current, the permeability will still predict an impedance much greater than which I measured! Also, is it just me or do the 400 and 200 turn BH curves cross the 1 Telsa mark at very different values of H??
The peak permeability of the 400 turn coil wsa only 0.0143!
In a partial conclusion of WFT: for the 200 and 400 turn coils, the BI curves are the same, but when I transform I into H, the curves become different. How can that be?:
VVdiff.PNG

And shouldn't the 840 turn Volts per Turns Vs I be the same as the other two curves??
[Weird, BH of 200 and 840 is the same, BI curves of 200 and 400 the same, seems like an impossibility because one is always in discord with the other two]

jim hardy said:
national library of Australia is aware of it
That's a 5 and a quater hour drive from me, so nice to know I have that option.
jim hardy said:
pm me an address and i'll mail you mine, just please return it ? looking closer mine's 1950 (MCML)
Thanks for the offer, I'm not going to say 'no', but time is really getting critical and I'm not sure how long that would take, I've really got to figure out what's going on here so I can press on with the rest of the project, this aspect has got me tearing my hair out.
 

Attachments

  • VperIN.PNG
    VperIN.PNG
    3 KB · Views: 437
Last edited:
  • #231
Alright, I still need you to shed some light on a great many things, including why the 840 turn Volts per Turns Vs. I, shouldn't that be the same as the other two curves?
[EDIT: please read through before putting pen to paper]
But I've had a think and I may have made a bit of progress regarding the BH of the 400 turn, I think I was using a wrong magnetic path length, increasing it, it looks like this:
titled.png

You can see it's closer to the 840 and 200 turn BH curves, HOWEVER I also had to change the 200 turn magnetic path length from 0.2274 to 0.28m, to get it to sit exactly over the 840 turn BH curve as you see above. BUT the 400 turn curve IS STILL FORWARD a bit and I'd like to know why! So it's permeability still isn't quite right, which is infuriating. You can read in the blurb in the picture, I think that as you said the non true RMS meter becomes dodgier and dodgier as the voltage gets higher and KVL is no longer represented truely. So I think that the current is probably pretty accurate and each voltage reading gives an 'ok' impedance when divided by the current, but still not great, and if you add the voltages up to get a resistance value than you're compounding the inaccuracy, as demonstraited if you used a calculated expectation of the bulbs:
Zload = 50.4 + 2008.8*current [Ohm]
That will give an even more dramatic divergence in the 'indirect curve' shape:
titled2.PNG

So I'm not sure what's reliable and what's not anymore, due to the non true rms. You're going to have to remind me, does a DMM measure the peak and calculate RMS or vice-versa? I take it, that it gets peak and estimates RMS? If so then that means V1 is reliable because it is a very sineusoidal supply, and that probably VL is reliable but that since V3 is going over the knee that the voltage on that gets less and less accurate and that's the source of inaccuracy. If so that means that it was actually my V3/I curve that was wrong and that the permeability was actually higher than I thought and the expected inductance was probably correct?

EDIT:
Using the notion that V3 was actually the unreliable weak link in KVL, for the aforementioned DMM reason, I calculated V3 = V1 - VL, and used that to calculate B, HOWEVER I REMEMBERED THERE WAS A SPLIT IN THE CENTRE LEG, I'd been modeling it as all a one piece core, BUT I suppose that's only true when there is a DC excitation. So by fitting the BH curves I can see that there is an effective magnetic path length of 0.6m, so using that to calculate H, then the curves fit and the permeability is almost the same, so the predicted impedance of the amp at that [A/m] is 1252 Ohms and the actual calculated impedance using (V1-VL)/I = 1260 Ohm, so they're really close now as you can see (400 turn indirect):
ideologue.PNG

You can also see that the voltage on the amp starts to drop as the voltage on the bulb starts to rise at the knee point. As you predicted.
So was I right about the RMS of V3 being a red-herring?
Also all my other questions still stand such as:
>Is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance (through cross-sectional area) or turns number'?
> including why the 840 turn Volts per Turns Vs. I, shouldn't that be the same as the other two curves?
> Post #226
>
tim9000 said:
I'm completely snowed under, I've been obsessing over (especially posts #215 and #216) this; and my Comsol simulation hurdle, I really need to start studying for my induction machines and AC windings topic test that's coming up.

I have this tendency to hear what I want to hear but I really am trying to understand where you're coming from, so sorry this is takng so long.
Please read this paragraph through including the quote and sentence below that, twice, so you take my meaning:
So there really isn't a ΔV/ΔI, infact Z*N = V/I = dΦ/dI ?
That is to say, 'the tangent to the BH curve IS the direct V/I curve value'?
However I don't understand how "and an AC ammeter would report the delta I dimension", unless 'delta I' is the same as = " H*length / N " because that's the conversion between BH and VI curves if I'm not mistaken?
You can see the big black current meter in the picture in post #93, I'm pretty sure it was a true rms ammeter, don't you think? So how would that show the current if it was very not sineusoidal?
This logic I would like to hear more about:
jim hardy said:
and that's why impedance out on the wings is the slope.
Actually it's the slope over the range of current sweep .

bhac3-jpg.87911.jpg


So, for your plots with no DC, impedance is volts/amps because you swept symmetrically about zero
WITH DC, your AC meters will still report volts and amps over the range of sweep, maybe from red line 2 to red line 3
and their ratio volts/amps is the slope over that range of sweep
I concur about that being the part where the sweep takes place, that area is caused by the BRMS adding and subtracting from the BDC, so it won't be too big and since it's in each leg and they're symmetrically opposite they should ballance out to just BDC shouldn't it?
{When you're looking at the VI curve Z = V/I, when you're looking at the BH curve Z*N = dΦ/dI }?? Unless you're saying that doesn't hold because the instruments measuring are inaccurate because of the non sinusoidal voltage and current?
 
Last edited:
  • #232
P.S:
That sentence regarding self saturation:
jim hardy said:
With that self saturating arrangement with diodes, post 120, your DC holds the cores "off" against the applied ac halfwave - zero current will i think be full on.
By driving the flux below zero before start of cycle, you control how many volt-seconds are required to reach saturation and collapse the impedance.
I specifically could do with an elaboration for.

Also, the reason I keep bringing back up this tangent business is I want to reconcile my induction function of impedance: Z = 2pif*L(B/H), method with your slope of curve method. I am confident my method of finding the Z of the amp at a B point works, but I'm sure yours does too, and must essentially be the same thing, and we've spent so long talking about it, I'd like to understand your method too.

tim9000 said:
>Is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance (through cross-sectional area) or turns number'?
OR is does maximum inductance point depend on V.s/N and Area? Because say you were already at the point of maximum inductance, if you increase area (holding excitation same), you decrease B and so move away from the point of maximum inductance, so you'd need to increase V.s/N again to get back to maximum inductance?
Because it becomes like if you have a set supply amplitude and frequency, that if you are at maximum inductance/maximum permeability, and you want more inductance than you have to increase the number of turns or the area, but if you do that, then you decrease B = V/(N*A*2*pi*f)
So what on Earth do we do about this Catch 22? Or is it an unfortunate fact that the more inductance we have, the less the permeability is? An inefficient use of the material right down the bottom of the BH curve?

Cheers
 
Last edited:
  • #233
tim9000 said:
So is the Average Volt-seconds more valid than the RMS, or vice-versa?
I don't think so. As you observed the RMS and average numbers are related by just a constant.
Wichever numbers our meters are reporting to us, RMS or average X 1.11 (and we're not absolutely sure which it is), so long as we we remain consistent in manipulating them our results should come out consistent.

tim9000 said:
You can see the shape is pulled back, so that it is steeper, however it seems to cross the 1 T point at over H = 120+
whereas before it was near 100 [A/m], and for the other 840 and 200 turn curves it was a bit over 50 [A/m]
i'd thought maybe we needed to visit path lengths , and i see from later posts you did.
timscoreflux2.jpg

for each condition of excitation
we need an equivalent magnetic 'effective path length'

TimcoreLeff.jpg

i just guesstimated to center of core cross section from the drawing, you can actually measure more carefully and contemplate flux .

^^^^^ that sketch there tells me that 200 and 400 turn readings will have a different approach to saturation.
Remember the parallel with Ohm's law: MMF = Flux X Reluctnace,
Let us consider a single 200 turn coil on left leg, pushing flux clockwise.
Effective peth length is series-parallel combination as in sketch, and check my number...
1. Flux in leftmost three segments flows through area A.
2. At junction with center leg, that flux splits 3 ways, some going down through area 2A and the rest continuing to right through area A.
3. So long as we're in linear area of core, mmf drop across each segment of the core is in proportion to flux/area X length
4. As soon as leftmost three legs approach their knee, they absorb larger share of MMF. Center leg and rightmost Dsection are not anywhere near saturation.
So i'd expect 200 turn curve to be pulled to left and show slightly higher flux at saturation?
Did it do that? Check my thinking, I'm famous for dyslexic thought reversals.

Repeat for 400 turn, ie both outside legs excited
Effective path length is sum of outside pieces
Flux now flows clockwise around outer loops, middle leg sees only unbalance so it's not abig mistake to ignore it (a big shorted turn around it would keep flux out of there).
Significant difference is now the whole path has same flux and same area so it hits knee all together instead of piecemeal.
That'll surely give a different approach to saturation ?

Repeat for 800 turn.
Path length is now parallel combination of the two D-sections
Again flux density is same everywhere so approach to saturation will be well behaved, maybe even better than 400 turn because center leg is no longer an unknown.

Now back to your curves
Should volts per turn vs current curves differ by ratio of path lengths ?
But when corrected for path length, agree pretty closely, but 200 turn curve affected by non-uniform B around its magnetic path ?

Your last graph looks really promising in that regard.

ideologue-png.88078.png


tim9000 said:
So was I right about the RMS of V3 being a red-herring?

I think so... but it's necessary to consider all possible stumbles and be aware of what we have chosen to ignore. Was not time wasted.
If you form the habit of checking out the "really dumb things" but never mentioning it, you occasionally get hailed as brilliant when one of those "small things of the Earth confounds the mighty" and you were the only one humble enough to check for it.

tim9000 said:
>Is it fair to say that 'for each material core, there will be a specific V.s/N at which the is the V.s/N where maximum inductance can be achieved, regardless/irrespective of reluctance (through cross-sectional area) or turns number'?
Are you postulating a point of inflection on the BH curve? I think the answer has to be yes
back to the future ?
For this material it'd be steepest part of the curve, and not a major effect though.

BH-curve-50.jpg
tim9000 said:
including why the 840 turn Volts per Turns Vs. I, shouldn't that be the same as the other two curves?
Path length ? Didnt you already come to that conclusion in above graph ?
 
  • #234
upload_2015-8-3_9-24-29-png.86783.png


With addition of the diodes and swapping from series to parallel,

let's look at what happens in each core.
First,
observe that load current (if any) is pulled out the dotted end of the load windings
making the dotted end of the control windings positive
which makes the dotted and of the control winding positive, opposing control current source.
From an old Navy training booklet, http://www.themeasuringsystemofthegods.com/magnetic amplifiers.pdf
upload_2015-9-1_11-4-7.png


it'd be easy enough to make your three legged core slf saturating.

Anyhow here's what happens

Control current holds core well down below center of BH (or volts/amps) curve

BHSelfSat.jpg

amplifier remains cut off because it has enough core to not saturate on a half cycle's volt-second product.
That is, when it started from significantly negative flux.

Now if i raise control current gradually
i'll come to a point where the core no longer can hold off applied voltage
and load current will commence to flow, copiously.

1. No longer in series,, the opposite coil is no longer demagnetizing that leg by load current. Diode blocks any current that would try to demagnetize it.
2. Load current now drives core further into saturation , so impedance collapses allowing more current yet and that's positive feedback.

There's no opposing voltage from other coil's being driven against control coil flux, remember they're no longer in series

The collapse happens over a much smaller range of control current , hence we say gain is higher.
Gain in practice is so high it's almost a bistable, and a bistable is just a high gain element with teeny amount of positive feedback.
To get manageable gain they add another coil where load current opposes saturation(negative feedback), with a lot fewer turns than load coil. That's negative feedback. So you see, they create a high gain element using positive feedback(self saturation)
then surround that high gain element with some negative feedback to make gain predictable.
Remember G/(GH+1) ? In opamps G is a million, in magamps probably hundreds.

Anyway that's why almost all magamps are self saturating (dammot italics sticking again)
and what you are building is a saturable reactor, precursor to magamp.


old jim
 
  • #235
tim9000 said:
OR is does maximum inductance point depend on V.s/N and Area?

?? inductance has to work back to n2 μrelative μ0 Area / Length of path

and only thing not a hard constant is μrelative, which is a function of flux...

inductance curve should be identically shaped scale model of permeability curve ?

hmm italic worked okay here.
 
  • #236
Hi Jim, Thanks for the replies!
jim hardy said:
Path length ? Didnt you already come to that conclusion in above graph ?
I Don't think so, because path length doesn't enter into the data here:
vvd.PNG


jim hardy said:
?? inductance has to work back to n2 μrelative μ0 Area / Length of path

and only thing not a hard constant is μrelative, which is a function of flux...

inductance curve should be identically shaped scale model of permeability curve ?
Isn't μrelative actually a function of B and not flux?
Thats what I thought (about inductance curve having the same shape as μ curve), then I remembered Brms = Vrms/(N*A*2*pi*f)
So Say I was using my 400 turn coil at 50Vrms, we saw that was it's V.s value for 400 turns that gave maximum value of inductance 7.8 H, maximum μrelative,
if I increased or decrease the voltage amplitude we'd move up the BH curve and away from μrelative, (and we saw the impedance of the amp droped under or over 50V) But say I want more inductance for the same 50V supply; so I think I'll increase N because L = N2 μrelative μ0 Area / Length of path
well N2 has gone up, but since B = V/(N*A*2*pi*f), B has gone down, and thus so has μrelative. Same decrease in B if I increase A. So hasn't the overalll inductance gone up, but μrelative has gone down?

Thats enough thoughts for this post.
 

Attachments

  • upload_2015-9-2_13-8-36.png
    upload_2015-9-2_13-8-36.png
    5.2 KB · Views: 434
  • upload_2015-9-2_13-8-48.png
    upload_2015-9-2_13-8-48.png
    5.2 KB · Views: 447
Last edited:
  • #237
tim9000 said:
Isn't μrelative actually a function of B and not flux?

B and Flux are two measures of the same thing,

gotta go now
 
  • #238
jim hardy said:
B and Flux are two measures of the same thing,

gotta go now
Not if area and/or turns aren't constant. Than the flux can be the same but the B can be different.

No worries, ttyl.
 
  • #239
jim hardy said:
bhselfsat-jpg.88102.jpg

amplifier remains cut off because it has enough core to not saturate on a half cycle's volt-second product.
That is, when it started from significantly negative flux.
Ah, I see the postitive feedback, you explained that well. I can see that you're aspousing that you can get full dΦ/dt by starting at the bottom part of the linear region in the bottom quadrant and moving up. But I don't see how the control current is starting from the negative quadrant of the BH curve, why isn't it starting at zero, or why is it "falling back"? If the conrol current acts to drive you up, how did you get down to -ve flux in the first place? Were you magnetically biasing it there with outside flux injection?
[The way you said "the control current holds it well under the BH" implies that the control current green line would move down as the control current was increased, but that would mean that the load current would desaturate the core, thus would be negative feedback, which you said wasn't the case.]

jim hardy said:
it'd be easy enough to make your three legged core slf saturating.
The Series analogue of that parallel circuit, would it be this:
series amp.PNG

I conceed that it wouldn't be as good as the parallel one but is that correct in principal? So each leg is only ever magnetised in one direction? Wouldn't the dΦ/dt of that picture be half that of the saturatable reactor we've been discussing (that I built)?
 
Last edited:
  • #240
tim9000 said:
I can see that you're aspousing that you can get full dΦ/dt by starting at the bottom part of the linear region in the bottom quadrant and moving up. But I don't see how the control current is starting from the negative quadrant of the BH curve, why isn't it starting at zero, or why is it "falling back"? If the conrol current acts to drive you up, how did you get down to -ve flux in the first place?

Control current opposes load current. You'd make control current negative, load current positive .
Observe that the diodes make the core see only positive half cycles , so we're back to why does a transformer saturate on first half cycle if you close in tight at zero crossing..
Remember when we looked at definite integral of sine, the result depends on where in the line cycle you start ?
If you take integral starting at zero, ∫sin sweeps from zero to 2 not from -1 to +1.
Flux being ∫volts does same thing, recall that conversation pages back.

If i have a core that saturates at arbitrary flux of +1 volt-second
and i apply a 1v peak sinewave starting at zero,
it'll saturate in first half cycle when flux crosses +1 on its way to +2.
I could make the core twice as big so it'll handle twice as many volt-seconds, then at end of first half cycle it'd have integrated right up to the point of saturation 2 volt-seconds.

or

i could apply negative DC to the control winding so core's rest flux is at -1, and the first half cycle would push flux positive by 2 , to +1, just the edge of saturation. That'd be "off" state for magamp.
I could reduce negative control current say 10%, now flux integrates from -0.9 to +1.1 which is saturated by 10%..

It's a balancing act much like goes on in your saturable reactor. A little control current controls a lot of load current, but with addition of the diodes load current never aids control current.
tim9000 said:
If the conrol current acts to drive you up, how did you get down to -ve flux in the first place? Were you magnetically biasing it there with outside flux injection?

Control current drives you DOWN.
Load volt-seconds push you UP.
When you cross the brink of saturation, copious load current pushes you further into saturation.
Gain is quite high right around the balance point . Just like an op-amp.
 
  • #241
Sorry to leave, neighbor had a burglar and needed moral support.
tim9000 said:
Not if area and/or turns aren't constant. Than the flux can be the same but the B can be different.

Flux and flux density... i make lots of arithmetic mistakes swapping between the two.
That's why i start with volts per turn, figure out webers/sec, convert that to amplitude of whatever waveform I'm using (i only mess with sine and triangle because their derivatives are well behaved), then having Webers i change to Webers per square meter B.

Of course one still occasionally runs into Maxwells and Gauss and Oersteds and has to go back to his basice...
 
  • #242
tim9000 said:
Thats what I thought (about inductance curve having the same shape as μ curve), then I remembered Brms = Vrms/(N*A*2*pi*f)
that's saying flux density is measured by volts per turn per unit area, which is equivalent to flux is measured by volts per turn, and both are true for sinusoids


tim9000 said:
Isn't μrelative actually a function of B and not flux?
Thats what I thought (about inductance curve having the same shape as μ curve), then I remembered Brms = Vrms/(N*A*2*pi*f)
So Say I was using my 400 turn coil at 50Vrms, we saw that was it's V.s value for 400 turns that gave maximum value of inductance 7.8 H, maximum μrelative,
if I increased or decrease the voltage amplitude we'd move up the BH curve and away from μrelative, (and we saw the impedance of the amp droped under or over 50V) But say I want more inductance for the same 50V supply; so I think I'll increase N because L = N2 μrelative μ0 Area / Length of path
well N2 has gone up, but since B = V/(N*A*2*pi*f), B has gone down, and thus so has μrelative. Same decrease in B if I increase A. So hasn't the overalll inductance gone up, but μrelative has gone down?
I am confused what you mean by urelative. .

if I increased or decrease the voltage amplitude we'd move up the BH curve and away from μrelative,
Can you point to μrelative on the BH curve?
To me it's the slope not something yu can move away from. T
You can shift operating point so your operating range sweeps regions of the curve having greeter or lesser slopes

i need to resolve that mental sticky point to have faith i understand your question..
 
  • #243
jim hardy said:
Sorry to leave, neighbor had a burglar and needed moral support.
My simpathies to your neighbour, that's aweful! I hope they didn't loose too much of value or anything of sentamental value.
jim hardy said:
that's saying flux density is measured by volts per turn per unit area, which is equivalent to flux is measured by volts per turn, and both are true for sinusoids...
Well B as volt-seconds per turn per unit area...So is there a problem with that?

jim hardy said:
I am confused what you mean by urelative. .

Can you point to μrelative on the BH curve?
To me it's the slope not something yu can move away from. T
You can shift operating point so your operating range sweeps regions of the curve having greeter or lesser slopes

i need to resolve that mental sticky point to have faith i understand your question..
(μ) mu or mu relative on the BH curve I just think of as being where the RMS B is operating at, that's the corresponding point of μ or μrelative:
Ok back to my friend the ferris BH permeability curve:
https://upload.wikimedia.org/wikipe...Permeability_of_ferromagnet_by_Zureks.svg.png
350px-Permeability_of_ferromagnet_by_Zureks.svg.png

I assume when I was putting on to the 400 turn coil and load the 50V rms at 50Hz, that I was at μmax because that's when we got maximum impedacnce (theirfore max inductance). But say I was to slide onto the core more sheets of lamina: increasing A, Than would B not drop because of Brms = Vrms/(N*A*2*pi*f)
Or if I wound more turns, increasing N, than V.s/N would drop wouldn't it?
So L = N2 μrelative μ0 Area / Length of path might
increase OVERALL, but haven't we moved from μMAX down to the left, to a lower point on the BH curve, closer to H = 0?
so L is up but μ and B are down, the A and N terms of the equation outweigh the drop in μ?

I'm sorry for the poor quality of my reply, I'm rushed because I wanted to catch you on your time of day cycle. I have to get to bed to get up for an early doctors appointment.
jim hardy said:
Control current drives you DOWN.
Load volt-seconds push you UP.
When you cross the brink of saturation, copious load current pushes you further into saturation.
Gain is quite high right around the balance point . Just like an op-amp.
OK so the green line DOES move DOWN when you increase control current. And the Red line moves UP the higher the AC voltage.
So looking at the right side of the two cores as the AC excitation draws a load current that will produce a demagnetising MMF in the cores. But at the same time, if you think of the dot-convention, the AC excitation produces a pair of dots on the bottom of the cores which pushes a current that increases the control current (the positive feedback) by like transformer action?

Thanks!
 
  • #244
tim9000 said:
Well B as volt-seconds per turn per unit area...So is there a problem with that?
none whatsoever
tim9000 said:
3a%2FPermeability_of_ferromagnet_by_Zureks.svg%2F350px-Permeability_of_ferromagnet_by_Zureks.svg.png

I assume when I was putting on to the 400 turn coil and load the 50V rms at 50Hz, that I was at μmax because that's when we got maximum impedacnce (theirfore max inductance). I'm with you this far.

But say I was to slide onto the core more sheets of lamina: increasing A, Than would B not drop because of Brms = Vrms/(N*A*2*pi*f)
Yes B would drop. Flux would remain constant.
Or
if I wound more turns, increasing N, than V.s/N would drop wouldn't it?
I agree , keeping excitation at 50 V rms, volts per turn would drop.
That means flux would drop. So would B since area wasn't changed.

So L = N2 μrelative μ0 Area / Length of path might
increase OVERALL, but haven't we moved from μMAX down to the left, to a lower point on the BH curve, closer to H = 0?
Yes.
so L is up but μ and B are down, the A and N terms of the equation outweigh the drop in μ?
That can only be answered by applying numbers to real data. Is your graph above from actual measurements,
and is it to scale or conceptual ?

tim9000 said:
I'm sorry for the poor quality of my reply, I'm rushed because I wanted to catch you on your time of day cycle. I have to get to bed to get up for an early doctors appointment.

i thought it was pretty cleanly stated. I have trouble with my acuity varying with time of day - mornings are best. But in today's interrupt driven world , discretionary time seems to appear only in evenings, my nadir.

tim9000 said:
OK so the green line DOES move DOWN when you increase control current. And the Red line moves UP the higher the AC voltage.
yep.
tim9000 said:
So looking at the right side of the two cores as the AC excitation draws a load current that will produce a demagnetising MMF in the cores. But at the same time, if you think of the dot-convention, the AC excitation produces a pair of dots on the bottom of the cores which pushes a current that increases the control current (the positive feedback) by like transformer action?
Dont understand sentence starting with "but". Which picture are you referring to ?


gotta tend to a doctor's appointment myself, Fair Anne's. Back tonight.
 
Last edited:
  • #245
jim hardy said:
"So L = N2 μrelative μ0 Area / Length of path might
increase OVERALL, but haven't we moved from μMAX down to the left, to a lower point on the BH curve, closer to H = 0?"
Yes.
"so L is up but μ and B are down, the A and N terms of the equation outweigh the drop in μ?"
That can only be answered by applying numbers to real data. Is your graph above from actual measurements,
and is it to scale or conceptual ?
Conceptually and practically they should be the same should they not, that's the point of design?
Well let's look at some data:
ohm.PNG

Those curves are wL = 2*pi*f*50/0.6 *400^2 * (B/H)
so everything is constant except permeability (B/H). I got max impedance to be 1260 Ohm at 50Vrms at 50Hz, (and you saw the BH curve in post #233) implying that we get maximum impedance when B = 0.72988689 T
I imagine that if current is controlled to be the same that THEN you could just wrap heaps of turns around the core and get heaps of flux. But if it's V.s that is to be the same, then it doesn't seem like I can do that.
Say I wanted to design an inductor to be as big as possible at a certain voltage and frequency, to get to the biggest it's like I want to design to stay on μMAX to make the most out of my steel, we were able to do that before by using the cross sectional area of A = 0.000555 m^2 but say I want even more inductance.
To get more inductance I'd need more turns, but if I do that the flux will drop, so to maintain μMAX I'd need to drop the area, but I don't want to do that, infact I want to increase the area.
This is my point, is there some fundamental limit on how big an inductor can be for a given V.s at μMAX? {I think I recall you saying that the inductance curve always matched the permeability curve, however that only seems to be true for a constant current, not a constant V.s}
Is it like that inductor we were talking about for 1260Ohm that is as efficient as you can get for 50Vrms@50Hz, any bigger than that you're doing so with a smaller flux density? So like μ gets down after an increase of heaps and heaps of turns to stay at μinitial (where μ is at H = 0) and you can only increase the inductance with μ = μinitial?

jim hardy said:
Dont understand sentence starting with "but". Which picture are you referring to ?
Fair Anne's?
I'm referring to Mr Steiner's picture in post #234 for example, re: load current causes demagnetisation MMF on right side and also the positive feedback to control current, by like transformer action, on left side?Also, what did you think of this:
tim9000 said:
The Series analogue of that parallel circuit, would it be this:
series-amp-png.88124.png

I conceed that it wouldn't be as good as the parallel one but is that correct in principal? So each leg is only ever magnetised in one direction? Wouldn't the dΦ/dt of that picture be half that of the saturatable reactor we've been discussing (that I built)?
 