Japan Earthquake: nuclear plants Fukushima part 2
In summary, there was a magnitude-5.3 earthquake that hit Japan's Fukushima prefecture, causing damage to the nuclear power plant. There is no indication that the earthquake has caused any damage to the plant's containment units, but Tepco is reinforcing the monitoring of the plant in response to the discovery of 5 loose bolts. There has been no news about the plant's fuel rods since the earthquake, but it is hoped that fuel fishing will begin in Unit 4 soon.
  • #1,121
jim hardy said:
Need a few pieces of it to analyze. Surely they've done that ?
Not yet. They inserted a camera to check for any obstacles for the planned robot insertion. Now they first want to use a "sediment cleaning device" (don't know about sample taking capabilities) and after that the robot (which will have radiation and temperature sensors and cameras, but again no sample taking capabilities as far as I know).
  • #1,122
Hiddencamper said:
Edit: another use keeps changing it. Not sure how to proceed
hmmm looks better now ! was that you ?
Meanwhile , back at the reactor
http://www.tepco.co.jp/en/nu/fukushima-np/handouts/2017/images/handouts_170202_01-e.pdf
  • #1,123
I don't think they should rush with that... To safely sample something from 'there' would require some serious thinking.
Ps.: As it is now I won't even try to retrieve that robot... Unintended 'sampling' would be a bad karma.
  • #1,124
  • #1,126
jim hardy said:
But this patent (...) is for the magnetic Westinghouse style control rods not GE hydraulic rods.
Thanks! Those things look like chains to me, but I wouldn't know what they are for:
Edit: I think Tepco identifies them as part of the CRD exchanger, I wouldn't know.
  • #1,127
The images circulating from Unit 5 give a close idea of the equipment in its original state.
https://s28.postimg.org/v3qlx6esb/zoom.jpg
  • #1,128
http://www.tepco.co.jp/nu/fukushima-np/handouts/2017/images1/handouts_170209_08-j.pdf (in Japanese)
Results of the first attempt to remove/clear away sediments from the CRD rails.
Page numbered 4 shows two pairs of images taken somewhere at the top of the CRD rails; the left image is taken before clearing away sediment, the right image is taken after. (Left pair is taken with guide-pipe camera, right pair is taken with the camera installed on the device itself.)
Page 4 shows another two pairs of images taken a bit lower on the slope, where the sediment is better stuck to the surface and harder to remove. Each pair contains before/after images. Left side pair is taken using the guide-pipe camera, hence the device is seen; right side pair of images are taken with the device camera.
Page 5 shows two images (one from guide-pipe camera and one from device camera) taken as the device is traveling on the sediment itself.
Page 6 - conclusions:
- they cleaned about 1m of the 5 metres they had planned to clean (not clear if the planned all 5m for one single session);
- as we move towards the pedestal, the sediment sticks more strongly to the surface and takes longer to clear away;
- they stopped the operation when visibility became bad, and retrieved the device, as they don't want to cause extra visibility troubles for the next step (inspection robot);
- the device was able to climb over and drive over the sediment but there were also places where it couldn't advance/travel over the sediment.
They will analyze the data obtained in view of deciding the next step.
Larger photos and a video (which I couldn't see yet) here:
http://photo.tepco.co.jp/date/2017/201702-j/170209-01j.html
Edit: I saw the video now. There are many fragments of the "sediment" which appear to be pieces of aluminum foil or something similar. At 1:37 the water stream peels off and overturns something that looks like a "slab" of material, maybe 1-2 cm thick, maybe 10x10 cm or more in area. Slab may not be the right word, it still looks like a pretty light material. Lots of radiation-induced noise in the video image.
Likes jim hardy and turi
  • #1,129
Now I see it:
Likes SteveElbows, jim hardy and Sotan
  • #1,130
I watched the first part of the press conference of Tepco where they showed the "sediment removal" video.
- The image getting darker (the part above where I clumsily translated as "visibility getting worse") in fact refers to the camera itself getting tired, most likely die to the damaging effect of the high radiation on the camera sensor. The images were getting darker and darker and they had to pull the device out sooner than planned - while they still had video. The 2h lifetime is in general agreement with the evaluated radiation dose and the 1000 Sv integrated, overall radiation resistance of the camera. The inspection robot to be used in the last step will probably behave similarly, as far as the camera life time is concerned.
- They didn't put this in the PDF report for lack of time, but will be announced later: they analyzed again the radiation-induced noise in the video images and they obtained a new value fo approximately 650 Sv/h, approximately in the same area where they evaluated 530 Sv/h the other day. So if the first time they might have had some doubts about that value, this new one in the same range appears to reinforce the conclusion that there is something, not very sure where, which causes images of that region to show such dose rates. (The speaker mentioned briefly that the 530 Sv/h reported the other day has been wrongly interpreted by certain news sites abroad, as an "increase" in radiation. He underlined again that a day after stopping the nuclear reaction in the vicinity of a used fuel bundle there are probably tens of thousands of Sv/h.)
- I said above that the device was unable to "crawl" in certain areas, the reason is that the tracks allow for approximately 2 cm ground clearance, the robot can easily go over 2 cm obstacles, but the highly irregular in shape sediment sometimes has much more height. It rubs onto the belly of the robot, the tracks don't provide traction any more, so it stalls. The inspection "scorpion" robto has very similar tracks so they will have to think very well what to do next.
- There is no plan to insert a second sediment-cleaning device, they can't easily replace the camera (the device itself is contaminated too), so for now there is no plan of a second attempt.
Likes Charles Smalls, jim hardy and turi
  • #1,131
Thanks !
Probably something that's been around a lot of neutrons.
I'm not jumping on the Corium bandwagon yet, a local hotspot could be a little fragment of something that got vented in first weeks.
  • #1,132
How would any fuel fragment wind up beneath the reactor vessel other than via a melt through?
Is not the vessel set directly on the pedestal, with access openings only from below?
  • #1,133
My grasp is not crystal clear
but i thought the 600 sv-ish reading was not under the vessel inside the pedestal, but in the region between the containment penetration and the pedestal .
So correct me if I'm wrong
And i believe there are pipes routed through there connecting safety valves to suppression pool in torus
and lots of other pipes connected to vessel
a fuel fragment in one of them would shine right through the pipe wall.
So the question becomes what's nearby that high radiation area ?
old jim
Likes etudiant and Sotan
  • #1,134
Two questions/thoughts
Isn't the entire containment flooded with water?
If so, why isn't the water shielding the camera from the radiation?
If it is, (both underwater, and shielding is happening), then wouldn't the actual radiation source be much much higher than they are calculating?
Related question, what is the dose rate (Svr/hr) for nuclear fuel that has spent 6 years cooling?
As in, if the fuel rods had been cooling for 6 years in a spent fuel pond, how radioactive would they be?
And is this rate being measured in reactor 2 the same?
  • #1,135
The containment is not flooded with water.
Water at the bottom of the PCV of Unit 2 is only about 30 cm deep, as you can see on page 18 of this document.
Also, if you take a look at the videos taken by Tepco on/around the CRD rails, it's pretty clear that nothing is under water there.
As for the radiation values it's a bit of a blur because of insufficient information but "in general" the dose rates measured (indirectly, just from analysis of video images) in the PCV of unit 2 "make sense for unshielded irradiated fuel", as Hiddencamper wrote somewhere 2 pages before.
Likes jim hardy
  • #1,136
It can be confusing because in the very first days they tried to flood/fill up the entire containment with seawater, but they could not succeed.
They could not even correctly measure the water level that time, so finally they stopped when the water pumped in were already several times more than the amount needed to fill the containment.
Right now it is as Sotan says: the containments are not flooded, but there are some (different depth for each unit) water at the bottom.
Likes LabratSR and Sotan
  • #1,137
Thank you, jim hardy, that diagram really helps clarify the situation.
It shows mheslep's suggestion is the more plausible, as the source is apparently some lateral distance away from the reactor.
  • #1,138
From a couple pages back, translating from a press conference
Sotan said:
Many reporters were troubled by the numbers reported for radiation level. So (if you look in the figures for Step 4 and Step 5 in this investigaton), we insert a guide pipe through the X-6 penetration, horizontally; as soon as we get inside the PCV, there's about 50 Sv/h. We keep inserting the pipe inside, horizontally, until we reach roughly around the middle of the space between PCV wall and pedestal wall. Here, in the air, image analysis suggests 530 Sv/h (!). Then the guiding pipe bends down and goes all the way to that hole in the pedestal wall; just as we enter the pedestal space, image analysis shows 20 Sv/h.
and from another link posted by Sotan, http://www.tepco.co.jp/en/nu/fukushima-np/handouts/2017/images/handouts_170130_02-e.pdf
(orange ovals mine)
Thanks Sotan !
I'd guess the camera went past something small and "hot" .
  • #1,139
You are correct with that drawing Jim.
Tepco has already published in a report (the one given in post #1109) this drawing below, which identifies the spots for which they evaluated the radiation doses.
The blue dots numbered 1, 2, 3 are the spots where they measured (by image analysis only) 30, 530 and 20 Sv/h respectively.
1 is immediately after entering the PCV. 2 is in the air, about 2.3m from the pedestal wall. 3 is immediately after entering the pedestal.
Changing the subject, I came home to watch the second part of the press conference held after the "sediment clearing session"... only to find that it is not available anymore. I should have downloaded it, I guess.
Likes jim hardy
  • #1,140
So many of the videos and reports become unavailable so quickly. I find some links referenced to NHK news both English and Japanese don't work after a short time. They doesn't seem to do much archiving.
Was footage of the probe traveling through the high dose range published? I have seen video of the camera entering the X-6 penetration and of it exiting into the pedestal but not the travel through the tube where it encounters the 650Sv/h level of distortion.
  • #1,141
The severe accident guidelines have you flood containment to backfill the hole in the reactor following a rupture. The immediate concern is to establish minimum debris submergence level (get the core slag under water). Then flood up to try and establish core cooling. Once you've flooded containment you could feasibly open up the drywell head and vessel head and "look down" into the core.
In this case, there is containment system damage causing water to spill out. So until they find and plug those leaks they will be unable to use normal means for shielding the core slag.
Note: post Fukushima severe accident guidelines have changed and do not emphasize immediate debris submergence for mark 1/2 containments. The goal is to establish minimum debris cooling injection rates to prevent a rapid steam pressure rise in the drywell and to preserve the suppression pool as a water scrubbed release path.
Likes LabratSR and turi
  • #1,142
English reports on debris removal work (probably based on Sotan's work :wink:):
http://www.tepco.co.jp/en/press/corp-com/release/2017/1375551_10469.html
http://www.tepco.co.jp/en/nu/fukushima-np/handouts/2017/images/handouts_170209_01-e.pdf
http://photo.tepco.co.jp/en/date/2017/201702-e/170209-01e.html
English summary of newest quarterly report:
http://www.tepco.co.jp/en/press/corp-com/release/2017/1375451_10469.html
Summary of summary:
  • SFP fuel removal planned in 2018 for Unit 3 and in 2020 for Unit 1, preparatory work underway.
  • Ice wall: Amount of water pumped up daily has declined from 400 cubic meters to 140 cubic meters.
Report in Japanese:
http://www.tepco.co.jp/press/release/2017/pdf1/170210j0102.pdf
Likes Sotan
  • #1,143
Thank you turi.
I just want to refer to the last link you posted above, the 91-page long report in Japanese. The title would sound something like "Progress of the reform plan on nuclear power safety" and aims to show the work Tepco is doing to generaly improve the safety level in its three nuclear facilities (Fukushima Daiichi, Fukushima Daini, Kashiwazaki-Kariwa plants, the last one, world's largest nuclear power plant, still employing 6000 workers and hoping to restart production some day). I only browsed through it enough to see that there's not much new content related to the mainly technical scope of this thread, so... I don't think I will quote anything of it in here.
  • #1,145
Seriously? So the fuel is just sitting somewhere, in air? For how long?
  • #1,146
Since 2011. More under constant rain than just air though.
  • #1,147
Don't get excited until they find it. The tempest might still be in the teapot.
  • #1,148
Newly stitched together images from Unit 2, courtesy of IRID:
http://photo.tepco.co.jp/date/2017/201702-j/170215-01j.html
Edit: To me, if I interpret the pictures correctly, it looks as if the alternative route to the left for the inspection robot isn't feasible as well. Something that could take hold of the middle beam would be necessary, but that would be a much more complex robot (or probably an electro magnet or two could help).
Likes Sotan
  • #1,149
The link posted by turi above leads to a PDF report in which Tepco shows us the options that they are considering these days, regarding the final step of the planned investigation of PCV/pedestal of Unit 2, namely the step which involves sending in the "scorpion" robot equipped with cameras, thermometer and radiation meter.
Pages 1-3 you've seen them before, they show the general concept, object and steps of this investigation. (Page numbers as inscribed at bottom-right corner)
Pages 4-6 compile various information obtained in previous steps - including a few newly stitched and reprocessed images. Page 5 underlines the gap (45 to 140 mm wide) that exists between the end of the CRD rails and the grating platform. White dotted line on Page 6 shows a possible route for inserting the robot (which, as you have seen in a presentation video, is capable of crossing some gaps).
Page 7 mentions that additional information could be obtained by performing this final step, with the robot taking over from where the sediment-cleaning robot stopped. The scorpion robot is shown, with its front and back camera, thermometer and radiation measuring device (which by the way still has a plus/minus 20% error). The latter device, installed in a "corrugated tube" (?) practically tied to the power cable of the robot, will be in contact with the sediment and therefore the reading will not be purely, 100%, air radiation dose.
Pages 8 and 9 show the two investigation options that they are considering, with pros and cons:
Page 8: In case they send the robot only down to the end of the CRD rails:
- they will be able to peek at the pedestal installations from an even lower point of view, getting info about the state of the hardware and the features of the sediment;
- they will measure temperature and radiation dose;
- if the device gets in trouble while crawling over the sediment, they can pull it back using the power cable. The robot might end up unable to proceed, due to: long tracks; relatively large weight; changes in the center of gravity due to manoeuvering the back-end camera.
Even if the robot does not make it to the final destination (end of the CRD rails) it would still contribute useful new data.
Page 9: In case they attempt to send the robot onto the grating platform:
- they would get more images of the holes in the grating, as well as of the bottom of the lower part of the reactor, and be able to assess the state of the CRD housings, of the sediment etc.;
However:
- the access is difficult and risky; the robot might end up unable to advance or - even worse - fall through the holes;
- while crossing the gap the robot will be in its fully extended configuration, so no images will be available from the back-end camera to help with planning the best route; they will depend only on images from the front camera;
- if the robot falls down through some opening, it might be impossible to retrieve just by pulling the power cables;
- as the investigation is the main priority, if the time needed to retrieve the robot becomes a limiting factor they might simply leave the robot in, at the end.
Finally page 10 gives some general perspective of the grating platform which is the object of this whole 7-step investigation. Red areas show places where grating has fallen, blue is safe grating, grey is unexplored area.
Same link given by turi above also leads to this second report, also in Japanese only, which is an attempt from Tepco to put the announced radiation doses into some perspective. They explain on page 1 that radiation is stopped/diminished by shielding (lead, iron, concrete...), by distance, and by the passage of time. On page 2 they point towards the place where the 650 Sv/h was estimated the other day, further explaining that the people operating the guiding pipes in this investigation, behind the shield, were subjected to only 6 mSv/h, while the value measured at the monitoring post located at the fence of Tepco's land shows only 2 microSv/h. All these are intended to show that there's no danger for the public, and even for the workers they do all they can to reduce exposure.
Likes LabratSR, jim hardy and turi
  • #1,151
Video, Images and PDF of newest robot excursion into unit 2:
http://photo.tepco.co.jp/date/2017/201702-j/170216-01j.html
Edit: I didn't see it in the video but on what little I understood from the PDF, the robot was left there (while the cabling was pulled back?), in the video at the end it looks as if the robot can't move and its crawlers slip. After some image stitching we should have more details, there are quite a few details previously not visible in the video.
Edit 2: English link:
http://photo.tepco.co.jp/en/date/2017/201702-e/170216-01e.html
Likes Charles Smalls, Sotan and LabratSR
  • #1,152
Press conference regarding the latest robot excursion:
http://www.tepco.co.jp/tepconews/library/archive-j.html?video_uuid=mt9v8ewx&catid=69619
Has anyone a good theory on what kind of material could be on that control rod drive exchange rail which causes the high radiation readings? Why is it where it is? Did it come from above (and another opening/crack in the pressure vessel) or did it somehow get there from inside the pedestal?
  • #1,153
Post #1133 of jim hardy (on page 57) gives the best hypothesis in my opinion.
The radioactive material is not on the CRD rail, but somewhere above it. Such as in... a pipe, that comes from the RPV. "a fuel fragment in one of them [pipes] would shine right through the pipe wall." to quote jim.
Watched about half of the press conference too.
- Even before that, while checking the online Japanese press, I noticed disappointment and found the word "failure" here and there. In the press conference the speaker underlines that they are still happy with the wealth of information that they got, even though things didn't go as well as they had wished.
- The published video is only a few minutes, but they got much more. The robot went in around 08:00, went quickly over the clean area, in 20-30 min began having trouble with the left track, then until 13:00 they tried various manoeuvers with it until they gave up, so it was not an easy or rushed decision. Even after that, they took another 1.5 hours of video of the area, using the powerful lighting and camera in the tail of the scorpion. They are happy with the quality of the image (it should look much better after some processing).
Likes turi
  • #1,154
There are SRV downcomers all around the containment, and we know that they had at attempted to get at least 1 SRV open while fuel damage was occurring. I believe they had some success too, but 1 SRV isn't sufficient to fully depressurize.
Likes turi
  • #1,155
Thanks. Does that fit with the higher dose rate from the radiation sensor (more sensitive towards the rail, if I have understood this correctly) versus the estimated dose rate from the camera?
48K
16K
267K