westfield said:Ok, that's clearer. I'm trying to broaden my understanding of why these hardened vent systems are even fitted to these plants when they are not filtered, it's like they never intend to use them.
I appreciate your real life knowledge in the subject. NPP designer I am not :)
Are you able to clarify something.
Disregarding which venting system, is venting (to the environment) at close to or exceeding the design pressure of the RPV considered something that might be required in a DBA or would that be only in the BDBA realm?
For a BWR, venting is not required in the design basis accident. Containment spray is credited for temperature/pressure control of the containment during an accident.
Depending on plant design, between 10-30 minutes after a LOCA, if the containment pressure is still high, the safety logic will transfer one of your RHR pumps from its LPCI mode to the containment spray mode. In this mode, the RHR heat exchanger is brought in service automatically, the LPCI injection valve shuts, and the containment spray valves open, making it rain in containment. This greatly reduces pressure and temperature, and is used for containment P/T control while you still have a steam environment. (Containment spray is so effective, that an inadvertent actuation will create a vacuum in containment, and could damage containment if you don't stop it in a timely fashion. Many plants have interlocks/permissives to help prevent this).
In this mode, heat is transferred from the containment steam atmosphere to the spray droplets, down into the suppression pool. RHR takes suction from the suppression pool and passes it through the RHR heat exchanger and then back through the sprayers. The heat exchanger transfers the heat to the ultimate heat sink. One of the design requirements for the BWR DBA LOCA is that peak containment pressure stays below the containment design pressure (45-65 PSIG for Mark I/II containments, 15 PSIG for Mark III containments). Containment spray is credited for that.
Under DBA, the Standby gas treatment system is only required to deal with any primary containment leakage. It is assumed you leak around 0.5% of your containment volume per day. standby gas treatment is required to filter this radionucleide inventory prior to release. In some plants, standby gas treatment can also be lined up with the containment if needed, although this is not a safety mode of operation, and is disabled/isolated while a LOCA signal is locked in. The idea is that SBGT cleans up leakage until you stabilize the plant, cool it down to clear the LOCA signal, then (in most plants) you can use SBGT to help clean up the containment atmosphere so workers can get into it. SBGT is not meant for venting a high temperature/pressure containment, only a low temp/press one.